Default Panel screw hits a live wire

While replacing the cover on this panel, the upper right screw came in contact with a 10 ga line. Lots of sparks! Don't rember having time to jump. Stirred by not shaken.
Attached Thumbnails
panel-screw-hits-live-wire-panel.jpg  
Reply With Quote
  #2  
Old 3/29/06, 7:51 PM
phinsperger's Avatar
phinsperger phinsperger is offline
Active Poster
 
Join Date: Dec 2003
Location: Orangeville, ON
Posts: 1,836
Please Note: phinsperger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel screw hits a live wire

Thank God you're all right.
Reply With Quote
  #3  
Old 3/29/06, 7:55 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Panel screw hits a live wire

Yes, I'm glad you're okay too.

Was the insulation compromised?..not a pointy screw I hope.
Reply With Quote
  #4  
Old 3/29/06, 8:06 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Panel screw hits a live wire

Hi Ray,

Glad you're OK, and the underwear will come clean after a couple of hot washes

This is a timely reminder to members to wear safety glasses when inspecting panels, the real hazard from these incidents is not just the risk of a shock but also eye injury from the arc flash.

Be safe

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #5  
Old 3/29/06, 8:22 PM
Doug Edwards's Avatar
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,846
Default Re: Panel screw hits a live wire

One thing I consciously check now days is the proximity of any of the interior wiring when I take a panel cover off. I find many times someone has replaced a misplaced screw with a drywall screw, a sheet metal screw or a wood screw. I carry a few extra panel screws in my truck so I do not have to use the pointed screws to replace a panel cover. If I find a wire directly behind the screw hole in the panel box I gingerly move it out of the line with the screws. Got a scare a few years back so I am very much aware of this now. Glad to hear you didn't get zapped.
Reply With Quote
  #6  
Old 3/29/06, 8:43 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Panel screw hits a live wire

Glad to hear your OK. I suppose you were wearing the proper PPE for opening a HOT panel.... Right?


At the very least, wear some good gloves and some eye protection.
Reply With Quote
  #7  
Old 3/30/06, 4:49 AM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel screw hits a live wire

Thanks for the concern, believe me its not the first time. Just out of interest the panel cover screws were the correct screws. When I put the screw in I felt a little resistance, thinking it was a rusted screw or thread. Turns out to be the wire interferring with the screw.

Most all the fuses in panel were over fused. These were all "delay" fuses most of them 25 amp on 14 ga.

A couple of years ago while putting a cover back on and putting the screw in I got a shock. The panel was in the bathroom of a restaurant.

A reminder for everyone to pay attention when dealing with electricity.

Thanks.
Reply With Quote
  #8  
Old 3/30/06, 12:49 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel screw hits a live wire

"First, do no harm".
When you start taking things apart you have some responsibility to get them back together without blowing anything up. I get a little nervous when folks of varying qualifications start poking around in service panels. Education is the key. Perhaps NACHI should have a certification protocol for what you do and what you look for before you can open these things.
Reply With Quote
  #9  
Old 3/30/06, 1:08 PM
dbush's Avatar
dbush dbush is offline
Active Poster
 
Join Date: Dec 2002
Location: Joplin, MO
Posts: 243
Send a message via MSN to dbush Send a message via Yahoo to dbush
Please Note: dbush is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel screw hits a live wire

I came across a first the other day. Panel cover was NAILED in. I refused to take them out. Told the listing agent that IF the seller wanted to have the nails removed, I would then inspect the panel but I WOULD not under any circumstances renail the panel cover on. After inspection, the cover was the least of the worries. I figure I saved the electrician a step, because he doesn't have to fix the cover when he fixes all the screw ups inside.
Reply With Quote
  #10  
Old 3/30/06, 8:29 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Panel screw hits a live wire

Quote:
Originally Posted by Greg Fretwell
When you start taking things apart you have some responsibility to get them back together without blowing anything up. I get a little nervous when folks of varying qualifications start poking around in service panels. Education is the key.
Agree completely ...

And in addition to the other suggestions, make sure ya use insulated electricians screwdrivers when you are anywhere near live panels/wires, to help make sure you dont go "live" also if something bad does happen (like the Gardner Bender GS-83 set for about $5 at lowes.com ... pretty cheap potential life saver ... )

Take a look at this topic I started a while back too ... http://www.nachi.org/bbsystem/viewtopic.php?t=1665

And keep in mind If you are not sure what you are doing or something doesn’t look right, bail to an electrician. It is okay to note in you report ... "full electrical panel inspection appeared unsafe ... it is recommend that a licensed electrician inspect the panel".

JMO & 2-nickels ... and stay SAFE ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #11  
Old 3/30/06, 8:35 PM
John Onofrey's Avatar
John Onofrey John Onofrey is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Richmond, TX
Posts: 4,659
Default Re: Panel screw hits a live wire

Quote:
Originally Posted by rwand1
A couple of years ago while putting a cover back on and putting the screw in I got a shock. The panel was in the bathroom of a restaurant.
I believe that here in the States, A bathroom is a prohibited location for a service panel.



John Onofrey Licensed Professional Inspector
Houston Home Inspection
Houston Home Inspector
www.texasinspectors.net

John Onofrey
President, Grail Media, LLC
"Effortless Email Marketing"
www.homehintsenews.com
2007 INACHI Inventions and Innovations Award Winner
Free! Inspector Email Marketing trial click here
Reply With Quote
  #12  
Old 3/31/06, 10:01 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Angry Re: Panel screw hits a live wire

Panel bonding....
I am always concerned about "return" paths especially since it could be me

Why don't the equipment Mfg's use service panel "hangers" anymore? You know the kind that can hold a dead front in position so you can screw the darn thing on without holding it in one hand and using the other to turn the screws!
Reply With Quote
  #13  
Old 3/31/06, 12:07 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Panel screw hits a live wire

I believe at the show I am doing in OHIO I will go into alot of extra detail about things like this.....maybe those people at the show can get some NACHI certification for attending....



Paul W. Abernathy
Reply With Quote
  #14  
Old 3/31/06, 12:18 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel screw hits a live wire

John said..
I believe that here in the States, A bathroom is a prohibited location for a service panel.

Yes I think that is the same here.
Reply With Quote
  #15  
Old 4/1/06, 7:32 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Panel screw hits a live wire

Quote:
Originally Posted by roconnor
Agree completely ...

And in addition to the other suggestions, make sure ya use insulated electricians screwdrivers when you are anywhere near live panels/wires
Hi Rob
I've never seen the need for using a screwdriver with an insulated blade if all you are using it for is to remove/install panel screws. Cordless rechargeable screwdrivers make life so much easier. Mine gets put on the floor beside the panel cover and doesn't get picked up again until the panel cover gets reinstalled.
</IMG>
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:02 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts