Brian,
Don't forget to subtract the 1/2 for drywall, which means the wire was 5/8 or closer to the backside of the wall.



http://www.nachi.org/forum/image.php?type=sigpic&userid=6376&dateline=1330979  258
Professional Inspection Services, LLC dba
1st Inspection Services
Bruce M. Graham III
Gainesville, FL 32608
352 871 8989
Florida Licensed Home Inspector #HI10
Radon Measurment Technician # R2279
NACHI05091592
ICC 5268478
www.1stinspectionsfl.com
www.bungalowstomansions.com
Reply With Quote
  #17  
Old 7/24/08, 7:25 AM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,198
Default Re: Person electrocuted by energized metal in a building

Good link, George.

But did you notice that this post was over two and half years old when you resurrected it????
Reply With Quote
  #18  
Old 8/2/08, 3:09 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

If this had happened on a AFCI or GFCI protested circuit would it have trip the breaker?
Reply With Quote
  #19  
Old 8/2/08, 3:22 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

A GFCI should have tripped before the person was seriously harmed.

BTW they make longer drywall screws. 1.25' is no guarantee that someone won't hit a wire.

The Fla building code now requires that steel framing is bonded ... because of this accident. NFPA has not seen that need yet. It is as easy as using a bonded steel box in each isolated section of framing firmly attached to the steel stud. It should be a recomended wiring practice for all sparkies, code or not. The material cost is nominal and the added labor is zero.
I understand there are even plastic boxes now with metal mounting flanges and a bonding screw.
Reply With Quote
  #20  
Old 8/2/08, 4:09 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

Quote:
Originally Posted by Greg Fretwell
A GFCI should have tripped before the person was seriously harmed.

BTW they make longer drywall screws. 1.25' is no guarantee that someone won't hit a wire.

The Fla building code now requires that steel framing is bonded ... because of this accident. NFPA has not seen that need yet. It is as easy as using a bonded steel box in each isolated section of framing firmly attached to the steel stud. It should be a recomended wiring practice for all sparkies, code or not. The material cost is nominal and the added labor is zero.
I understand there are even plastic boxes now with metal mounting flanges and a bonding screw.
Looks like this was the proposed change:


Section E3303

Bonding Metal Framing Members:

Metal framing members. Metal framing members shall be bonded to the equipment grounding conductor for the circuit that may energize the framing and be sized in accordance with the National Electric Code Table 250.122. For the purpose of this section, a grounded metal outlet box attached to the framing shall be permitted.


Rationale:






This year an appliance installer died from electrocution due to an energized metal framing member that came in contact with the metal duct that was connected to the appliance. Bonding of the metal framing members is necessary to counteract this possibility.

Reply With Quote
  #21  
Old 8/2/08, 7:19 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

If the damaged wire was on an AFCI protected circuit would it have tripped the breaker?
Reply With Quote
  #22  
Old 8/2/08, 8:08 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Person electrocuted by energized metal in a building

Probably not until the fault current went over 30ma. Still survivable in most cases but getting up in that "freezing" range. He may have been stuck until the breaker tripped. In the case of this accident when the guy was back behind an appliance it may be academic.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Stupid ASHI legislatin in Washington DEAD. gromicko Legislation, Licensing & Legal Issues for Inspectors 20 1/29/08 9:05 AM
Article on Commercial and Residential Inspections and Assessment mcyr Commercial Inspections 2 8/6/07 1:26 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 9:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts