Default Panel box wiring..Question

The main panel had larger wires connected to smaller wires with wire nuts

and duct tape...like a 10 awg to a 20 awg. Is this acceptable ? What

type of write up would be appropriate ?



Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/28/10, 10:47 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Panel box wiring..Question

Are you sure it was 20 awg? That would be too small for any circuit.

Wire nuts in the panel are not an issue. Down sizing the wire can be acceptable depending on the size of the breaker attached to the conductors.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/28/10, 11:39 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Panel box wiring..Question

Quote:
Originally Posted by jpope View Post
Are you sure it was 20 awg? That would be too small for any circuit.

Wire nuts in the panel are not an issue. Down sizing the wire can be acceptable depending on the size of the breaker attached to the conductors.
thanks Jeff...I meant to say...a 10awg to a 12awg....I was thinking of 20amp
breaker....Thank God for Nachi...
Reply With Quote
  #4  
Old 10/28/10, 6:55 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel box wiring..Question

Yes, the OCPD would need to be rated for the smallest conductor on that circuit even if those splices were not within the panel. So you could leave the panel with a #10 AWG conductor and splice a #14 conductor AWG to it some where down the line. The OCPD would then need to be 15 amps. As Jeff stated splices are fine due to NEC 312.8.
Reply With Quote
  #5  
Old 10/29/10, 11:00 AM
James L. Keilson's Avatar
James L. Keilson James L. Keilson is offline
InterNACHI Member
 
Join Date: Oct 2010
Location: Maryland, USA
Posts: 1,378
Send a message via ICQ to jkeilson
Default Re: Panel box wiring..Question

Quote:
Originally Posted by Robert Meier View Post
Yes, the OCPD would need to be rated for the smallest conductor on that circuit even if those splices were not within the panel. So you could leave the panel with a #10 AWG conductor and splice a #14 conductor AWG to it some where down the line. The OCPD would then need to be 15 amps. As Jeff stated splices are fine due to NEC 312.8.
This completely correct. You can downsize the wire as long as it is on the proper breaker for the smaller size wire.
Reply With Quote
  #6  
Old 10/30/10, 8:00 AM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Panel box wiring..Question

David- when I see larger conductors spliced to smaller conductors in a panel like that it raises the "aluminum wire" red flag. That's not always the case, but I've found it more than a few times. Just a thought.



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
  #7  
Old 10/30/10, 8:45 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel box wiring..Question

Quote:
Originally Posted by bsmith View Post
David- when I see larger conductors spliced to smaller conductors in a panel like that it raises the "aluminum wire" red flag. That's not always the case, but I've found it more than a few times. Just a thought.

So what would be your concern the wire connector type?
Reply With Quote
  #8  
Old 10/30/10, 9:11 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel box wiring..Question

I would assume the major concern is the possibility that this would be an indication of the the presence of otherwise unsuspected aluminum banch circuit wiring.
Reply With Quote
  #9  
Old 10/30/10, 9:17 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel box wiring..Question

Quote:
Originally Posted by mthomas2 View Post
I would assume the major concern is the possibility that this would be an indication of the the presence of otherwise unsuspected aluminum banch circuit wiring.

Got it. So pigtailing a piece of copper at the CB would make you think that the structure may have small aluminum branch circuit wiring.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
service panel question fbuttermore Electrical Inspections 6 10/3/10 1:50 PM
1910 Build mcyr Electrical Inspections 12 8/1/10 1:41 PM
Another bonding of service panel question? mthiltgen Electrical Inspections 9 3/4/10 6:41 PM
Panel Question gmckenzie Electrical Inspections 9 8/24/07 1:25 AM


All times are GMT -4. The time now is 9:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts