Is it acceptable to pigtail a copper wire to an aluminum 2 AWG SE cable? I came across a 100 AMP panel yesterday that was recently replaced and looked OK, with the exception of the this copper splice (pigtail) inside the panel. One side of the SE cable was aluminum and the other was pigtailed with a 12 inch section of copper.
Thanks, Kevin Kevin A. Richardson, BA Level III Certified Infrared Thermographer, #7493 BPI Certified Building Performance Analyst Maryland Licensed Home Inspector, #29727 INACHI Certified Home Inspector, #04091175 301-942-4610 www.richnspect.com (Residential Inspections) www.infrared-diagnostics.com (Commercial Infrared Services) www.thehomegreenteam.com (Home Energy Performance Audits) |
| Find an InterNACHI certified Vermont Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
It may be okay.
The conductor(s) need to be sized properly, the connector needs to be listed for CU/AL connections and it should include an antioxidant paste. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
they even have a purple wire nut exclusively for that type of pigtailing.
|
|
#4
|
|||
|
|||
|
Thanks, Guys!!
I kinda thought it was OK, but wanted a second opinion. Thanks, Kevin Kevin A. Richardson, BA Level III Certified Infrared Thermographer, #7493 BPI Certified Building Performance Analyst Maryland Licensed Home Inspector, #29727 INACHI Certified Home Inspector, #04091175 301-942-4610 www.richnspect.com (Residential Inspections) www.infrared-diagnostics.com (Commercial Infrared Services) www.thehomegreenteam.com (Home Energy Performance Audits) |
|
#5
|
|||
|
|||
|
A connection like that should have all of the items listed, but you should not be able to see them. The mechanical portion should be a split bolt, or an approved set screw connector. Then it is usually wrapped with a rubber insulating tape and then vinyl tape for protection. I have never seen a wire nut that was large enough for the connection you describe.
|
|
#6
|
||||
|
||||
|
Polaris Splices- Easy method and CU/AL Rated are a good choice as well.
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |