Default Panel Size

This is a Murray split panel installed in 1982. The middle breaker on the right is 60 amps and feeds the lower section labeled sub panel. The two breakers at the top are for the Range and HVAC. As you can see, 5 throws will kill the power but I don't know what the panel is rated at.
Attached Images
File Type: jpg Kenny.JPG (134.4 KB, 28 views)
File Type: jpg Kenny1.JPG (89.1 KB, 24 views)
File Type: jpg kenny2.JPG (106.9 KB, 28 views)
Reply With Quote
  #2  
Old 10/7/08, 5:58 PM
Gerry Beaumont's Avatar
Gerry Beaumont Gerry Beaumont is online now
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 5,208
Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute Gerry Beaumont has a reputation beyond repute
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Panel Size

Hi Gary,

without the UL listing information it is hard to tell, however, given its physical size and capacity I doubt that it was rated for less than 125-150 amps.

What size was the SEC?

Regards

Gerry



Virtue is more to be feared than vice, because its excesses are not subject to the regulation of conscience.
Adam Smith (1723-1790)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106
Reply With Quote
  #3  
Old 10/7/08, 6:54 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,897
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel Size

Can you read the size of the conductors going to the main lugs? That will give you a pretty good clue, in your case.
Reply With Quote
  #4  
Old 10/7/08, 8:51 PM
Gary T. Heller's Avatar
Gary T. Heller Gary T. Heller is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Peoria, AZ
Posts: 188
Gary T. Heller is often very helpful Gary T. Heller is often very helpful
Default Re: Panel Size

Thanks Jerry and Marc. I did not read them because at a glance the SEC looked sufficient. I have to go back when the power is on to finish the inspection. If the conductors are #2 copper would you call the panel out as 125 amp? The panel has no tags.
Reply With Quote
  #5  
Old 10/7/08, 10:18 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 6,937
Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information Paul W. Abernathy is very trusted source of information
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Panel Size

Is it just me but that looks larger than that....let me zoom in on the letters....


Ok.......I zoomed in on the image and you are not going to believe this but it appears to be....yes hold your mouth fellas.....250 MCM Compact I believe( old back before they started calling it KCMil )


Ok...here is what I believe.........are you ready.

They ran 250 AL MCM ( KcMil ) and they had no idea of 310.15(B)(6)....so they used 310.16 and 250 AL MCM ( KcMil) at 75 degree's is good for 205A...and based on the size of the meter ( dont always use it but remember my video...it can assist you in sizing for confirmation )....I believe this to be a 200A panel......

I could be wrong....but thats my opinion based on wat i see....
Attached Images
File Type: jpg Kenny2.jpg (17.0 KB, 41 views)



Paul W. Abernathy,CMI,CEI,CEPE
Electrical Plans Examiner/Engineer I
NEC Code Expert & Consultant

- ICC & IAEI Certified Electrical Inspector
- DHCD Virginia Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- DHCD Virginia Certified Electrical Plans Examiner
- DPOR Virginia CE Provider - Electricians
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

P.S. Check me out on Mike Holts 2008 Exam Prep DVD Series.

Last edited by pabernathy; 10/7/08 at 10:29 PM.
Reply With Quote
  #6  
Old 10/7/08, 10:20 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 4,200
Larry D. Kage .
Default Re: Panel Size

Gary, your glasses can't protect your eyes from on top of the meter base...



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical for Dummies mcyr Electrical 16 6/9/08 10:59 PM
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:47 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics