Default Person electrocuted by energized metal in a building

http://www.local6.com/money/7302637/detail.html

How can this video be saved?
Reply With Quote
  #2  
Old 2/22/06, 1:16 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

Maybe you can email channel 6 for it. This is buried in a java script that is giving me an error when I try to open it.

This incident only reinforces the question of why they don't require bonding steel framing. In a commercial job it gets bonded via all the metal boxes and raceways but in residential there is not going to be much metal.

I didn't see the deail on this particular accident but my guess is he was holding a metal dryer vent pipe in one hand and touched the "hot" vent box in the wall.
Personally I think they should be bonding every isolated section of metal framing. That could be as simple as using a metal box, fastened with a nut and bolt to the steel, bonding via the egc.
Reply With Quote
  #3  
Old 2/22/06, 1:21 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

I'm not familiar with huge developments of tract homes. Haven't seen any metal studs and framing used around here. What is the standard procedure for grounding the framing? Is the framing solid enough to be effectively grounded at all points if the attachment to the grounding electrode system is only one point? Is the method of attachment just a mechanical lug? I assume there are rules for tying this framing in to the grounding system, I haven't had the need to look it up, though my journeyman license is up for renewal and I need some cont. ed credits so I think I'll make a point of looking this up during my studying.
Reply With Quote
  #4  
Old 2/22/06, 1:23 PM
jclark1's Avatar
jclark1 jclark1 is offline
Active Poster
 
Join Date: Nov 2005
Location: Vashon, Wa
Posts: 644
Please Note: jclark1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

ok as soon as I posted these questions, bingo, there was Greg's post. Wow, I can't believe there aren't reqs. for residential.
Reply With Quote
  #5  
Old 2/22/06, 1:30 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

James, you end up at 250.104(C) and the question becomes whether it is exposed. I say yes it is, if nowhere else, at the metal box where the dryer vent piping attaches to the dryer. That is why I bet that is where the "appliance driver" got killed.
If they do end up invoking 250.104 they will be using 250.66 to size the bonding. That may be excessive but 8ga is not unreasonable. A 14ga would have operated the 20a O/C device feeding this fault.
Reply With Quote
  #6  
Old 2/22/06, 1:30 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

'Bizarre' Electrocution Prompts Home Builder Lawsuit

http://images.ibsys.com/2006/0221/7302626_240X180.jpg


POSTED: 5:37 pm EST February 21, 2006

UPDATED: 6:50 am EST February 22, 2006


One of the nation's largest home builders, its electrical subcontractors and a Central Florida county have been named in a wrongful death lawsuit after an appliance deliveryman was electrocuted in a "bizarre accident," according to a Problem Solvers investigation.


Deliveryman Rafael Ugalde died while on the job at 2777 Shearwater St. in Lennar's Lost Lake Reserve in Clermont, Fla.


Ugalde was electrocuted even though power to the room had been turned off, the report said.


"Wires behind a hallway wall hold the key to the bizarre accident that killed Ugalde," Problem Solver Mike Holfeld said.


Attorney O.B. Samuel, who has documented the investigation into Ugalde's death, said a drywall screw had been fired through the yellow wire casing, piercing the hot wire inside and the metal stud. That created a giant power circuit that electrified the house, according to the report.






"When they tore down the wall, it was quite obvious what had happened," Samuel said.

An electrical subcontractor for the Lennar project found 110 volts flowing through the screws of the room's mirror, the report said.

"That discovery is important because Rafael Ugalde was electrocuted as he hooked the dryer hose to a vent," Holfeld said.

The medical examiner noted that the metal duct and vent tested positive for 110 volts, according to the report.


Under state code, the electric wires should have been bundled with a plastic strap or metal clip. However, there was no evidence the wires were ever bundled.


Local 6 News also learned that Ugalde's shoes were wet while he was in the structure yet he never touched an outlet.




"Five months later and no one has accepted responsibility for the fatal mistake," Holfeld said.


"Well, then this story changes
because we're not talking about an accident, we're talking murder," Lisa Ugalde said.


The lawsuit's trail of blame includes the Lake County building inspector.


Documents obtained by Local 6 showed an inspector approved the electrical wiring on Sept. 6, 14 days before Ugalde was electrocuted.


"No denials were issued for the wiring," Holfeld said. "Ironically, the final approval was issued two weeks after Ugalde died."


The lawsuit is expected to be filed this week.


An attorney for Lennar Homes told Local 6 News that new safety protocols have been put in place since the accident. The company said it is confident that the rest of the homes in the subdivision are safe.


"Lake County and the electrical subcontractors are not talking," Holfeld said. "So, the question remains, who made the mistake? And, who will a jury hold accountable?"


Watch Local 6 News for more on this story.
Reply With Quote
  #7  
Old 2/22/06, 1:37 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

http://mfile.akamai.com/12909/wmv/vo...01329.200k.asx
Reply With Quote
  #8  
Old 2/23/06, 3:33 AM
Harvey Gordon's Avatar
Harvey Gordon Harvey Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 249
Default Re: Person electrocuted by energized metal in a building

Just goes to show...you never know what you will touch that may be HOT!





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #9  
Old 2/25/06, 3:08 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

Better access for viewing. I understand that the proposed requirement to bond all metal studs was not accepted.

http://mfile.akamai.com/12909/wmv/vo...01329.200k.asxhttp://mfile.akamai.com/12909/wmv/vo...01329.200k.asx
Reply With Quote
  #10  
Old 2/25/06, 5:01 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Person electrocuted by energized metal in a building

Joe Tedesco:

Excellent post.

A learning experience for all Inspectors involved in Construction Phase Inspections.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #11  
Old 2/26/06, 10:13 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Person electrocuted by energized metal in a building

love the image of the screw going through the NM itself.....classic..



Paul W. Abernathy
Reply With Quote
  #12  
Old 2/26/06, 12:17 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

The buzz over on the Fl IAEI bb is that this wil get added to the "glitch" amendments in November. We will be bonding steel framing. I am just not sure what the accepted methods will be.
Reply With Quote
  #13  
Old 7/23/08, 10:06 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Person electrocuted by energized metal in a building

Quote:
Originally Posted by jtedesco1
There is an addon for Firefox that will download almost any video and convert it for you (if it needs to be conerted).

Here is a link: https://addons.mozilla.org/en-US/firefox/addon/3006



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #14  
Old 7/23/08, 10:57 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,223
Default Re: Person electrocuted by energized metal in a building

Drywallers and romex....it's as simple as oil and water.
Reply With Quote
  #15  
Old 7/24/08, 12:01 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

Quote:
Originally Posted by jwicklander
Drywallers and romex....it's as simple as oil and water.
That screw is only 1.25" long. There never should have been unprotected Romex close enough for a 1.25" screw to hit it.

What always scares me is the deep boxes that place the Romex nearly up against the drywall on the backside. If the rockers miss the stud...............

Also, the stucco guys use a pneumatic stapler and staples about 2-1/2 inches long. When they miss the stud, look out!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Stupid ASHI legislatin in Washington DEAD. gromicko Legislation, Licensing & Legal Issues for Inspectors 20 1/29/08 9:05 AM
Article on Commercial and Residential Inspections and Assessment mcyr Commercial Inspections 2 8/6/07 1:26 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 4:03 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts