Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical
Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.
Old 3/31/09, 12:09 AM
Nick Gromicko's Avatar
Default Please proof this article on AFCIs.
http://www.nachi.org/arc-fault-circuit-interrupters.htm
Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Find an InterNACHI certified Kentucky Home Inspector (and anywhere else in North America)
Old 3/31/09, 12:12 AM
Jeffrey R. Pope's Avatar
Default Re: Please proof this article on AFCIs.
AFCIs function by monitoring the electrical waveform and promptly closing the circuit they serve if they detect changes in the wave pattern that are characteristic of a dangerous arc.
They don't close a circuit, they open the circuit. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Old 3/31/09, 12:16 AM
Nice catch Jeff! Dummy me. I changed to "opening (interrupting)"
Thanks!
Nick Gromicko, CMI
Founder
Old 3/31/09, 11:14 AM
Originally Posted by gromicko View Post
When an electric current crosses an air gap from an energized component to a grounded component ...
I would think that this is only one form of arc fault. An arc fault can also occur when current crosses other high-resistance gaps between components (such as corroded connections). Likewise, an arc fault can occur between two ungrounded components, such as in a 240 volts circuit, but I don't know if any AFCIs are designed to detect those faults.
You may also want to note that the reason AFCIs were developed is because other types of circuit interrupters are unable to detect such conditions before catastrophic damage has occurred.
Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Old 4/3/09, 6:16 PM
Eric Krause Eric Krause is offline
Hi Nick,
You might want to add and/or clarify information about combination AFCIs. I keep encountering people who do not yet understand what is meant by a combination AFCI. The orginal AFCIs sensed parallel arcing (line to neutral or line to ground) but did not sense the problem of serial arcing (associated with a loose/cut/severed/corroded wire/connections). The combination AFCI protects the combination of parallel plus serial arc faults. The electrical manufacturer's websites (Square D, Murray, etc) have better descriptions than what I have just described but I hope this feed back helps.
Eric Krause
Old 4/3/09, 6:49 PM
As a follow up to my recent feed back, I believe all AFCIs are required to be combination type (parallel arc and series arc). I was also a little confused when proof reading the section with the bullet points about -Branch/feeder, -Outlet circuit, -Combination, and -cord. The NEC requires that the whole branch circuit be de-energized when an arc fault is detected. AFCI breakers do this. An outlet (at least up to now) would not de-energize the circuit upstream of the outlet (between the outlet and the box). I think that is where a six foot rule comes in (I believe an AFCI receptacle might be permitted within six feet of the panel). It looked as though to me a bullet point might have been referring to an AFCI outlet/receptacle which is not acceptable to the NEC on a branch serving the rooms that are now specified in the 2008 NEC.
Eric Krause
Old 4/4/09, 12:41 PM
Paul W. Abernathy's Avatar
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Very Nice Nick.
Just keep in mind "Combination" type AFCI breakers are not a combination of Breaker and Device type units as the below statement eludes to. The Combination has to do with the detection of Parallel and Series types of arc fault situations.
"Combination—complies with the requirements of both the branch/feeder and the outlet circuit AFCI’s. "
You may want to add a small verbiage of the difference. The Branch-Feeder type are no longer allowed when being strictly called for Combination types.
FYI the exception for the 6' device AFCI was added in 2005 NEC, but as of yet it has not made it to the market that I am currently aware of. Below is the change to the 2008 NEC reflecting the removal of the 6' barrier.
Exception No. 1: Where RMC, IMC, EMT or steel armored
cable, Type AC, meeting the requirements of 250.118 using
metal outlet and junction boxes is installed for the portion
of the branch circuit between the branch-circuit overcurrent
device and the first outlet, it shall be permitted to
install a combination AFCI at the first outlet to provide
protection for the remaining portion of the branch circuit.
Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru
- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"
Old 4/4/09, 2:38 PM
Mark Thorman Mark Thorman is offline
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
You might want to go into more detail regarding the nuisance tripping with attention to vacuum cleaners currently on the market. One of the most frequent question I recieve after an inspection is why does my high end vacuum cleaner trip the breaker. I now include a note about vacuums in all my reports now.
www.MauiHomeInspections.com
Old 4/5/09, 1:32 PM
I am not aware of this being a real issue with the newer AFCI models. What needs to happen is if someone see's this happen ( which is more rare these days in my view and experience ) that they contact the manufacture with the model of Vacuume cleaner so that the manufactures can get the motors if needed, learn the waveform and get it into the next generation of devices.
I believe it is such a rare situation these days that it would not warrant being on a report simply because the AFCI is functioning properly and something within the motor is being recognized by the AFCI. While it may not be hazard and an inconvience it is not ( again my opinion ) not a wide spread issue....my parents have a high end electorlux and causes no problems on their AFCI circuits.
I believe that 95% of all nuisance tripping can be marked up as a real issue that was detected by the AFCI doing it's job. Many case to neutral connections downstream are diagnosed with these devices, many older pieces of equipment with motors going bad are diagnosed with these devices and with GFCI devices.....I will bring you to the example of a Nutone Bathroom Fan a few years ago that caused alot of issues for the AFCI manufactures.......once they received information on the model and could replicate the waveform the next generation of AFCI's solved the problem.....as with any technology ( which I happen to be VERY in favor of ) moves baby steps forward we will all benefit from the technology.
If only one life is saved......they are worth every penny of the investment.
Old 4/5/09, 3:07 PM
I agree that the vacuum cleaner issue is not a significant one but when I do a walk thru with a new home and mention it to my buyers in front of the builder, the builder always agrees and tells us that they do get complaints and that they recommend getting a different brand vaccum. This web site is close to what my report says.
http://www.us.squared.com/us/squared...2homeowner.pdf
Old 4/5/09, 8:14 PM
No worries...but as of that printing it makes reference to Jan 2001 and we have come along way baby....lol
Please proof this article: TPR Valves and Discharge Piping. gromicko Plumbing 2 3/30/09 7:42 PM
Please proof this article: An Overview of Water Heater Expansion Tanks. gromicko Plumbing 5 3/30/09 3:54 PM
Please proof this article: Safety Glass for Inspectors gromicko Misc. Discussion 3 3/20/09 12:18 AM
Roy the proof you asked for wdevries Canadian Inspectors 55 7/8/08 11:30 AM
Are electricians supposed to use these tools as per 70E? jtedesco1 Electrical 27 12/15/07 4:40 PM
Popular
Membership
Education
Chapters & Members
Articles & Links
Other Organizations