Default Panel disconnect

200 amp service disconnect outside at meter. Distribution panel inside fed with 3 wire at 200 amp breaker using PVC conduit. Neutrals and grounds terminated together at each bus.

Question- Isn't the panel inside a remote distribution (sub) panel, meaning the neutrals should be isolated?

Also shouldn't this be a 4 wire feed, or can neutral act as ground?

Cutler-Hammer. Pic is best I have.
Attached Thumbnails
panel-disconnect-hpim7798.jpg   panel-disconnect-hpim7816.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/16/10, 7:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Panel disconnect

You are correct. The disconnect is located in the service equipment. The other panel is a distribution (sub) panel and should be wired as such - four-wire feed, with isolated neutrals.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 10/16/10, 7:56 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel disconnect

Is that main panel loose or is it an optical conclusion.

www.MauiHomeInspections.com
Reply With Quote
  #4  
Old 10/16/10, 8:29 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel disconnect

Quote:
Originally Posted by jpope View Post
You are correct. The disconnect is located in the service equipment. The other panel is a distribution (sub) panel and should be wired as such - four-wire feed, with isolated neutrals.
Thanks, thought I was. Been this way since home was built in 'O6, owner is a fire chief and his friend is the small town code inspector.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #5  
Old 10/16/10, 8:30 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel disconnect

Quote:
Originally Posted by Mark Thorman View Post
Is that main panel loose or is it an optical conclusion.

www.MauiHomeInspections.com
Optical



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #6  
Old 10/16/10, 8:31 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel disconnect

As stated it should be a 4 wire feeder with the neutrals and EGC's separated at the sub-panel. There also are some issues with the NM cables not being properly secured within 12" of the panelboard.
Reply With Quote
  #7  
Old 10/16/10, 8:35 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel disconnect

Quote:
Originally Posted by Robert Meier View Post
As stated it should be a 4 wire feeder with the neutrals and EGC's separated at the sub-panel. There also are some issues with the NM cables not being properly secured within 12" of the panelboard.
Thanks, I noted unsecured cables, used for finished basement. Do you know if these Cutler-Hammer breakers can be used for 2 circuits (double tapped) bottom on each side?
Attached Thumbnails
panel-disconnect-hpim7796.jpg   panel-disconnect-hpim7797.jpg  



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 10/16/10 at 8:40 PM..
Reply With Quote
  #8  
Old 10/16/10, 9:40 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel disconnect

Quote:
Originally Posted by ccurrins View Post
Thanks, I noted unsecured cables, used for finished basement. Do you know if these Cutler-Hammer breakers can be used for 2 circuits (double tapped) bottom on each side?
I can't say with 100% certainty, but I'm 99% sure that they're lugs are not listed for more than one conductor.

A simple splice can fix the problem.
Reply With Quote
  #9  
Old 10/16/10, 10:14 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel disconnect

Quote:
Originally Posted by Robert Meier View Post
I can't say with 100% certainty, but I'm 99% sure that they're lugs are not listed for more than one conductor.

A simple splice can fix the problem.
99% is good enough for me. That's was my take on it. They kind of appeared to have a slot for 2 conductors, but the only breakers I'm familiar with that allow that are made by Square D.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #10  
Old 10/16/10, 10:57 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel disconnect

Quote:
Originally Posted by ccurrins View Post
99% is good enough for me. That's was my take on it. They kind of appeared to have a slot for 2 conductors, but the only breakers I'm familiar with that allow that are made by Square D.

If you're so inclined you could look in the UL "white book" for the listing of that particular CB.

http://www.ul.com/global/eng/pages/o...l/newsletters/
Reply With Quote
  #11  
Old 10/18/10, 2:02 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel disconnect

Quote:
Originally Posted by Robert Meier View Post
If you're so inclined you could look in the UL "white book" for the listing of that particular CB.

http://www.ul.com/global/eng/pages/o...l/newsletters/
Thanks Robert. I did find that the breaker in question,CH BR, is not designed for 2 conductors.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #12  
Old 10/24/10, 8:39 PM
Greg Keene, CPI's Avatar
Greg Keene, CPI Greg Keene, CPI is offline
InterNACHI Member
 
Join Date: May 2007
Location: Evergreen, CO
Posts: 628
Default Re: Panel disconnect

Just a thougt, but the panel inside may not be a sub panel. I have seen main disconnects at the meter where the ground and nuetral were not bonded at the shut off, but they were bonded inside the main distribution panel. If that is the case, then the inside panel is not a sub and the ground and neutral would be bonded inside. Sometime you have to remove the dead front at the disconnect to see what is happeneing.



Greg Keene
Clear Choice Home Inspections
Evergreen, CO
303-674-3234
greg@clearchoice-hi.com
Reply With Quote
  #13  
Old 10/24/10, 10:25 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Panel disconnect

Quote:
Originally Posted by gkeene View Post
Just a thougt, but the panel inside may not be a sub panel. I have seen main disconnects at the meter where the ground and nuetral were not bonded at the shut off, but they were bonded inside the main distribution panel. If that is the case, then the inside panel is not a sub and the ground and neutral would be bonded inside. Sometime you have to remove the dead front at the disconnect to see what is happeneing.
So if the neutral is not bonded to ground at service "main" disconnect and there is only a 3 wire feed, 2 hots and 1 neutral, as with this panel, with neutral connected to ground bus, where is the path to earth?

Also when the service wire from the meter connects to the disconnects, the disconnects are now considered the "main service". All grounding must be bonded together with the neutrals at this point. Any service panels after this point, whether it's the main service or not, is now considered a "sub-panel" and both the ground wires and neutral wires must be isolated from each other.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 10/24/10 at 10:54 PM..
Reply With Quote
Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 10/25/10, 11:33 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Panel disconnect

Quote:
Originally Posted by gkeene View Post
Just a thougt, but the panel inside may not be a sub panel. I have seen main disconnects at the meter where the ground and nuetral were not bonded at the shut off, but they were bonded inside the main distribution panel. If that is the case, then the inside panel is not a sub and the ground and neutral would be bonded inside. Sometime you have to remove the dead front at the disconnect to see what is happeneing.
I think you will find this to be incorrect.

There is "service" equipment, and there is "other" equipment. The service-disconnect is located in the service equipment. At that point, there must be a connection to earth, which must be bonded to the service neutral. Refer to NEC 250.24(A) & 250.24(A)(1)

Any panels/equipment on the load-side of the service equipment must have neutrals isolated from the grounding conductors (some exceptions do apply) - Refer to NEC 250.24(A)(5)



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 10/25/10 at 12:00 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Main Panel vs Sub-Panel and main disconnect? rbassett Electrical Inspections 11 10/24/09 6:16 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:13 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts