Default Panel question at REO inspection today

Looking for feedback. See any issues? Other than the opening in the picture with the cover installed. I'm curious about the 14GA wire feeding the double 20A breakers near the bottom, marked pool filter. There was no GFCI (or disconnect at all) near the pool equipment.
Attached Thumbnails
panel-question-reo-inspection-today-pict0110.jpg   panel-question-reo-inspection-today-pict0111.jpg   panel-question-reo-inspection-today-pict0113.jpg  



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.
Reply With Quote
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 6/12/10, 8:30 AM
wsiegel wsiegel is online now
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel question at REO inspection today

# 14 in on a 20 amp breaker is wrong. Also looks like you have two neutrals under one screw. Are those multiple aluminum grounds all under one screw??
Reply With Quote
  #3  
Old 6/12/10, 9:18 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel question at REO inspection today

There was a period of time when GFCI protection was not required for hardwired pool pump motor's. This requirement was reinstated in the 2008 NEC. Also I believe that a hardwired pump may have an OCPD larger than the conductor size due to starting current compensation, as with other motors covered under Article 430 of the NEC. A thermally protected pump would use the OCPD to provided short circuit and ground fault protection, but not overload protection.
Reply With Quote
  #4  
Old 6/12/10, 9:30 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel question at REO inspection today

Thanks for thinking the same thing I was about the conductors to the motor load. I scanned this and then got some coffee while I thought about this and you posted in the mean time.
Reply With Quote
  #5  
Old 6/12/10, 9:35 AM
Darin Redding's Avatar
Darin Redding Darin Redding is offline
InterNACHI Member
 
Join Date: Jan 2010
Location: San Diego, CA
Posts: 485
Default Re: Panel question at REO inspection today

Quote:
Also looks like you have two neutrals under one screw.
Sure looks that way in the picture, but I looked specifically for that condition and didn't find any.
Quote:
Are those multiple aluminum grounds all under one screw??
Yes.



Darin Redding, CPI
Housecall Property Inspections
san diego home inspection
rental inspection | warranty inspection
Facebook Like
darin@sandiegohomeinspect.com
619-663-8740
home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista.

Last edited by dredding; 6/12/10 at 9:39 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 9:59 PM
Panel Surround / Exposed Wiring Question thance Electrical Inspections 11 2/19/08 9:06 PM
Panel Question thejnicki Electrical Inspections 18 10/7/06 1:07 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts