Can a panel box be installed in a laundry room? The panel will be next to the dryer behind the entrance door. When the door is closed the panel will have all required clearances.
|
|
#2
|
||||
|
||||
|
Doesn't seem like a problem from what you described as far as I know. Concerns are bathrooms and closets.
Darrell Hadler CMI Five Star Home Inspections Medicine Hat, AB. Canada NACHI# 04111082 Cell phone# (403)502-3593 Inspected once . . . inspected right!
|
|
#3
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Behind a door is one of the best places for a panel since the door swing preserves the working space.
|
|
#4
|
||||
|
||||
|
Agreed.......I don't have a problem either with the panel in the Laundry room. Usually in that case it is a "Remote Distribution Panel" so make sure all the other issues are taken care of...but as for location not a problem as greg stated.
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#5
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Something to remember:
Panels are permitted in closets. They are not permitted in closets that may have easily ignitable materials. 240.24(D) |
![]() |