Default Pictures from crazy inspection

I just wanted to post a couple shots from a restaurant inspection I did yesterday for a client who is looking to lease the facility. I had a commercial electrician with me doing the inspection and he said that this builing would be the ultimate electrician training facility. First picture is of live 100amp service conductors feeding a sub panel, notice how well the are protected and hung neatly off the metal pumbing lines. The second is of a live open box on the kitchen floor under a leaky stainless steel sink. And just a couple more for humour. Stopped counting at about 50 open junctions. The owner said the building has passed all code inspections and he had no idea that there was so much wrong. The plumbing was another fun issue all together. Am I just being too picky?
Attached Thumbnails
pictures-crazy-inspection-3210-homestead-drive-038.jpg   pictures-crazy-inspection-3210-homestead-drive-097.jpg   pictures-crazy-inspection-3210-homestead-drive-066.jpg   pictures-crazy-inspection-3210-homestead-drive-043.jpg   pictures-crazy-inspection-3210-homestead-drive-046.jpg  


Last edited by jbettencourt; 1/14/09 at 10:11 AM..
Reply With Quote
  #2  
Old 1/14/09, 10:34 AM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 604
Default Re: Pictures from crazy inspection

Wether your buying or leasing, your best investment is always an inspection. For those doubters shame shame. As for the recent code inspections WHAT EVER. Why do people try to pull one over on us.



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #3  
Old 1/14/09, 10:42 AM
Linas I. Dapkus's Avatar
Linas I. Dapkus Linas I. Dapkus is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL
Posts: 3,730
Default Re: Pictures from crazy inspection

That pipe insulation looks like it might be asbestos.
Reply With Quote
  #4  
Old 1/14/09, 10:56 AM
jbettencourt jbettencourt is offline
InterNACHI Member
 
Join Date: Oct 2007
Location: Stoney Creek, ON
Posts: 507
Please Note: jbettencourt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pictures from crazy inspection

Linas that was noted in the report, there was very little of it and it was far from the worst part with the plumbing. Troy the electrician told the owner that if an electrical safety inspector was to inspect the building that the local hydro company would pull the meter. Gas lines were not properly marked or with proper shutoffs, what a nightmare. I should have charged more!
Reply With Quote
  #5  
Old 1/14/09, 11:50 AM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 604
Default Re: Pictures from crazy inspection

Wouldn't that be great charge based on the amount of defects, What a concept. If that was case we would all be laughing all the way to the bank



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #6  
Old 1/14/09, 4:09 PM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,792
Default Re: Pictures from crazy inspection

Nice pics Jerry, I also agree with Linas, possible ACM.





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #7  
Old 1/14/09, 6:04 PM
Ian A. Niquette's Avatar
Ian A. Niquette Ian A. Niquette is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Markesan, WI
Posts: 1,193
Send a message via ICQ to iniquette
Default Re: Pictures from crazy inspection

Gonna have to start callin you the Deal killer pretty soon Jerry!! thanks for sharing.



Ian Niquette
Square One Home Inspection
Markesan WI 53946
www.squareonehomeinspection.com
Active Rain Network



What we've got here is......failure......to communicate.....
Reply With Quote
  #8  
Old 1/14/09, 8:13 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Pictures from crazy inspection

Personally i think it looks ok , easy access to all electric connections, You can hang your trouble light from loop in wires . and as for asbestos good fire protection.
Btw i am kidding great Pictures thanks for sharing
Reply With Quote
  #9  
Old 1/14/09, 10:31 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 791
Default Re: Pictures from crazy inspection

Quote:
Originally Posted by jbettencourt View Post
I just wanted to post a couple shots from a restaurant inspection I did yesterday for a client who is looking to lease the facility. I had a commercial electrician with me doing the inspection and he said that this builing would be the ultimate electrician training facility. First picture is of live 100amp service conductors feeding a sub panel, notice how well the are protected and hung neatly off the metal pumbing lines. The second is of a live open box on the kitchen floor under a leaky stainless steel sink. And just a couple more for humour. Stopped counting at about 50 open junctions. The owner said the building has passed all code inspections and he had no idea that there was so much wrong. The plumbing was another fun issue all together. Am I just being too picky?
Jerry,

It sounds like the nightmare I had last month, a 21 rooms Inn's with commercial kitchen, dining room, bar, laundry room and banquet rooms...

I didn't get an electrician because I knew that after opening one distribution panel that I would recommend an electrician...and I did.

There is so much regulations when it comes to commercial kitchen that it would simply be too much to list here but I was lucky as the gas supply to the appliances was turned off; also the refrigeration (walk-in coolers, freezers were all off (the Inn was vacant). When the sink hand washing tap was turned on the floor drain overflowed...this Inn's was on septic!

I disclaimed fire code issues and inspected only three random units to keep costs down for my client to which he was happy with.

It took me five hours to do this inspection not to mention writing the report.

Cheers,
Attached Thumbnails
pictures-crazy-inspection-img_0006.jpg   pictures-crazy-inspection-img_0281.jpg   pictures-crazy-inspection-img_0221.jpg   pictures-crazy-inspection-img_0200.jpg   pictures-crazy-inspection-img_0176.jpg  




Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #10  
Old 1/14/09, 11:28 PM
Terry B. Clayton Terry B. Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 193
Default Re: Pictures from crazy inspection

Would you have already requested to see previous inspection documents as part of the commercial inspection. just asking possibly not part of the inspection agreement. Hope you made good money lot of hazards.
Reply With Quote
  #11  
Old 1/14/09, 11:35 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Pictures from crazy inspection

Just asking? If it is a commercial building shouldn't the wiring be done in conduit?
Reply With Quote
  #12  
Old 1/21/09, 8:39 AM
Linda J. Foster's Avatar
Linda J. Foster Linda J. Foster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 463
Default Re: Pictures from crazy inspection

What is picture 4 ?



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

(210) 347-1023
TREC #7654
InterNACHI #06032691

Reply With Quote
  #13  
Old 1/21/09, 8:58 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Pictures from crazy inspection

Quote:
Originally Posted by lfoster View Post
What is picture 4 ?
clothes chute?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #14  
Old 1/22/09, 11:11 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 791
Default Re: Pictures from crazy inspection

Quote:
Originally Posted by mlarson View Post
clothes chute?
This laundry chute which was two floors above a concrete floor was accessible by anyone including small child and is a fire hazard.

As for the electrical wiring not being in a conduit, my guess is it depends on the situation/location; I've seen wiring with and without conduits.



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #15  
Old 1/23/09, 2:31 AM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 519
Default Re: Pictures from crazy inspection

Quote:
Originally Posted by tclayton View Post
Would you have already requested to see previous inspection documents as part of the commercial inspection. just asking possibly not part of the inspection agreement. Hope you made good money lot of hazards.

Good point Terry,

If you can get any coop from the owner.. It's great to be able to speak to people who have performed maintenance, tenants generally remark as to how current owner is handling issues etc..

I try to get a head's up well in advance so as to speak to anyone I can in connection with building etc.

Tim



Tim Spargo

Home Inspection Lancaster CA, Palmdale CA Antelope Valley





Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Pictures Needed kgoff Misc. Discussion 1 4/16/07 8:53 PM


All times are GMT -4. The time now is 12:15 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts