Panel had a 60 amp main breaker, two outlet and switch breakers and one 50 Amp AC breaker.

Question: Would you find this supply and the amount of breakers sufficient for a 1500 sq ft home?
Reply With Quote
  #2  
Old 10/6/06, 2:20 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

not to today's standards
Reply With Quote
  #3  
Old 10/6/06, 3:10 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

60a may be plenty for the general lighting and other 120v loads in a 1500 sq/ft house. 4500va for the GL, 4500 for the kitchen and laundry, 37.5a.
The 50a breaker indicates this is probably a split bus panel.
Are the other utilities gas or oil (hot water, furnace stove).
Reply With Quote
  #4  
Old 10/6/06, 4:35 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

I agree with Greg.
The original question is pretty vague, and the first rely is very vague.
There is much that is not known here.
Reply With Quote
  #5  
Old 10/6/06, 5:26 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel Question

Personally......I say while it is Vague....I say a 60a panel is not going to properly ( it will TECHNICALLY...but ) a 1,500 sq ft dwelling because in doing so it tells me the plugs will be loaded with Extention Cords and Adapters and no room for expansion. and as greg stated it has more to do with other issues...

We are not speaking to electricians here.....so your duty is to make sure the client is AWARE of future expenses...not if the current panel will serve the 1,500 Sq Ft Dwelling....as it obviously does.....right now and will continue to until which point additions are made and that is the statement you would need to make them aware of and let them know the facts.

1.) 4,500VA GL
2.) 4,500VA Kitchen/Laundry ( at minimum )
3.) 8,000 VA Range ( Since we just dont know...which they have )


Minimum Size Feeder Required


[see 220.10]


General Lighting 4500 VA
Small Appliance 3000 VA*
Laundry 1500 VA*
Total 9000 VA
3000 VA at 100% 3000 VA
9000 VA

3000 VA = 6000 VA at 35% 2100 VA
Net Load 5100 VA
Range
(see Table 220.19) 8000 VA

Net Computed Load 13,100 VA

13,100 (divided by ) 240 = 54.58 AMPS

* This is just so you know what it would be IF you had a Kitchen and Laundry to consider...which you do not in your question


Now while MY response may also be vague.......you can see the basics of the setup.......here is your question....

Now on the GL Receptacle thing...as Greg stated if the house has only (2) breakers they would for one need to be 20A breakers.....otherwise based on that size (3) 15A would be required. See below...


General Lighting Load: 4500 VA



÷ 120 V = 37.5 A

This requires three 15-A, 2-wire or two 20-A, 2-wire circuits.

Hope this helps....but as a HI you need to make the buyer aware of the most important thing and it has nothing to do with us electricians telling you if it will run a 1,500 dwelling........it is YOUR job as a HI to inform them that while it may have been fine at one point and it MAY handle the demands placed on it right now.......do you plan on expanding, adding anything, using any computers, how about AC units or upgrades in the future....

You must make them aware of what they are buying and that is has limitations to future expansion.

Plus that accounts for your (2) breakers.....meaning chances are the kitchen may be upgraded at some point.......a person buying the home will want to know WHAT they will expect in the future.

This is where your job is important...to make them aware of the known capacity and what will be needed in the future to meet upgrades or desires......thats why you do not have to calculate panel sizes.....your job is clear......if at ANY point they choose to upgrade they need to know about their possible future expenses associated with this purchase...NOT is the service large enough for NOW....might be......and is based on the INFO you gave...but not to todays standards or practicle standards if they plan on buying it and adding anything later.







Paul W. Abernathy

Last edited by pabernathy; 10/6/06 at 5:31 PM..
Reply With Quote
  #6  
Old 10/6/06, 5:47 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

Today's requirements would call for a 100 ampere service.

One-Family Dwelling.
For a one-family dwelling, the service disconnecting means shall have a rating of not less than 100 amperes, 3-wire.


Reply With Quote
  #7  
Old 10/6/06, 6:21 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel Question

while todays WOULD.....the question is on a house that obviously does not meet that 100A TODAYS requirement. I am sure at the time the house was built the 60A was allowed and this done.

Read my statement tim..it will explain what you should say to the client and how you should say it..as a HI...not a Electrician.



Paul W. Abernathy
Reply With Quote
  #8  
Old 10/6/06, 6:30 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel Question

P.S....what I was saying is..it is a diplomatic way of saying the following:

"Hey Dude...while this panel may run the house now...are you going to STAY in the stone ages or plan on coming into the 21st century while in this house."

Ahh...but without kinda saying it like that........



Paul W. Abernathy
Reply With Quote
  #9  
Old 10/6/06, 6:47 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

The 60 ampere service may be just fine, and if the following was considered the "dude and dudess or dude" would be happy:

Insert picture of Jolly Fat dude Here!

220.87 Determining Existing Loads.
The calculation of a feeder or service load for existing installations shall be permitted to use actual maximum demand to determine the existing load under all of the following conditions:

(1) The maximum demand data is available for a 1-year period.

Exception: If the maximum demand data for a 1-year period is not available, the calculated load shall be permitted to be based on the maximum demand (measure of average power demand over a 15-minute period) continuously recorded over a minimum 30-day period using a recording ammeter or power meter connected to the highest loaded phase of the feeder or service, based on the initial loading at the start of the recording. The recording shall reflect the maximum demand of the feeder or service by being taken when the building or space is occupied and shall include by measurement or calculation the larger of the heating or cooling equipment load, and other loads that may be periodic in nature due to seasonal or similar conditions.
Reply With Quote
  #10  
Old 10/6/06, 7:47 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel Question

Quote:
Originally Posted by jtedesco1

Insert picture of Jolly Fat dude Here!

Someone insert a PIC of me ..I will play the Jolly Fat Dude tonight !



Paul W. Abernathy
Reply With Quote
  #11  
Old 10/6/06, 7:49 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel Question

Quote:
Originally Posted by jtedesco1
If the maximum demand data for a 1-year period is not available, the calculated load shall be permitted to be based on the maximum demand (measure of average power demand over a 15-minute period) continuously recorded over a minimum 30-day period using a recording ammeter or power meter connected to the highest loaded phase of the feeder or service, based on the initial loading at the start of the recording. The recording shall reflect the maximum demand of the feeder or service by being taken when the building or space is occupied and shall include by measurement or calculation the larger of the heating or cooling equipment load, and other loads that may be periodic in nature due to seasonal or similar conditions.


Yeah.......I can see the homeowner doing this...lol......NOT!...



Paul W. Abernathy
Reply With Quote
  #12  
Old 10/7/06, 12:14 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

The 60a "main" and the 50a "A/C" breaker had me thinking "Split Bus" and that it was probably 100a.
I guess it is better to ask more questions than to assume ... sorry for the confusion.
Reply With Quote
  #13  
Old 10/7/06, 12:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel Question

No greg.....you did not assume...you were being a GREAT electrician.....

As you probably agree it would be rare to see a circuit breaker panel with a 60A main breaker....yet still have (2) other breakers and a (1) 50A breaker...so I can see totally where you are going on that.

Just dont think a split buss design would be in that type of format layout the way they describe it....but you are 100% right in that if they could show a picture or even give the SEC conductor size it would HELP....



Paul W. Abernathy
Reply With Quote
  #14  
Old 10/7/06, 1:01 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Question

If a house really pulled 60a 24/7 they would have a $1000 electric bill so we really have to assume some diversity.
Reply With Quote
  #15  
Old 10/7/06, 1:25 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel Question

We can assume that.....but the question is should the HI inform them of the obvious.....since their job is to inform them of upcoming expenses when buying a home......and my opinion would be if they are buying for the future...be aware of upgrade and additional circuit needs...

Unless they plan on doing NOTHING and living in the stone ages for the next who knows how many years.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Service Panel question for board sparkies pbolliger Electrical Inspections 8 5/14/06 9:24 AM


All times are GMT -4. The time now is 4:02 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts