Default Panel Cover Screws

I inspected a new home today and the panel cover was secured with “self tapping” screws, the kind you would use to drill through metal. These screws are not pointed like wood screws; however they are not blunt end screws either. They could definitely damage the wire insulation if they came in contact.

I can not find under the electrical section of the IRC where it says blunt end screw are required. Can anyone provide me with that info? Thank you in advance.
Reply With Quote
  #2  
Old 4/23/07, 3:46 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Panel Cover Screws

http://www.nachi.org/forum/f19/wrong-screws-panel-front-15427/

You really do not need a code section to call this out.
Reply With Quote
  #3  
Old 4/23/07, 4:01 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Panel Cover Screws

Brian,

I agree with you that this is a no brainer, however is there anything in the code. I just want a reference for the builder.
Reply With Quote
  #4  
Old 4/23/07, 4:22 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Panel Cover Screws

It would be more of a listing issue I would think.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #5  
Old 4/23/07, 5:30 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Cover Screws

Nec 110.3(b)
Reply With Quote
  #6  
Old 4/23/07, 7:05 PM
Mathew Hawley Mathew Hawley is offline
InterNACHI Member
 
Join Date: Nov 2006
Location: Melbourne, Fl
Posts: 782
Default Re: Panel Cover Screws

Thank you Marc
Reply With Quote
  #7  
Old 4/23/07, 7:49 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Cover Screws

Matthew,

If the builder has the nerve to ask you about the specific code that prohibits using pointed sheet metal screws in an electrical box, tell them it's under the code of common sense and tell them to look it up.
Reply With Quote
  #8  
Old 4/23/07, 8:27 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Cover Screws

Quote:
Originally Posted by Scott Schultz
Matthew,

If the builder has the nerve to ask you about the specific code that prohibits using pointed sheet metal screws in an electrical box, tell them it's under the code of common sense and tell them to look it up.
You've got that right!

Nearly everything that you'd think is "common sense" is part of a code text someplace. I just wish people would just think a bit, first.

Cutler-Hamer panel cover screws do look a lot like self-tappers, so I might ask if that's what we're dealing with?

I might take a photo of "factory" screws for most of the major brands, if anyone thinks that would be helpful? It would take some effort, so somebody let me know if that's somethig that would be interesting to have documented.
Reply With Quote
  #9  
Old 4/23/07, 8:49 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Cover Screws

This thread has brought up a question I have wondered about for a long time.
How many states will allow a Home Inspector to quote a code section? I know that in NC this is not allowed.
Reply With Quote
  #10  
Old 4/23/07, 9:03 PM
Bruce M. Graham Bruce M. Graham is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Gainesville, FL
Posts: 2,099
Default Re: Panel Cover Screws

I think Kentucky prohibits it also.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #11  
Old 4/23/07, 9:04 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Cover Screws

Also be aware there are two different thread pitches for these "fat head" screws. If you mix them up the panel threads will be trashed and it won't hold either of them after that. One type is the single spiral fine thead, the other is a double helix "fast" thread that goes in twice as fast.
If you can't run it in with your fingers ... stop. There is a chance you have the wrong screw. Hacks who are not coming back just run them down. It works a couple times then they are totally stripped.
Reply With Quote
  #12  
Old 4/23/07, 9:35 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Cover Screws

Quote:
Originally Posted by Mike Whitt
This thread has brought up a question I have wondered about for a long time.
How many states will allow a Home Inspector to quote a code section? I know that in NC this is not allowed.
I think it's generally prohibited, but lots of these guys just want to know for their own personal information. People like to "expand their horizons" with a little personal reading. I seriously doubt that any actual code sections are getting cited in any written customer reports. It seems to me that the information exchanged on this site has little or nothing to do with the content of the resultant report, and more to do with the general education of the inspector who was asking. To that end, I'm happy to respond with as much detail and accuracy as I know how to.
Reply With Quote
  #13  
Old 4/23/07, 9:56 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,172
Default Re: Panel Cover Screws

Quote:
Originally Posted by Marc D. Shunk
I think it's generally prohibited, but lots of these guys just want to know for their own personal information. People like to "expand their horizons" with a little personal reading. I seriously doubt that any actual code sections are getting cited in any written customer reports. It seems to me that the information exchanged on this site has little or nothing to do with the content of the resultant report, and more to do with the general education of the inspector who was asking. To that end, I'm happy to respond with as much detail and accuracy as I know how to.
I'm sure many agree with me, when I say THANK YOU for all the information you provide to us !!!

(And yes, your idea of pictures is a great one. Another tool !!! )

Reply With Quote
  #14  
Old 4/23/07, 10:08 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Cover Screws

Quote:
Originally Posted by Marc D. Shunk
I think it's generally prohibited, but lots of these guys just want to know for their own personal information. People like to "expand their horizons" with a little personal reading. I seriously doubt that any actual code sections are getting cited in any written customer reports. It seems to me that the information exchanged on this site has little or nothing to do with the content of the resultant report, and more to do with the general education of the inspector who was asking. To that end, I'm happy to respond with as much detail and accuracy as I know how to.
Thanks for the explanation.
I agree that knowing the article and section helps with any type of work that is being done as it also helps with the overall knowledge

Again thanks for the explanation.
Reply With Quote
  #15  
Old 4/23/07, 10:24 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Panel Cover Screws

Quote:
Originally Posted by Mike Whitt
This thread has brought up a question I have wondered about for a long time.
How many states will allow a Home Inspector to quote a code section? I know that in NC this is not allowed.
Mike, not that I do it, but please let me know where NC prohibits referece to codes. Thanks.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Sub panel need cover? bmargiotti Electrical Inspections 13 3/5/06 4:28 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:01 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts