Would the sump pit cover qualify as sufficient flooring to meet clearance requirements?
Attached Thumbnails
panel-clearance-hpim7143.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 9/12/10, 5:19 PM
David Hays David Hays is online now
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Panel clearance

No. If you are inspecting to code you would need 3' clear space in front.You would also need the clear space 30" wide.



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #3  
Old 9/12/10, 6:06 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel clearance

Quote:
Originally Posted by dhays View Post
No. If you are inspecting to code you would need 3' clear space in front.You would also need the clear space 30" wide.
I know that. But how could this be corrected without relocating panel or pump? Home built in 1983.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #4  
Old 9/12/10, 6:18 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel clearance

Quote:
Originally Posted by ccurrins View Post
I know that. But how could this be corrected without relocating panel or pump? Home built in 1983.
IMO it cannot be done. One or the other must go somewhere else.
Reply With Quote
  #5  
Old 9/12/10, 6:46 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Panel clearance

A picture is worth a 1000 words
Attached Thumbnails
panel-clearance-jsw_p9090140.jpg  



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #6  
Old 9/12/10, 7:05 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Panel clearance

Quote:
Originally Posted by ccurrins View Post
I know that. But how could this be corrected without relocating panel or pump? Home built in 1983.
Chris,
I think we all know that the sump pit and/or the electrical panel isn't going to be moved. So, report it as you see it and move on.

Now, off the record, if this was in my home, I would install a solid, rigid (preferably steel) cover plate and bolt it to the floor. This would satisfy my need for safety, and still allow access to the pit for maintenance. Really, how often does one go to their breaker panel anymore, let alone needing repairs in it?
Jeff
Reply With Quote
  #7  
Old 9/12/10, 7:28 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel clearance

Quote:
Originally Posted by dhays View Post
No. If you are inspecting to code you would need 3' clear space in front.You would also need the clear space 30" wide.

If the home built before the 1980's only 2.5 feet was required.

www.MauiHomeInspections.com
Reply With Quote
  #8  
Old 9/13/10, 12:13 AM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel clearance

Thanks for the replies. I new there wasn't much that can be done. Just curious how others would report the safety issue. I reported like Jeff has said. I mentioned it but not as a defect in the summary.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #9  
Old 9/13/10, 2:35 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel clearance

And nobody sees a problem with the sump pit discharging into the sewer?
Reply With Quote
  #10  
Old 9/14/10, 5:50 PM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 30,614
Default Re: Panel clearance

Big problem.



Nick Gromicko, Certified Master Inspector

Find a Home Inspector
"Just as iron sharpens iron, one man sharpens another." Proverbs 27:17
Reply With Quote
  #11  
Old 9/14/10, 6:38 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,715
Default Re: Panel clearance

Is this a grinder pump, or a sump pump? Grinders go to main sewer; sumps should go to outside the home. What is that pipe on the left from?



CMI, CPI, KS #0110-0094 Termite #16601
KS Radon #KS-MS-0027
BBB A+ Accredited Business
Serving the Greater Kansas City Metro Area
Eastern Kansas/Western Missouri
http://www.metrospeckc.com
"If opportunity doesn't knock, build a door"--Milton Berle
Reply With Quote
  #12  
Old 9/14/10, 8:07 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel clearance

Quote:
Originally Posted by gfarnsworth View Post
Is this a grinder pump, or a sump pump? Grinders go to main sewer; sumps should go to outside the home. What is that pipe on the left from?
Look like a sewer ejector pump to me. A sump pump would normally have only one pipe.
Reply With Quote
  #13  
Old 9/14/10, 9:28 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel clearance

Quote:
Originally Posted by Ian Gills View Post
And nobody sees a problem with the sump pit discharging into the sewer?
The black (ABS) pipe is a vent pipe, it drains outside at left side.
Attached Thumbnails
panel-clearance-hpim7146.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Need a home inspection in Wyoming? Check out InterNACHI's listing of Wyoming certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 9/18/10, 9:52 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel clearance

Ok....based on the angle of the picture the pump itself may not be in the 30 inch wide working space...but the vent pipe to the left is....simpy reroute the vent pipe to the right, up and over...

Only needs 30 inches for panel width space and 36 in front.....re-route some pipes....unless ofcourse this is my optical illusion.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts