#1
|
||||
|
||||
|
Looking for feedback. See any issues? Other than the opening in the picture with the cover installed. I'm curious about the 14GA wire feeding the double 20A breakers near the bottom, marked pool filter. There was no GFCI (or disconnect at all) near the pool equipment.
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. |
| Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
# 14 in on a 20 amp breaker is wrong. Also looks like you have two neutrals under one screw. Are those multiple aluminum grounds all under one screw??
|
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
There was a period of time when GFCI protection was not required for hardwired pool pump motor's. This requirement was reinstated in the 2008 NEC. Also I believe that a hardwired pump may have an OCPD larger than the conductor size due to starting current compensation, as with other motors covered under Article 430 of the NEC. A thermally protected pump would use the OCPD to provided short circuit and ground fault protection, but not overload protection.
|
|
#4
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks for thinking the same thing I was about the conductors to the motor load. I scanned this and then got some coffee while I thought about this and you posted in the mean time.
|
|
#5
|
||||
|
||||
|
Quote:
Quote:
Darin Redding, CPI Housecall Property Inspections san diego home inspection rental inspection | warranty inspection Facebook Like darin@sandiegohomeinspect.com 619-663-8740 home inspector in San Diego, Carlsbad, Poway, La Mesa, El Cajon, Chula Vista. Last edited by dredding; 6/12/10 at 9:39 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Main panel...recommendation ? | dnasser | Electrical Inspections | 6 | 11/22/09 9:55 PM |
| Electrical for Dummies | mcyr | Electrical Inspections | 16 | 6/9/08 9:59 PM |
| Panel Surround / Exposed Wiring Question | thance | Electrical Inspections | 11 | 2/19/08 9:06 PM |
| Panel Question | thejnicki | Electrical Inspections | 18 | 10/7/06 1:07 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |