Default Panel in living room

200 year old house. The main panel was installed in a "closet" in the living room. Any code against this? I don't know when it was installed, but somewhat recently. It is a 200AMP service. There is no building inspector in the town.

left side of picture

Thanks,
Attached Thumbnails
panel-living-room-img_6466.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 1/19/07, 11:25 PM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 447
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel in living room

Why would it be a problem?
Reply With Quote
  #3  
Old 1/19/07, 11:45 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel in living room

The only issue I see is the door is not 30" wide. I don't really see this as a practical problem since the closet is so shallow but it is a technical violation.

BTW this is exactly how my panel is installed in my bedroom except it is a 32" door. My space is a little deeper/wider and I have wall space around the sides for my cable splitter/amp, telco 66 punch block and network switch along with the Christmas light timer and low voltage lighting controller. I also store batteries and tools on pegboard on the sides. It makes a handy catch all space for your electrical needs.
Reply With Quote
  #4  
Old 1/20/07, 6:58 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Panel in living room

I don't think panels have been allowed in closets in quite some time. Panel covers occasionally become energized, and all those nice, flammable clothes pressed tightly up against an energized panel creates a real nice fire hazard.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #5  
Old 1/20/07, 11:19 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel in living room

This is not a clothes closet as referenced in 240.24(D). It is an electrical closet like what they reference in 110.31. As long as they do not store "easily ignited material" there, it is OK.
Reply With Quote
  #6  
Old 1/20/07, 11:36 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Panel in living room

Quote:
Originally Posted by Greg Fretwell
This is not a clothes closet as referenced in 240.24(D). It is an electrical closet like what they reference in 110.31. As long as they do not store "easily ignited material" there, it is OK.
Might help if I would actually look at the picture, huh?



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #7  
Old 1/20/07, 12:48 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Panel in living room

Howdy,

yes, I would agree this is not going to be under any classification of a clothes Closet, greg is correct in the 30" width as a technical violation.

Now I wish the picture was up closer because It appears the conductors are not secured within 12" of leaving the panel enclosure and so on....could be other issues but as for being in a NON-CLOTHES closet and redefined as an electrical closet...then I dont have a problem with that.....

Now they can make it a BIG problem very fast if they choose to put things in that equipment closet that would force it to NOT be what it is now..

Sometimes in remodels the AHJ's allow slight changes and allowances to certain things...clearances if we are talking about inches...is usually something they will allow....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 1/20/07, 4:29 PM
Scott Falvey Scott Falvey is offline
InterNACHI Member
 
Join Date: May 2005
Location: Newbury, NH
Posts: 393
Default Re: Panel in living room

As requested, here is a closer picture, sorry for not using this one instead. I have noted other issues including the securing within 12". Thanks for the input.
Attached Thumbnails
panel-living-room-img_6471.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #9  
Old 1/20/07, 5:59 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Panel in living room

Yeah....safe to say I see OTHER issues in that situation versus simply harping on the 30" width clearance...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 1/20/07, 11:14 PM
ekartal6 ekartal6 is offline
Active Poster
 
Join Date: Oct 2006
Location: Schaumburg, IL
Posts: 1,107
Please Note: ekartal6 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel in living room

If the less than 30'' W clearnce was the only problem, would you still call it out? There appears to be enough room to access the service equipment.
Reply With Quote
  #11  
Old 1/20/07, 11:15 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,246
Default Re: Panel in living room

Quote:
Originally Posted by ekartal6
If the less than 30'' W clearnce was the only problem, would you still call it out? There appears to be enough room to access the service equipment.
I would, but not in a "universe is collapsing" sort of way.



  • Need a positive networking site? Click here to join Active Rain, a networking community of over 140,000 real estate professionals helping others.

  • NACHI 2005 U.S. Member of the Year
Reply With Quote
  #12  
Old 1/21/07, 12:30 AM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Panel in living room

That bottoms portion looks like R2D2 vomited.

Oh no faceplate on the receptacle box.

tom
Reply With Quote
  #13  
Old 1/21/07, 1:17 AM
ggreene ggreene is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Springhill, Fl
Posts: 163
Default Re: Panel in living room

If This Is The Original Locaton, It May According To Local Custom Be Grandfathered,for Its Location. But The Closet Looks Much Newer! I'd Worry More For Access Than Location.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Where do I put the Aquarium? mcyr Structural 3 11/6/07 4:05 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 1:20 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts