Default Panel wiring question

Home has a 200 amp FPE main panel. There were a few concerns with the main panel as it was an FPE, had open cover knockout at cover, double tap, low voltage transformer in panel, open knock outs and over crowded wiring and a few other issues as well.

There was a 100 amp sub panel connected and what I have never seen before is they connected all the neutral ground connections in the main and just ran the hot to the sub breakers. One reason for the over crowded wiring. The had all the neutrals and grounds separated in the main.

I referred both panels to a sparky as I would replace the FPE and leave it to the electrician if he is going to use the sub or just add one larger main panel box.

What are your thoughts on the wiring to the sub panel? Is blue an acceptable wire color to use?
Attached Thumbnails
panel-wiring-question-131709-085-small-.jpg.jpg
Views:	138
Size:	71.3 KB
ID:	26597   panel-wiring-question-131709-080-small-.jpg.jpg
Views:	148
Size:	66.9 KB
ID:	26598   panel-wiring-question-131709-087-small-.jpg.jpg
Views:	183
Size:	75.5 KB
ID:	26599  
Reply With Quote
  #2  
Old 1/31/09, 4:14 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Panel wiring question

As far as the FPE panel,

"The FPE Stab-Lok panel is considered a safety hazard. Hazards associated with this manufacturer have been documented by industry experts. A high percentage of FPE Stab-Lok breakers have failed to open under over-current conditions. Replacement is advised for safety reasons. At the minimum, the panel should be thoroughly inspected and deemed acceptable by a competent licensed electrician familiar with this type of panel . (See http://www.aohomeinspection.com/resources.htm and other documents for details of hazards.)"

Done.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 1/31/09, 4:26 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Panel wiring question

Working link HERE



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #4  
Old 1/31/09, 4:29 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Panel wiring question

Do you guys actually read the freaking question/post. I know about the FPE. Thats not waht I asked about.
Reply With Quote
  #5  
Old 1/31/09, 4:32 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Panel wiring question

Quote:
Originally Posted by dmacy View Post
Do you guys actually read the freaking question/post. I know about the FPE. Thats not waht I asked about.
My apolgies David. I did not read to the end.

There is no problem with the blue wire and wire nuts in the panel.

Light blue does happen to be the color reserved for "earthed conductor" in Europe but your not there.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI


Last edited by mlarson; 1/31/09 at 4:37 PM..
Reply With Quote
  #6  
Old 1/31/09, 4:35 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Panel wiring question

Thanks

Why would they make all the connections in the main? Seems way overcrowded.
Reply With Quote
  #7  
Old 1/31/09, 4:39 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Panel wiring question

Quote:
Originally Posted by dmacy View Post
Thanks

Why would they make all the connections in the main? Seems way overcrowded.
Looking at the old cloth wiring on the right, I assume that the FPE panel is not original to the home.

Pretty typical to extend those old wire runs in that manner.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #8  
Old 1/31/09, 4:44 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Panel wiring question

Is that exposed wire coming out of the 2nd and third 20 amper from the top left side?

Looks like someone just sniped off the conductors.
Reply With Quote
  #9  
Old 1/31/09, 4:48 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: NE. OH
Posts: 2,658
Default Re: Panel wiring question

Yes they were sniped away. FPE panel would be original. House is 25 years old.
Reply With Quote
  #10  
Old 1/31/09, 8:46 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Panel wiring question

Quote:
Originally Posted by dmacy View Post
...What are your thoughts on the wiring to the sub panel? Is blue an acceptable wire color to use?
My notes to myself in my language.

Color Function
============================
Black: Hot wire
Red: Hot wire
Blue: Hot wire
White code black: Hot wire
White: Neutral wire
Green : Grounding wire
Green and yellow: Grounding wire
Bare copper: Grounding wire



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 1/31/09, 8:47 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Panel wiring question

Quote:
Originally Posted by dmacy View Post
Thanks

Why would they make all the connections in the main? Seems way overcrowded.
OK, you referred the main to Sparky because it was an FPE. Who cares about the crowding issue. If they replace it, as I assume you recommend, the issue of overcrowding is not an issue.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #12  
Old 2/1/09, 12:34 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Panel wiring question

Quote:
Originally Posted by dmacy View Post
What are your thoughts on the wiring to the sub panel? Is blue an acceptable wire color to use?
You betcha. Any color but green or white is fair game to use as a hot conductor.

The crowding is not even remotely close to being a problem. You're allowed 75% gutter fill, which is loosely defined as the number of conductors you can bash back in there with the butt of your hammer and still get the cover on.
Reply With Quote
  #13  
Old 2/2/09, 8:38 PM
Bill Smith's Avatar
Bill Smith Bill Smith is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: East Northport, NY
Posts: 1,043
Default Re: Panel wiring question

Quote:
Originally Posted by Marc D. Shunk View Post
You're allowed 75% gutter fill, which is loosely defined as the number of conductors you can bash back in there with the butt of your hammer and still get the cover on.
That gave me a chuckle!



"A man cannot be truly grateful and remain unhappy"
http://www.SmithHomeInspection.com
SmithHomeInspection@yahoo.com
NY State Lic. # 16000008304
631-434-5200
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sub panel question smcintire Electrical Inspections 9 7/13/08 12:55 AM
Panel Question rnewman1 Electrical Inspections 2 12/13/07 2:01 PM
Panel Question gmckenzie Electrical Inspections 9 8/24/07 1:25 AM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM