Is it acceptable to pigtail a copper wire to an aluminum 2 AWG SE cable? I came across a 100 AMP panel yesterday that was recently replaced and looked OK, with the exception of the this copper splice (pigtail) inside the panel. One side of the SE cable was aluminum and the other was pigtailed with a 12 inch section of copper.

Thanks,

Kevin



Kevin A. Richardson, BA
Level III Certified Infrared Thermographer, #7493
BPI Certified Building Performance Analyst
Maryland Licensed Home Inspector, #29727
INACHI Certified Home Inspector, #04091175

301-942-4610
www.richnspect.com
(Residential Inspections)
www.infrared-diagnostics.com
(Commercial Infrared Services)
www.thehomegreenteam.com
(Home Energy Performance Audits)
Reply With Quote
Find an InterNACHI certified Vermont Home Inspector (and anywhere else in North America)
  #2  
Old 10/21/09, 12:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Pigtailing SEC

It may be okay.

The conductor(s) need to be sized properly, the connector needs to be listed for CU/AL connections and it should include an antioxidant paste.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 10/21/09, 6:30 PM
Robert Hess Robert Hess is offline
InterNACHI Member
 
Join Date: Jul 2006
Location: Middletown, NY
Posts: 12
Default Re: Pigtailing SEC

they even have a purple wire nut exclusively for that type of pigtailing.
Reply With Quote
  #4  
Old 10/21/09, 7:28 PM
Kevin A. Richardson Kevin A. Richardson is offline
InterNACHI Member
 
Join Date: Sep 2004
Posts: 1,145
Default Re: Pigtailing SEC

Thanks, Guys!!

I kinda thought it was OK, but wanted a second opinion.

Thanks,

Kevin



Kevin A. Richardson, BA
Level III Certified Infrared Thermographer, #7493
BPI Certified Building Performance Analyst
Maryland Licensed Home Inspector, #29727
INACHI Certified Home Inspector, #04091175

301-942-4610
www.richnspect.com
(Residential Inspections)
www.infrared-diagnostics.com
(Commercial Infrared Services)
www.thehomegreenteam.com
(Home Energy Performance Audits)
Reply With Quote
  #5  
Old 10/22/09, 6:17 AM
James A. Levy James A. Levy is online now
InterNACHI Member
 
Join Date: Dec 2008
Location: Medford,NJ
Posts: 152
Default Re: Pigtailing SEC

A connection like that should have all of the items listed, but you should not be able to see them. The mechanical portion should be a split bolt, or an approved set screw connector. Then it is usually wrapped with a rubber insulating tape and then vinyl tape for protection. I have never seen a wire nut that was large enough for the connection you describe.
Reply With Quote
  #6  
Old 10/27/09, 11:32 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Pigtailing SEC

Polaris Splices- Easy method and CU/AL Rated are a good choice as well.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical 0 7/2/07 1:35 PM


All times are GMT -4. The time now is 7:45 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts