The main panel had larger wires connected to smaller wires with wire nuts
and duct tape...like a 10 awg to a 20 awg. Is this acceptable ? What type of write up would be appropriate ? ![]()
|
| Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Are you sure it was 20 awg? That would be too small for any circuit.
Wire nuts in the panel are not an issue. Down sizing the wire can be acceptable depending on the size of the breaker attached to the conductors. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
||||
|
||||
|
Quote:
breaker....Thank God for Nachi... |
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes, the OCPD would need to be rated for the smallest conductor on that circuit even if those splices were not within the panel. So you could leave the panel with a #10 AWG conductor and splice a #14 conductor AWG to it some where down the line. The OCPD would then need to be 15 amps. As Jeff stated splices are fine due to NEC 312.8.
|
|
#5
|
||||
|
||||
|
Quote:
|
|
#6
|
||||
|
||||
|
David- when I see larger conductors spliced to smaller conductors in a panel like that it raises the "aluminum wire" red flag. That's not always the case, but I've found it more than a few times. Just a thought.
"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com SmithHomeInspection@yahoo.com NY State Lic. # 16000008304 631-434-5200 |
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
So what would be your concern the wire connector type? |
|
#8
|
|||
|
|||
|
Please Note:
mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would assume the major concern is the possibility that this would be an indication of the the presence of otherwise unsuspected aluminum banch circuit wiring.
|
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Got it. So pigtailing a piece of copper at the CB would make you think that the structure may have small aluminum branch circuit wiring. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| service panel question | fbuttermore | Electrical Inspections | 6 | 10/3/10 1:50 PM |
| 1910 Build | mcyr | Electrical Inspections | 12 | 8/1/10 1:41 PM |
| Another bonding of service panel question? | mthiltgen | Electrical Inspections | 9 | 3/4/10 6:41 PM |
| Panel Question | gmckenzie | Electrical Inspections | 9 | 8/24/07 1:25 AM |