Default Re: Plastic Square D service panel

yeah.....Trilliant was by Sq. D and it was manufactured from 1990-1996 and was their first attempt at a nonmetallic service panel. I guess it did not wear well as they dont manufacture it anymore.....BUT they pull a nice price on surplus forums and on flea-bay....

it was only used for NM Cable and the like and had built in clamps.....They did not sell well but if you indeed have one it will have the name on the cover.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #17  
Old 9/26/08, 8:33 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Plastic Square D service panel

Quote:
Originally Posted by gbeaumont View Post
hi to all,

I remember the thread about Trilliant panels, I am sure they were discontinued years ago.

Here's another plastic panel that I never found out the manufacturer of

Regards

Gerry
Due to the lack of space in that enclosure I would venture to say it was probably made by some manufacturer trying to make a break into the industry...probably used standard other brand components and it just never caught on....but I could be wrong.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #18  
Old 9/26/08, 8:37 PM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,531
Default Re: Plastic Square D service panel

Paul,

The photo you posted is the exact same panel I saw today. It is a 150 AMP panel, it was installed 1991 in new construction.

THANKS!

When I learn how to post photos I will post the photos.
Reply With Quote
  #19  
Old 9/26/08, 8:43 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Plastic Square D service panel

Yep.....1991 most certainly a Trilliant panel......I dont recall any problems with them that i am aware of.

I do recall a actual " RECALL " on some surge arresters that were designed specifically for the "Trilliant" panels....so if they have a surge arresters installed on it and it has a model number of (Cat. No. SDT1175SB)...again they were made specifically for those type panels and the surge arresters was recalled.

Other than that....I am aware of no problems with these panels.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #20  
Old 9/26/08, 8:57 PM
Erby Crofutt's Avatar
Erby Crofutt Erby Crofutt is offline
InterNACHI Member
 
Join Date: Sep 2002
Location: Georgetown, KY
Posts: 1,184
Default Re: Plastic Square D service panel

Given that Square D has a factory here in Lexington, KY, I've seen quite a number of these Trilliant panels.

The first time I ran into one, I called Square D about them.

No known problems. They were Square D's attempt at a "decorator" panel.

They just didn't sell well enough to continue production.

The cover is held on with four quarter turn twist lock screws. Twist the screw about 1/4 turn to unlock it and let the cover come off.

It can be a pain in the butt to get the lock screw back into the hole.

Other than that, inspect as usual.
Reply With Quote
  #21  
Old 9/26/08, 9:04 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Plastic Square D service panel

Quote:
Originally Posted by pabernathy View Post
Due to the lack of space in that enclosure I would venture to say it was probably made by some manufacturer trying to make a break into the industry...probably used standard other brand components and it just never caught on....but I could be wrong.....

Paul, you may be correct, I don't know why but I have the feeling that they may have also been built for a marine/RV purpose.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #22  
Old 9/26/08, 9:27 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic Square D service panel

I've never seen one of those Trilliant panels, but that black one Gerry posted is the one I have seen.
Reply With Quote
  #23  
Old 9/26/08, 10:01 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Plastic Square D service panel

Wonder when we will be using green materials. How about a wicker box cabinet?

Reply With Quote
  #24  
Old 9/26/08, 10:48 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic Square D service panel

Quote:
Originally Posted by bhartley View Post
What are the issues with a plastic electrical service panel cover, if any?
The service panel is made by Square D.

Thanks, for you help in advance.
None, no issues, they are still listed and still permitted see, Section 408.40 in the 2008 NEC.

The term (if of metal) was added to Section 384-20 long ago to recognize this new product line described as "Trilliant Home Power System"
Reply With Quote
  #25  
Old 9/27/08, 12:56 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic Square D service panel

There was nothing wrong with the Trilliant panel, save for the fact that they were looked upon by electricians with suspicion. Pretty much all the panels in Europe are plastic, so it's in our future again, for sure. The Trilliant was the right product at the wrong time in the US marketplace. The breakers are crazy expensive nowadays. I wired a couple Habitat houses with NOS Trilliant panels and breakers someone donated. The one and only time I ever worked with the stuff.
Reply With Quote
  #26  
Old 9/27/08, 1:49 AM
Buck Hartley, CMI's Avatar
Buck Hartley, CMI Buck Hartley, CMI is offline
InterNACHI Member
 
Join Date: Nov 2005
Location: Shawnee, KS
Posts: 1,531
Default Re: Plastic Square D service panel

I could not remove the cover because of the plastic screws, one screw would not release.

Thanks, for all the input.
Reply With Quote
  #27  
Old 9/27/08, 4:55 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Plastic Square D service panel

Quote:
Originally Posted by Marc D. Shunk View Post
There was nothing wrong with the Trilliant panel, save for the fact that they were looked upon by electricians with suspicion. Pretty much all the panels in Europe are plastic, so it's in our future again, for sure. The Trilliant was the right product at the wrong time in the US marketplace. The breakers are crazy expensive nowadays. I wired a couple Habitat houses with NOS Trilliant panels and breakers someone donated. The one and only time I ever worked with the stuff.
Look here for product information
Reply With Quote
  #28  
Old 9/27/08, 8:37 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Plastic Square D service panel

Dont believe anyone said anything was wrong with the Trilliant panels....just the surge arrestors made specifically for them as reported by the CPSC.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #29  
Old 9/27/08, 11:04 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Plastic Square D service panel

I actually installed two 200A and on 100A Triliant panels when my home was built in about 1992. I don't think they are really plastic - probably a Lexan product. The panels had some really nice features and the breakers themselves (as I understand it) were basically the same as other Sq D breakers, just in a slightly different housing. It is a shame they were never accepted into the marketplace. Fast cable install (no need for romex connectors) but otherwise wire the same as any other panel.

I have never had a minute's trouble with them, although I did remove the surge protectors when they were recalled and seem to remember 1 or 2 early failures of ground fault breakers (would not test trip) - fortunately I had bought a few "spares".

As mentioned above, to remove the cover, just rotate the plastic screw to the unlock position marked on the cover and then PULL (on the cover) straight out. To replace, position the screw into the hole and PUSH hard. Believe me, it works - I've been into mine plenty of times - as recently as last week to add a circuit.

I'll be glad to post some photos, if anyone is interested.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #30  
Old 9/27/08, 11:18 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Plastic Square D service panel

Hi Frank,

I'd love to see some shots of those in situe, no doubt many others would agree with me.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Service panel damage dlee2 General Inspection Discussion 4 2/5/07 5:59 PM
Service wire size to breaker panel sfalvey Electrical Inspections 12 10/31/06 5:28 PM
Zinsco Service Disconnect Panel pdickerson Electrical Inspections 7 9/16/06 12:59 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 1:10 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts