Do you note limitations of working spoace when you encounter panels within framed cabinet enclosures?
Joseph P. Hagarty joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member Last edited by jhagarty; 2/18/08 at 4:33 PM.. |
|
#2
|
||||
|
||||
|
Yes. Especially like last Wednesday, when it was in an enclosed space like your photograph...and over a toilet.
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#3
|
||||
|
||||
|
Quote:
Submit your AWARDS NOMINATIONS here Visit the InterNACHI Awards web portal here Blessed are the blissfully ignorant... for they shall be easily led...
|
|
#4
|
||||
|
||||
|
I agree that it's acceptable, so long as the entire cover has the required clearance when the cabinet is opened. You should be unimpeded when removing the cover.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is a depth rule too. Anything within the 30" window in front of the panel should not be beyond the face of the panel. Jim Pauley says you should be able to push a refrigerator box up to the panel and touch the whole cover.
In your case, if that door frame was only an inch or so past the panel I might not get too concerned but it is still a violation. In a practical sense, can you stand close enough without anything in your way to get unimpeded access to everything in there? |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical Inspections | 77 | 5/10/12 6:13 PM |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |