If what is supposed to be a main panel (with a main breaker and bonded neutral conductor) is disconnected by a fused safety switch next to the meter, wouldn't that panel be a sub-panel? I would think it needs the neutrals and grounds separated and not bonded. I must also add that it is fed by SER cable from the fused switch.
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/24/11, 7:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Panel Question

It depends on how it's set up. Do you have a picture?

It may be all part of the service equipment (depending on the connection method, the distance between the switch and the panel, etc.) or it may be separate equipment.

What do you mean by "SER" cable?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 5/24/11, 8:15 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Panel Question

It sounds like to me you just have two disconnects (one outside and one inside).



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
  #4  
Old 5/24/11, 8:37 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

The good news if everything else was done correctly, with the SER type SE cable you probably only need to remove the bonding screw at the sub-panel.
Reply With Quote
  #5  
Old 5/24/11, 8:44 PM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Panel Question

Quote:
Originally Posted by jpope View Post
It depends on how it's set up. Do you have a picture?

It may be all part of the service equipment (depending on the connection method, the distance between the switch and the panel, etc.) or it may be separate equipment.

What do you mean by "SER" cable?
I will dig up a pic. since I am in the middle of the report now. SER meaning a neutral and an equipment ground. In contrast, SEU cable having a helically wound neutral conductor only.
Reply With Quote
  #6  
Old 5/24/11, 8:49 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

Where is the Grounding Electrode Conductor(s) connected?
Reply With Quote
  #7  
Old 5/24/11, 8:55 PM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Panel Question

This is the disconnect, the birds nest of a neutral bus-bar with neutrals and grounds under the same screw, and yes the panel is mounted to the ceiling.
Those are the obvious things. I thought if the disconnect were fused or a breaker, that was considered the main and anything downstream of it was a sub-panel.
Attached Thumbnails
panel-question-dsc06276.jpg   panel-question-dsc06279.jpg   panel-question-dsc06280.jpg  
Reply With Quote
  #8  
Old 5/24/11, 8:57 PM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Panel Question

Quote:
Originally Posted by Robert Meier View Post
Where is the Grounding Electrode Conductor(s) connected?
It is a water pipe grounding conductor out of a trough that is below the meter and disconnect.
Reply With Quote
  #9  
Old 5/25/11, 2:04 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Panel Question

I'm guessing that Robert is asking if the GEC is connected @ the fused switch or the ceiling mounted panel (I haven't typed that too many times) to establish your main and remote panels.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #10  
Old 5/25/11, 8:05 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

Your photo's shed some new light on to this installation. Yes, the EGC's and neutrals should terminate separately in the sub panel. The GEC should go to the fused disconnect neutral and the neutral should be bonded to the enclosure. You said that they ran SER to the subpanel, did they terminate both the neutral and EGC in the feeder to the same bus?
Reply With Quote
  #11  
Old 5/25/11, 10:01 AM
James A. Levy's Avatar
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 2,772
Default Re: Panel Question

Quote:
Originally Posted by Robert Meier View Post
Your photo's shed some new light on to this installation. Yes, the EGC's and neutrals should terminate separately in the sub panel. The GEC should go to the fused disconnect neutral and the neutral should be bonded to the enclosure. You said that they ran SER to the subpanel, did they terminate both the neutral and EGC in the feeder to the same bus?
Yes they terminated on the same bus as if it were a main panel. That was why I questioned myself on that one.

In my report, I went with my gut feeling and called out improper installation and that the neutrals and grounds needed to be separated and not bonded to the panel.

Thanks for the info.

Drew
Reply With Quote
  #12  
Old 5/26/11, 8:58 AM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Panel Question

Quote:
Originally Posted by jlevy1 View Post
If what is supposed to be a main panel (with a main breaker and bonded neutral conductor) is disconnected by a fused safety switch next to the meter, wouldn't that panel be a sub-panel? I would think it needs the neutrals and grounds separated and not bonded. I must also add that it is fed by SER cable from the fused switch.
James,

The fused safety-switch is the service panel. The downstream panel is a distribution panel (aka sub-panel) and should be wired accordingly. SER is OK. Having a main breaker in the distribution panel is OK too.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #13  
Old 5/30/11, 10:56 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Panel Question

Quote:
Originally Posted by gwells View Post
The fused safety-switch is the service panel ...
I think you mean "service equipment" ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Need a home inspection in Montana? Check out InterNACHI's listing of Montana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/30/11, 11:51 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

Quote:
Originally Posted by roconnor View Post
I think you mean "service equipment" ...

And also the service disconnect.
Reply With Quote
  #15  
Old 5/30/11, 1:20 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Panel Question

Okay I am learning something new because it is not being done in my area, but it would not surprise me it is wrong because our electricians and code officials are mainly hillbillies.
So if there was a main outside breaker at the meter before it goes into the panel inside the house, the panel needs to be treated as a sub-panel?



Braun Inspection Consultants
Serving Jefferson City, Columbia, Sedalia, Fulton and Lake of the Ozarks
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Another bonding of service panel question? mthiltgen Electrical Inspections 9 3/4/10 6:41 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Panel Question bsmith Electrical Inspections 11 5/27/09 9:59 PM
Panel wiring question dmacy Electrical Inspections 12 2/2/09 8:38 PM


All times are GMT -4. The time now is 9:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts