The wiring to the 15 amp breakers in this subpanel doesn't seem right. What is a good way to explain?
The 100 amp breaker is fed from a 60 amp breaker at the main panel. |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Interesting non-compliant use of a 3 pole disconnect. Tap rule violation. Two conductors in a lug designed for one. Plenty enough to say it ain't right and write it up.
I see copper and aluminium under the same lug on the backpan. |
|
#3
|
||||
|
||||
|
Where is the aluminum? I see the copper.
Just curious, the call out is well justified. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
||||
|
||||
|
Thanks. Kinda hard to see it from the picture.
Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#6
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Fruitcake electrician or Johnny on the Spot handyman
|
|
#7
|
|||
|
|||
|
Appreciate the input - Al
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| A fake (temporary) site I built to help explain where we are going with this... | gromicko | Miscellaneous Discussion for Inspectors | 63 | 6/8/07 2:23 AM |
| Crazy BB explain please | cbottger | Inspecting HVAC Systems | 7 | 4/11/07 4:24 PM |
| Try to explain this one to me?? | crichiii | Inspecting HVAC Systems | 17 | 12/16/06 10:15 AM |
| Some one please explain | mcotten | Inspecting HVAC Systems | 5 | 2/4/06 12:23 PM |