Default POCO drop

Is there anything wrong with this.

Seems like the POCO can get away with a lot more than others can.
Attached Thumbnails
poco-drop-drop_small-big_small.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #2  
Old 2/27/08, 6:09 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: POCO drop

Quote:
Originally Posted by wdecker
Is there anything wrong with this.

Seems like the POCO can get away with a lot more than others can.
Is that temporary drop for a building being renovated/upgraded?
Reply With Quote
  #3  
Old 2/27/08, 6:22 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: POCO drop

Quote:
Originally Posted by Brian A. MacNeish
Is that temporary drop for a building being renovated/upgraded?
Older apartment building condo conversion. The building was fully occupied and the buyer was buying a unit from the original buyer who bought 2 years before.

Here is another one. Doesn't this violate the "near a window" rule?
Attached Thumbnails
poco-drop-dscf3232.jpg  



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #4  
Old 2/27/08, 6:32 PM
Troy Farmer's Avatar
Troy Farmer Troy Farmer is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Eagle, ID
Posts: 619
Default Re: POCO drop

or shocking imagine only to survive the fire thinking that hey I'm going to jump and then you get the shock of your life. Where is the common sense
You only hope that when you hit the ground your heart restarts.
At least they could have provided a handrail??



Troy Farmer
Presidential Inspections LLC
Chapter President Southern Idaho
PO Box 2144
Eagle, Idaho 83616
208-573-5300
http://www.presidentialinspection.com
http://info@presidentialinspection.com


"He who can, does. He who can’t, teaches"
"Where would we be without Teachers"
Reply With Quote
  #5  
Old 2/27/08, 7:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: POCO drop

Quote:
Originally Posted by wdecker
Here is another one. Doesn't this violate the "near a window" rule?
If there were a "near-a-window" rule, I would say yes , but there are "specific requirements" and it appears that this is a compliant installation.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/27/08, 7:20 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: POCO drop

From that pic the feeders are right on the cable line .
Reply With Quote
  #7  
Old 2/27/08, 7:23 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: POCO drop

Quote:
Originally Posted by jpope
If there were a "near-a-window" rule, I would say yes , but there are "specific requirements" and it appears that this is a compliant installation.
I was taught that there cannot be a drop (or drip loops) within 3' (laterally) around a window.

Educate me, please.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #8  
Old 2/27/08, 7:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: POCO drop

Sides and bottom only. The top of the "openable" portion of the window must simply be below the conductors.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 2/27/08, 7:39 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: POCO drop

Quote:
Originally Posted by jpope
Sides and bottom only. The top of the "openable" portion of the window must simply be below the conductors.
Thanks, Jeff.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 2/27/08, 7:41 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: POCO drop

Here is the reference;

CEC 230.9(A) Clearance from Windows. Service conductors installed as open conductors or multiconductor cable without an overall outer jacket shall have a clearance of not less than 900 mm (3 ft) from windows that are designed to be opened, doors, porches, balconies, ladders, stairs, fire escapes, or similar locations.

Exception: Conductors run above the top level of a window shall be permitted to be less than the 900-mm (3-ft) requirement.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #11  
Old 2/27/08, 7:45 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: POCO drop

Quote:
Originally Posted by wdecker
Is there anything wrong with this.

Seems like the POCO can get away with a lot more than others can.
Curious why you opened this thread with one of your old pictures?
Reply With Quote
  #12  
Old 2/27/08, 7:47 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: POCO drop

William,

As Jeff stated, over the window is fine.

But it appears that your drip loop is hanging right next to the window opening. A clear Violation.....

"Click to Enlarge"
poco-drop-se-window1.jpg
Reply With Quote
  #13  
Old 2/27/08, 8:00 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: POCO drop

]


Last edited by belliott; 2/27/08 at 8:08 PM..
Reply With Quote
  #14  
Old 2/27/08, 8:07 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: POCO drop

Quote:
Originally Posted by Marc D. Shunk
Curious why you opened this thread with one of your old pictures?
Sorry, Mark. I thought it was another picture (the one with the multiple drop cables spliced to the service drop) before.

Just call me the Department of Redundancy Department



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #15  
Old 2/27/08, 8:09 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: POCO drop

Quote:
Originally Posted by dvalley
William,

As Jeff stated, over the window is fine.

But it appears that your drip loop is hanging right next to the window opening. A clear Violation.....

"Click to Enlarge"
Attachment 18995
The drop is clearly (don't be fooled by the shadow) within the "openable" part of the window (the top also opens, and we do so, in Chicago. Old habits.).



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Shop lights above a drop ceiling....? tdietrich1 Electrical Inspections 4 2/1/08 9:41 PM
Service Drop Dropped While at Inspection!! mlong Electrical Inspections 9 10/20/07 6:20 AM
Service Drop Q alarsen1 Electrical Inspections 11 2/25/07 9:45 AM
Service Drop Clearance Over Roof mlong Electrical Inspections 6 12/19/06 7:39 AM
Service Drop Was Finally Removed! jtedesco1 Electrical Inspections 1 12/1/06 2:40 AM


All times are GMT -4. The time now is 9:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts