Hey guys...need the big guns...deal fell through 'cause I stated that the pool pump bond wire was not present indicating that the existed the possibility that there was no bonding of the metal surfaces within 10' from the waters edge.

It seems that I was right...but just one question...can someone explain:

1. Why I was right? and,
2. How do I explain why it is necesarry or required for the the metal surfaces within 10' of the waters edge to be bonded back to the pool pump...and maybe,
3. What is Bonding versus Grounding

Thanks





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #2  
Old 2/28/06, 1:28 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Pool Bonding

Sorry Harvey, but you were wrong (partially).

The dimension is 5 feet horz. and 12 feet vert. for required bonding.

Nothing is bonded "back to" anything, but rather, they share a "common bond" (they're all connected).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 2/28/06, 1:29 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Bonding

Quote:
Originally Posted by hgordon
Hey guys...need the big guns...deal fell through 'cause I stated that the pool pump bond wire was not present indicating that the existed the possibility that there was no bonding of the metal surfaces within 10' from the waters edge.

It seems that I was right...but just one question...can someone explain:

1. Why I was right? and,
2. How do I explain why it is necesarry or required for the the metal surfaces within 10' of the waters edge to be bonded back to the pool pump...and maybe,
3. What is Bonding versus Grounding

Thanks
1. See Article 680 - Part II. Permanently Installed Pools

2. Electrical Equipment: Metal parts of electrical equipment associated with the pool water circulating system, including pump motors and metal parts of equipment associated with pool covers, including electric motors, shall be bonded.

3. Bonding (Bonded). The permanent joining of metallic parts to form an electrically conductive path that ensures electrical continuity and the capacity to conduct safely any current likely to be imposed.

The purpose of bonding is to establish an effective path for fault current that, in turn, facilitates the operation of the overcurrent protective device.

Grounded. Connected to earth or to some conducting body that serves in place of the earth.
Reply With Quote
  #4  
Old 2/28/06, 1:40 AM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Default Re: Pool Bonding

Jeff,

My visual cluse was there was no bond wire to the pool pump.

It was my understanding that metal surrounding the waters edge, as well as the pool light were required to be bonded back to the pool pump.





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #5  
Old 2/28/06, 10:45 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Pool Bonding

Quote:
Originally Posted by hgordon
It was my understanding that metal surrounding the waters edge, as well as the pool light were required to be bonded back to the pool pump.
Those components are contained within a common bond. There is no single "bonding point" like you would think of in a grounding system (ground rod, water pipe, ufer). It's more like throwing everything into a basket. If it's not in the basket, it's not bonded - no single component is more critical than another. They must all share the same potential to ground.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 2/28/06, 12:14 PM
Harvey L. Gordon's Avatar
Harvey L. Gordon Harvey L. Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 252
Default Re: Pool Bonding

Then how do I check that metal is bonded at the waters edge (and I refuse to go in the pool and create some static energy).





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #7  
Old 2/28/06, 12:25 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Pool Bonding

Verifying the integrity of the bond is far beyond our scope, however, many components can be identified as being bonded based on their bonding lug.

Items such as pumps, heaters and metal filters should have a visible bonding lug with an appropriately sized bonding wire attached to it. Typically, the bonding wire is protruding from the concrete and is assumed to be bonded to the rebar.

In many cases, you'll see the same lugs at wrought iron fencing and window frames within the regulated zone.

If there is ever any question, I will defer the item to be verified for proper bonding of components.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 2/28/06, 12:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Pool Bonding

Pictures are worth 1,000 words....




Change requires an equipotential bonding grid be installed to reduce voltage gradients in and around permanently installed pools, outdoor spas, and outdoor hot tubs.


(B) Bonded Parts. The following parts of a permanently installed pool, outdoor spa, and outdoor hot tub must be bonded to a equipotential bonding grid of the type specified in 680.26(C).

Author’s Comment: See 680.42(B) for the bonding methods permitted for outdoor spas and hot tubs.

(1) Metallic Parts of Structure. All metallic parts of the water structure, including the reinforcing metal of the permanently installed pool, outdoor spa, and outdoor hot tub shell and deck, must be bonded to the equipotential grid. The usual steel tie wires are considered suitable for bonding the reinforcing steel together for this purpose. Welding or special clamping is not required, but the tie wires must be made tight. Figure 680-4

Where the reinforcing steel of the permanently installed pool, outdoor spa, and outdoor hot tub shell and deck are encapsulated with a nonconductive compound or if it’s not available, an equipotential grid constructed in accordance with 680.26(C) must be installed to mask stray voltage gradients.


(2) Underwater Lighting. All metal forming shells for underwater permanently installed pool, outdoor spa, and outdoor hot tub luminaires and speakers.
(3) Metal Fittings. Metal fittings within or attached to the permanently installed pool, outdoor spa, and outdoor hot tub structure, such as ladders and handrails.
(4) Electrical Equipment. Metal parts of electrical equipment associated with the permanently installed pool, outdoor spa, and outdoor hot tub water circulating system, such as water heaters and pump motors. Accessible metal parts of listed equipment incorporating a system of double insulation and providing a means for grounding internal metal parts are not required to be directly bonded to the equipotential grid.
(5) Metal Wiring Methods and Equipment. Metal-sheathed cables and raceways, metal piping, and all fixed metal parts, as well as metallic surfaces of electrical equipment, must be bonded to the equipotential grid if located:
(1) Within 5 ft horizontally of the inside walls of the permanently installed pool, outdoor spa, and outdoor hot tub, and
(2) Within 12 ft measured vertically above the maximum water level of the permanently installed pool, outdoor spa, and outdoor hot tub, or any observation stands, towers, or platforms or any diving structures.




(A) Receptacles
(5) GFCI Protection. All 125V receptacles located within 20 ft. of the inside walls of a pool or fountain must be protected by a ground-fault circuit interrupter. Receptacles supplying pool pump motors rated 15 or 20A, single-phase, 120V through 240V must be provided with GFCI protection. Figure 680-5





Intent: The revised text is intended to clarify that GFCI protection is required for all 15 or 20A, 120V through 240V,240V circuits that supply single-phase receptacles for pool pump motors.

Courtest of Mike Holt Enterprises- Can you tell I am a huge fan of Mr. Holt...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 3/1/06 at 9:18 AM..
Reply With Quote
  #9  
Old 2/28/06, 12:57 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Pool Bonding


A new item (4) was added and it reads:

(A) Receptacles
(4) Restricted Space. One 15 or 20A, single-phase, 125V receptacle can be installed not less than 5 ft. measured horizontally from the inside wall of the pool at a dwelling unit, if the dimensions of the lot does not allow the receptacle outlet required in 680-22(A)(3) to be 10 ft. from the water. Figure 680-4
Intent: The new rule allows the required 15 or 20A, single-phase, 125V receptacle for outdoor pools and spas for dwelling units [680-22(A)(3)] to be located less than 10 ft., but not closer than 5 ft., from the pool, if the dimensions of the property prevent locating the receptacle 10 ft. away as required in 680.22(A)(3).

Courtesy of Mike Holt Enterprises



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 2/28/06, 11:15 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Bonding

Paul, the accepted method in 250.26(C)(3) NEC2005 for alternate means is a 12"x12" grid of #8 solid copper, joined at every intersection by a listed means.
In a practical sense you will use a welded wire ground mat. That is really a monitary prohibition on encapulated rebar and paver pool decks.
Over at ECN there are pictures of a job where they had to do one of these grids under pool pavers. I can try to track them down if you want to see it.
Reply With Quote
  #11  
Old 3/1/06, 6:05 AM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 274
Default Re: Pool Bonding

Paul or Greg,

In regards to the illustration above [NEC 680.26 (B)(1)]

(1) Does the equipment need to be bonded if it is to the side of the house, behind a concrete wall enclosure, Appoximately 15' away from the pool edge? What are the distances for bonding pool equipment? And how long has it been required?

There has been discussion on this before , I just forgot to bookmark the page.

Thanks!
Reply With Quote
  #12  
Old 3/1/06, 8:42 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Pool Bonding

Greg,

I would LOVE to see it......I would venture to say it is one of the accepted methods..but not THE accepted method...lol....Would you not agree....MOST certainly I would like to see it if you can get it for me...sad thing is I am out of the office today and do not have my 2005 handy.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 3/1/06 at 8:46 AM..
Reply With Quote
  #13  
Old 3/1/06, 8:51 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Pool Bonding

Here is the verbage update to 680.26

http://www.electrician.com/2005nec1/.../slide0556.htm



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 3/1/06, 2:51 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Bonding

http://electrical-contractor.net/ubb...ML/002086.html

This is the link to the discussion and the pictures of the job at the end
Reply With Quote
  #15  
Old 3/1/06, 4:54 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Pool Bonding

Thanks Greg....on that pre-fab mat.....looks like standard square fence metal myself that is connected together with split bolts...

It begs me to ask....since I am not in the office today does the 2005 NEC specify copper for this grid......and as stated I think 2002 leaves us without having to do this method......2005 most certainly expands it.

Thanks again greg on the link....the install that fella did looks nice, Have you heard any news on any newer updated products for this...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year

Last edited by pabernathy; 3/2/06 at 1:13 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
It's time for Professional Pool Inspections Revel L. Thom Ancillary Inspection Services & Additional Topics 13 7/26/07 11:50 AM
Pentair Water Pool Gas Heater Recall Gary Reecher Inspecting HVAC Systems 0 1/4/07 9:15 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 2:10 AM


All times are GMT -4. The time now is 3:45 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts