Default Plastic ceiling fan box?

Would you be OK with a ceiling fan hanging from a plastic box like this? A plastic ceiling fan box is a new one on me. I'm worried about fatigue and material failure down the road.



According to NEC 314.27 a ceiling fan box should be "listed, marked by the manufacturer as suitable for this purpose....The required marking shall include the maximum weight to be supported."

I can't find any of that on the product itself. I'm not sure that simply saying "UL 514C listed" on the packaging and website is OK.

http://www.hubbellcatalog.com/raco/R...&FAM=RacoBoxes



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 11/2/10, 9:58 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Plastic ceiling fan box?

From Raco Catalog
Attached Thumbnails
plastic-ceiling-fan-box-raco.jpg  



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #3  
Old 11/2/10, 10:00 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Plastic ceiling fan box?

But Michael, how do we know it's actually listed for that use by UL?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 11/2/10, 10:09 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic ceiling fan box?

If you read the instructions you will see that the box does not support the fan. The fan is supported by the framing member above that box.
Reply With Quote
  #5  
Old 11/2/10, 10:12 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Plastic ceiling fan box?

Quote:
Originally Posted by jfunderburk View Post
But Michael, how do we know it's actually listed for that use by UL?
Compliances
• – Standard 514-C,
File E104681 and R9320
• All versions of RACO® 7120 are UL approved
for nonmetallic wiring systems
• Boxes are listed for their Electrical
Applications (Electrical Codes), UL
Green Book
• Boxes are listed for mechanical properties,
including the 2-hour Fire Rating,
(building codes) UL Orange Book
• Federal Manufacturer’s number
28488



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #6  
Old 11/2/10, 4:00 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic ceiling fan box?

If the fan is supported by the framing member then the box isn't required to be rated for fan support. The NEC gives you the option of using a fan box or supporting the fan independently of the box. The key wording in the requirement is sole support. I've used the box in the OP and happen to like them.

Quote:
314.27(D) Boxes at Ceiling-Suspended (Paddle) Fan Outlets. Outlet boxes or outlet box systems used as the sole support of a ceiling-suspended (paddle) fan shall be listed, shall be marked by their manufacturer as suitable for this purpose, and shall not support ceiling-suspended (paddle) fans that weigh more than 32 kg (70 lb). For outlet boxes or outlet box systems designed to support ceiling-suspended (paddle) fans that weigh more than 16 kg (35 lb), the required marking shall include the maximum weight to be supported.
Reply With Quote
  #7  
Old 11/2/10, 5:11 PM
Kenneth Dolin's Avatar
Kenneth Dolin Kenneth Dolin is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Palm Beach County, Florida
Posts: 502
Default Re: Plastic ceiling fan box?

But the box has picture of a fan and home depot sells it so it must be ok



Ken Dolin
Kenco Home Inspections
WWW.Kenco.org
State of Florida Licensed Home Inspector HI 59
Reply With Quote
  #8  
Old 11/2/10, 5:40 PM
Michael Roberson's Avatar
Michael Roberson Michael Roberson is offline
InterNACHI Member
 
Join Date: May 2008
Location: West Michigan, Lower Penninsula
Posts: 1,732
Default Re: Plastic ceiling fan box?

These boxes are very strong. I have used them before. This wouldn't be my first choice, but I would definitely use it if I found myself in the situation where my box placement was directly in the middle of a truss. It gives you some space to put your wire connections.
Reply With Quote
  #9  
Old 11/2/10, 5:58 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic ceiling fan box?

That box does not have to be strong since it is only a place to make the splices. It is not providing the support for the fan. The fan is hanging on two long screws into the framing member.
Reply With Quote
  #10  
Old 11/2/10, 7:18 PM
Terry Clayton Terry Clayton is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Arnold, MO
Posts: 246
Default Re: Plastic ceiling fan box?

I have used this box for several years and find it to be universal and prefer it to most boxes rated for fan support. Using this box mounted to a framing member provides for a much sturdier and less flexing fan installation, but as with any thing else it is only as good as the installer wants it to be.
Reply With Quote
  #11  
Old 11/2/10, 8:01 PM
David Hays David Hays is online now
InterNACHI Member
 
Join Date: Feb 2010
Location: Denver, CO
Posts: 353
Default Re: Plastic ceiling fan box?

I just used one of those boxes a few weeks ago. As others have stated the fan is supported to the structure with the long screws supplied with the box. The box is for the electrical wire splices.
As I recall, all of the directions were clearly printed with the box.
If you don't like this box, don't use it. There are plenty of other products that work.



David Hays
All Points Home Inspections LLC
Denver, CO
720-670-0366
allpointshomeinspect@yahoo.com
www.allpointshomeinspections.org
Reply With Quote
  #12  
Old 11/2/10, 8:35 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,797
Default Re: Plastic ceiling fan box?

Quote:
Originally Posted by Jim Port View Post
That box does not have to be strong since it is only a place to make the splices. It is not providing the support for the fan. The fan is hanging on two long screws into the framing member.
How many times does Jim have to say it?
The box does not support the fan that weighs about 35 lbs. The rating is for the hardware that comes with the fan. The hardware and screws supplied are to get the 70-75 lb. rating support.
Plastic, steel, the goddarn blocking and screws are holding up the weight.

plastic-ceiling-fan-box-ceiling_fan_text.jpg

plastic-ceiling-fan-box-ceilingfanmount400.jpg

Hope this makes it more understandable.
Reply With Quote
  #13  
Old 11/2/10, 8:41 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic ceiling fan box?

I was starting to get that deja vu feeling.
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 11/2/10, 9:04 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic ceiling fan box?

And this one has a few violations.

Reply With Quote
  #15  
Old 11/2/10, 9:09 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 19,797
Default Re: Plastic ceiling fan box?

I was waiting for that.

That is the only picture of the bracket that supports the fan I could find.

Thanks for bringing it up.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Plaster Ceiling Systems - Hidden Danger Philip LaMachio Interior Inspections 3 12/1/09 8:38 AM
Yep, The plastic Nail mcyr Structural Inspections 6 3/23/08 10:53 AM
Asbestos ceiling tiles scoslett Interior Inspections 30 10/20/07 2:30 PM
Gas changes for plastic vents in Canada rcooke Canadian Inspectors 0 7/30/07 2:15 PM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 4 1/22/07 12:24 PM


All times are GMT -4. The time now is 9:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts