Default Please proof this new article on conductor types

http://www.nachi.org/conductor-types

cheers
Reply With Quote
Find an InterNACHI certified Alaska Home Inspector (and anywhere else in North America)
  #2  
Old 5/21/09, 8:42 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Please proof this new article on conductor types

Quote:
Originally Posted by rlondon View Post
I will look at it in more detail but the very first thing I see is the 14-3 example is incorrect. You show a Red, White and Green and this is not how you would see it. Try Red, Black, White and Bare( Copper Color ).

I will look for more.

Your Statement: "They are not permitted in residential construction higher than three stories, or in any commercial construction."

Technically the 3 story limitation was lifted but it still may depend on the limitations from th IBC.

Your Statement: "NM and NMC cables should be secured at intervals that do not exceed 4˝ feet, and they should be secured within 12 inches of junction boxes and panels to which they are attached. Cables that do not comply with this rule can sag and are vulnerable to damage."

This is correct in most cases ( the 12" part ), but if the box is a non-metallic ( most are ) single gang box the distance is 8".

Exception: Where nonmetallic-sheathed cable or multiconductor
Type UF cable is used with single gang boxes not

larger than a nominal size 57 mm × 100 mm (2

1.4 in.× 4 in.) mounted in walls or ceilings, and where the cable
is fastened within 200 mm (8 in.) of the box measured along
the sheath and where the sheath extends through a cable
knockout not less than 6 mm (
1.4 in.), securing the cable to

the box shall not be required. Multiple cable entries shall
be permitted in a single cable knockout opening.



Armored Cables (AC)
Armored cable (AC), also known as BX, was developed in the early 1900s by Edwin Greenfield. It was first called “BX” to abbreviate “product B – Experimental,” although AC is far more commonly used today. Like Romex cables, they cannot be used in residences higher than three stories, and the rules for protection and support of AC wiring are essentially the same as the rules for Romex. Unlike Romex, however, AC wiring has a flexible metallic sheathing that allows for extra protection. Some major manufacturers of armored cable are General Cable, AFC Cable Systems, and United Copper Systems.

Ok, I know plenty of multifamily dwellings higher than 3 stories using AC Cable. Also while good info lets understand that BX is not AC cable in that the outer jacket of AC Cable is approved as an EGC while BX was never evaluated or approved for this application. Many DIYers use the BX to justify replaceing old 2 prong plugs with 3 prong plugs and install a bonding jumper. In reality the connections for BX and it's steel jacket may give the appearance of being ok but it is not....just some additional info.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 5/21/09 at 9:00 PM..
Reply With Quote
  #3  
Old 5/22/09, 12:27 AM
Nick Gromicko's Avatar
Nick Gromicko Nick Gromicko is offline
InterNACHI Member
 
Join Date: Aug 2002
Location: Valley Forge, PA
Posts: 19,581
Default Re: Please proof this new article on conductor types

Thanks Paul!



Nick Gromicko, CMI
Founder
World's biggest, best inspection association
"Planet InterNACHI... resistance is futile"
Reply With Quote
  #4  
Old 5/22/09, 1:15 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Please proof this new article on conductor types

1. As Paul mentioned, the 14/3 needs to be addressed. Also, NM cable is now sold as NM-B (NM is the old style of cable manufactured years ago, it is no longer available)
2. The illustration of the SE cable is a little misleading. It is typically a flat cable with the grounded conductor helically wound around the other conductors contained within the sheathing.
3. The AC cable would most likely be a black and white conductor if showing a 2-wire cable.


How specific would you want this critique to be? I do not want to pound someone for the work they started, at least not publically. If you would like more input from me, please PM me.
Reply With Quote
  #5  
Old 5/23/09, 9:04 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Please proof this new article on conductor types

I am sure they dont mind being pounded Pierre as they openly asked for the critique of the article. I spoke on specific things I saw in a short glance but I am sure they would welcome a more indepth review with open arms.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Please proof this new article about double-paned windows. John McKenna mentioned. gromicko Thermal Imaging, Infrared Cameras & Energy Audits 3 4/29/09 11:57 PM
Please proof this article on Chinese drywall. gromicko IAC2 Forum 1 4/29/09 8:20 AM
Please proof this new article on bidets. gromicko Plumbing 0 4/22/09 4:55 PM
Roy the proof you asked for wdevries Canadian Inspectors 55 7/8/08 11:30 AM
Are electricians supposed to use these tools as per 70E? jtedesco1 Electrical 27 12/15/07 4:40 PM


All times are GMT -4. The time now is 9:23 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts