200 amp service disconnect outside at meter. Distribution panel inside fed with 3 wire at 200 amp breaker using PVC conduit. Neutrals and grounds terminated together at each bus.
Question- Isn't the panel inside a remote distribution (sub) panel, meaning the neutrals should be isolated? Also shouldn't this be a 4 wire feed, or can neutral act as ground? Cutler-Hammer. Pic is best I have. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
You are correct. The disconnect is located in the service equipment. The other panel is a distribution (sub) panel and should be wired as such - four-wire feed, with isolated neutrals.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#4
|
||||
|
||||
|
Thanks, thought I was. Been this way since home was built in 'O6, owner is a fire chief and his friend is the small town code inspector.
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#5
|
||||
|
||||
|
Quote:
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
As stated it should be a 4 wire feeder with the neutrals and EGC's separated at the sub-panel. There also are some issues with the NM cables not being properly secured within 12" of the panelboard.
|
|
#7
|
||||
|
||||
|
Thanks, I noted unsecured cables, used for finished basement. Do you know if these Cutler-Hammer breakers can be used for 2 circuits (double tapped) bottom on each side?
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Last edited by ccurrins; 10/16/10 at 8:40 PM.. |
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
A simple splice can fix the problem. |
|
#9
|
||||
|
||||
|
Quote:
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#10
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
If you're so inclined you could look in the UL "white book" for the listing of that particular CB. http://www.ul.com/global/eng/pages/o...l/newsletters/ |
|
#11
|
||||
|
||||
|
Quote:
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#12
|
||||
|
||||
|
Just a thougt, but the panel inside may not be a sub panel. I have seen main disconnects at the meter where the ground and nuetral were not bonded at the shut off, but they were bonded inside the main distribution panel. If that is the case, then the inside panel is not a sub and the ground and neutral would be bonded inside. Sometime you have to remove the dead front at the disconnect to see what is happeneing.
|
|
#13
|
||||
|
||||
|
Quote:
Also when the service wire from the meter connects to the disconnects, the disconnects are now considered the "main service". All grounding must be bonded together with the neutrals at this point. Any service panels after this point, whether it's the main service or not, is now considered a "sub-panel" and both the ground wires and neutral wires must be isolated from each other. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Last edited by ccurrins; 10/24/10 at 10:54 PM.. |
| Need a home inspection in Maine? Check out InterNACHI's listing of Maine certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
There is "service" equipment, and there is "other" equipment. The service-disconnect is located in the service equipment. At that point, there must be a connection to earth, which must be bonded to the service neutral. Refer to NEC 250.24(A) & 250.24(A)(1) Any panels/equipment on the load-side of the service equipment must have neutrals isolated from the grounding conductors (some exceptions do apply) - Refer to NEC 250.24(A)(5) IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 10/25/10 at 12:00 PM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Main Panel vs Sub-Panel and main disconnect? | rbassett | Electrical Inspections | 11 | 10/24/09 6:16 PM |
| Electrical for Dummies | mcyr | Electrical Inspections | 16 | 6/9/08 9:59 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |