Default Panel wire questions

OK ill admit electrical is not my strong point. My question is they installed a new heat pump and in the panel they have larger lines spliced to smaller lines going into a 20amp breaker. Is this OK


panel-wire-questions-dscf4025.jpg

panel-wire-questions-dscf4026.jpg

panel-wire-questions-dscf4027.jpg
Reply With Quote
Need a home inspection in Alaska? Check out InterNACHI's listing of Alaska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/7/11, 10:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Panel wire questions

As long as the minimum ampacity rating of the heat-pump can be adequately served by the smaller conductors, it's good. The data plate will give you the circuit rating.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 5/7/11, 10:57 PM
Philip J. Cavalcante Philip J. Cavalcante is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Callaway, Md
Posts: 246
Default Re: Panel wire questions

I did that and its fine just never seen that large of a reduction in line size. Thanks as always
Reply With Quote
  #4  
Old 5/8/11, 7:25 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel wire questions

Given the amount of tape that they used I would wonder how that actually spliced those two conductors together. It appears that the smaller conductor has been taped black. If it was originally white then that's a problem. Also the two lugs on the neutral bar behind the breaker in question (photo #2) are probably not the type required to terminate on the neutral bar.
Reply With Quote
  #5  
Old 5/8/11, 1:48 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Panel wire questions

Quote:
Originally Posted by Robert Meier View Post
Given the amount of tape that they used I would wonder how that actually spliced those two conductors together. It appears that the smaller conductor has been taped black. If it was originally white then that's a problem. Also the two lugs on the neutral bar behind the breaker in question (photo #2) are probably not the type required to terminate on the neutral bar.
As Robert said, the splice doesn't look right and the lugs on the grounded bus are not right. In addition to the amount of tape, the tape was not correctly applied. The only acceptable type of connection in this instance is a compression connector.

The lug on the grounded bus is on top of another screw head. There is a serious risk of a loss of neutral. Loss of neutral is a leading cause of electrical fires. That is a much more serious deficiency than the tap on the ungrounded conductors.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #6  
Old 5/9/11, 9:32 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel wire questions

I agree with Robert and George that the lugs are not the correct ones that should have been used. However, since the heat pump is straight 240V that would be the grounding conductor, not the neutral.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel..... ground wire question dnasser Electrical Inspections 4 7/11/10 1:15 AM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Panel Questions - main, mid, sub lfoster Electrical Inspections 6 11/11/08 9:42 PM
Need help understanding panel dokeefe Electrical Inspections 7 10/27/08 9:23 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:16 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts