Hey guys...need the big guns...deal fell through 'cause I stated that the pool pump bond wire was not present indicating that the existed the possibility that there was no bonding of the metal surfaces within 10' from the waters edge.
It seems that I was right...but just one question...can someone explain: 1. Why I was right? and, 2. How do I explain why it is necesarry or required for the the metal surfaces within 10' of the waters edge to be bonded back to the pool pump...and maybe, 3. What is Bonding versus Grounding Thanks Harvey Gordon - President - FloridaNACHI (The OFFICIAL Florida State Chapter of NACHI) SEFloridaNACHI (Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties) ______________ Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org ______________ |
|
#2
|
||||
|
||||
|
Sorry Harvey, but you were wrong (partially).
The dimension is 5 feet horz. and 12 feet vert. for required bonding. Nothing is bonded "back to" anything, but rather, they share a "common bond" (they're all connected). IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
2. Electrical Equipment: Metal parts of electrical equipment associated with the pool water circulating system, including pump motors and metal parts of equipment associated with pool covers, including electric motors, shall be bonded. 3. Bonding (Bonded). The permanent joining of metallic parts to form an electrically conductive path that ensures electrical continuity and the capacity to conduct safely any current likely to be imposed. The purpose of bonding is to establish an effective path for fault current that, in turn, facilitates the operation of the overcurrent protective device. Grounded. Connected to earth or to some conducting body that serves in place of the earth. |
|
#4
|
||||
|
||||
|
Jeff,
My visual cluse was there was no bond wire to the pool pump. It was my understanding that metal surrounding the waters edge, as well as the pool light were required to be bonded back to the pool pump. Harvey Gordon - President - FloridaNACHI (The OFFICIAL Florida State Chapter of NACHI) SEFloridaNACHI (Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties) ______________ Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org ______________ |
|
#5
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
||||
|
||||
|
Then how do I check that metal is bonded at the waters edge (and I refuse to go in the pool and create some static energy).
Harvey Gordon - President - FloridaNACHI (The OFFICIAL Florida State Chapter of NACHI) SEFloridaNACHI (Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties) ______________ Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org ______________ |
|
#7
|
||||
|
||||
|
Verifying the integrity of the bond is far beyond our scope, however, many components can be identified as being bonded based on their bonding lug.
Items such as pumps, heaters and metal filters should have a visible bonding lug with an appropriately sized bonding wire attached to it. Typically, the bonding wire is protruding from the concrete and is assumed to be bonded to the rebar. In many cases, you'll see the same lugs at wrought iron fencing and window frames within the regulated zone. If there is ever any question, I will defer the item to be verified for proper bonding of components. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Pictures are worth 1,000 words....
![]() (A) ReceptaclesIntent: The revised text is intended to clarify that GFCI protection is required for all 15 or 20A, 120V through 240V,240V circuits that supply single-phase receptacles for pool pump motors. Courtest of Mike Holt Enterprises- Can you tell I am a huge fan of Mr. Holt... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 3/1/06 at 9:18 AM.. |
|
#9
|
||||
|
||||
![]() A new item (4) was added and it reads: (A) ReceptaclesIntent: The new rule allows the required 15 or 20A, single-phase, 125V receptacle for outdoor pools and spas for dwelling units [680-22(A)(3)] to be located less than 10 ft., but not closer than 5 ft., from the pool, if the dimensions of the property prevent locating the receptacle 10 ft. away as required in 680.22(A)(3). Courtesy of Mike Holt Enterprises Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#10
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Paul, the accepted method in 250.26(C)(3) NEC2005 for alternate means is a 12"x12" grid of #8 solid copper, joined at every intersection by a listed means.
In a practical sense you will use a welded wire ground mat. That is really a monitary prohibition on encapulated rebar and paver pool decks. Over at ECN there are pictures of a job where they had to do one of these grids under pool pavers. I can try to track them down if you want to see it. |
|
#11
|
||||
|
||||
|
Paul or Greg,
In regards to the illustration above [NEC 680.26 (B)(1)] (1) Does the equipment need to be bonded if it is to the side of the house, behind a concrete wall enclosure, Appoximately 15' away from the pool edge? What are the distances for bonding pool equipment? And how long has it been required? There has been discussion on this before , I just forgot to bookmark the page. Thanks! |
|
#12
|
||||
|
||||
|
Greg,
I would LOVE to see it.... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 3/1/06 at 8:46 AM.. |
|
#13
|
||||
|
||||
|
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#14
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
http://electrical-contractor.net/ubb...ML/002086.html
This is the link to the discussion and the pictures of the job at the end |
|
#15
|
||||
|
||||
|
Thanks Greg....on that pre-fab mat.....looks like standard square fence metal myself that is connected together with split bolts...
It begs me to ask....since I am not in the office today does the 2005 NEC specify copper for this grid......and as stated I think 2002 leaves us without having to do this method......2005 most certainly expands it. Thanks again greg on the link....the install that fella did looks nice, Have you heard any news on any newer updated products for this... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year Last edited by pabernathy; 3/2/06 at 1:13 AM.. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| It's time for Professional Pool Inspections | Revel L. Thom | Ancillary Inspection Services & Additional Topics | 13 | 7/26/07 11:50 AM |
| Pentair Water Pool Gas Heater Recall | Gary Reecher | Inspecting HVAC Systems | 0 | 1/4/07 9:15 PM |
| Demystify Grounding & Bonding Class | pabernathy | Inspection Education & Training | 5 | 12/24/06 2:10 AM |