Default Paper tags inside the panel !!?

I opened a 100 amp distribution panel to find paper tags attached to conductors with string. I've never seen this before, but I don't like the idea. I'm telling the client to have them removed, but am I supported by any documentation?
Attached Thumbnails
paper-tags-inside-panel-naugle-035a.jpg  
Reply With Quote
  #2  
Old 9/25/06, 2:13 PM
nwagner's Avatar
nwagner nwagner is offline
InterNACHI Member
 
Join Date: May 2006
Location: Baraboo, WI
Posts: 2,948
Default Re: Paper tags inside the panel !!?

You're definately supported by common sense. I'll leave the NEC referencing the regulars...
Reply With Quote
  #3  
Old 9/25/06, 2:44 PM
gmathias gmathias is offline
New User
 
Join Date: Aug 2004
Location: Lewisburg, PA
Posts: 64
Please Note: gmathias is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Paper tags inside the panel !!?

Thanks
Reply With Quote
  #4  
Old 9/25/06, 3:32 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Paper tags inside the panel !!?

That is very common with panels of that era. I think for the small amount of paper present there is no problem with it.
I think a lot of the more "commercial" guys did that back in the day.
Hey, at least the circuits are identified.

Also, that panel is extremely clean. The wiring could be straightened up a bit, but the panel itself is spotelss.

**Edit- Looking back at the pic I think the panel is newer than I originally thought. Must have been an old timer who did it. No one uses those tags any more.

**second edit- typo**

Last edited by Speedy Petey; 9/25/06 at 8:52 PM..
Reply With Quote
  #5  
Old 9/25/06, 5:46 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Paper tags inside the panel !!?

Double tapped Neutrals.
Reply With Quote
  #6  
Old 9/25/06, 5:59 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Paper tags inside the panel !!?

The big question is does it pose an electrical or safety problem. Personally, I wouldn't call it out. Normally, what I see is that electricans use scrap pieces of the romex exterioral shealthing to label the individuall cable runs.
Reply With Quote
  #7  
Old 9/25/06, 8:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Paper tags inside the panel !!?

Quote:
Originally Posted by dchew
The big question is does it pose an electrical or safety problem.
You could say that, but I'd disagree.

These paper tags are certainly not "listed components." At the very least, should be reported as such, whether you feel they pose a hazard or not.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 9/25/06, 8:50 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Paper tags inside the panel !!?

Jeff, we are typically on the same page but I gotta part with you here.

There is no restriction as to how much sheathing we leave on NM cable inside the panel. Only a minimum length.
There is quite a bit of paper in NM cable and I have seen some guys leave 6"+ sheathing so they can write on it.
That is no less of an issue than we have here.

You guys would really put this in a report?
Reply With Quote
  #9  
Old 9/25/06, 9:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Paper tags inside the panel !!?

I understand where you're coming from Pete, but this is one of those situations (again) where the electrical "expert" has the latitude to call this "acceptable," where (IMHO) the HI does not.

The paper inside NM is part of a listed component, these tags are not.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 9/25/06, 9:11 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Paper tags inside the panel !!?

Quote:
Originally Posted by Speedy Petey
Jeff, we are typically on the same page but I gotta part with you here.

There is no restriction as to how much sheathing we leave on NM cable inside the panel. Only a minimum length.
There is quite a bit of paper in NM cable and I have seen some guys leave 6"+ sheathing so they can write on it.
That is no less of an issue than we have here.

You guys would really put this in a report?
I agree I would not even consider calling this .
How many cables have we put on tags and plasic markers .
Most control panels have lots of prints left in them.
Roy Cooke
Reply With Quote
  #11  
Old 9/25/06, 9:18 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Paper tags inside the panel !!?

Quote:
Originally Posted by Speedy Petey

You guys would really put this in a report?
I wouldn't.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #12  
Old 9/25/06, 9:25 PM
Andrew Shick's Avatar
Andrew Shick Andrew Shick is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Grain Valley, MO
Posts: 633
Default Re: Paper tags inside the panel !!?

Quote:
Originally Posted by Speedy Petey
You guys would really put this in a report?
Nope.
Reply With Quote
  #13  
Old 9/25/06, 9:29 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Paper tags inside the panel !!?

Quote:
Originally Posted by Speedy Petey
You guys would really put this in a report?
No, I wouldn't.
Sorry Jeff we just don't see eye to eye on this one.
Reply With Quote
  #14  
Old 9/25/06, 11:15 PM
gmathias gmathias is offline
New User
 
Join Date: Aug 2004
Location: Lewisburg, PA
Posts: 64
Please Note: gmathias is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Paper tags inside the panel !!?

Thanks for your "spirited" input. I understand (I think) the black and white of this. I've suggested that they have the paper tags removed as the breakers are labeled on the inside of the panel cover door.
Reply With Quote
  #15  
Old 9/27/06, 10:39 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Paper tags inside the panel !!?

I've been in Vegas and haven't been visiting the board much

Quote:
Originally Posted by mlarson
No, I wouldn't.
Sorry Jeff we just don't see eye to eye on this one.
That's okay.

This condition would not warrant a "needed" correction necessarily, but I wouldn't consider it a "non-issue."

At the very least, I would have reported the presence of the tags. After that, I'm not sure where I would have gone with it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Service panel full of paper tags gwilcox Electrical Inspections 5 8/17/07 6:55 AM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 9:16 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts