Default Re: Pool Bonding

680.26(C)(3)(a) says "The grid shall be constructed of minimum #8 AWG bare solid copper conductors ... bonded to each other at all points of crossing ... <per 680(D)> ... in accordance with 250.8" (exothermic welding, listed pressure connectors, listed clamps, or other listed means).
The ground mats are listed.
Reply With Quote
  #17  
Old 3/1/06, 4:49 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Bonding

This is new in 2005
Reply With Quote
  #18  
Old 3/1/06, 8:37 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Pool Bonding

Yep.....I was trying to get some info before I got back in the office to the 2005 NEC..but you answered it...thanks......talk about cost with the price of copper going up.......



Paul W. Abernathy
Reply With Quote
  #19  
Old 3/1/06, 11:31 PM
Harvey Gordon's Avatar
Harvey Gordon Harvey Gordon is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Margate, FL
Posts: 249
Default Re: Pool Bonding

Paul and Jeff...I believe then that I was mis-educated....unless this grid is recent...I was told that all was to be bonded back to the pool pump...now is that simply a work around?





Harvey Gordon
- President -
FloridaNACHI
(The OFFICIAL Florida State Chapter of NACHI)
SEFloridaNACHI
(Serving NACHI Members in Martin, Palm Beach, Broward, Miami-Dade, and Monroe Counties)
______________
Questions or Comments about FloridaNACHI or if you would like to start a LOCAL Florida Chapter may be sent directly to me at hgordon@fl.nachi.org
______________







Reply With Quote
  #20  
Old 3/1/06, 11:56 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Pool Bonding

Harvy,

The requirement for the bonding grid is not new, what greg is refering to has to do with an new addition to the 2005 NEC. The bonding of the grid to as listed in the previous responses are the same as they have been. With exception to a newly added verbage in 2002....

Hope that helps..



Paul W. Abernathy
Reply With Quote
  #21  
Old 3/2/06, 12:16 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Bonding

Harvey, they should be going to the pump in this grid. They may have just bought a new pump and didn't hook up the wire but it should be there. If not they have to run a wire to the grid. It may be able to be picked up at the underground light J box if they have a light.
Reply With Quote
  #22  
Old 4/24/06, 4:10 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Bonding

The grid that is required based on the '05 NEC is going to be a deal breaker for some pools, and I believe will create people finding a way around it. It will be an expensive addition to the pool itself, and pool sellers are not telling their clients about the requirement, until after the pool is almost installed.

Harvey
The bonding of pools is not quite the same as bonding of systems. The purpose of bonding at pools is to create an " Equipotential Bonding Grid".
This grid will keep all points at the same Potential. In other words, if there is an elevation in voltage in the pool area (lets say lightning hits around a mile away and it is traveling through the earth), the voltage elevation will be the same in all of the protected areas, so there is no potential... no potential means not current flow... even though there is a higher voltage in the area, because there is no current flow, all people are protected and safe from shock. That is the theory behind this.

One of the good things is this "Equipotential grid" is not required to be installed as one piece of conductor. It is bonding (which is another word for connection), so it can be installed in pieces.

Yes, one will need to bond to the pump motor, even if the pump motor and equipment may be 100 feet from the pool, as some pool equipment is installed at some distance from the pool for various reasons. If the bond conductor is installed at a remote location for the pump, the burial depth for the bond conductor is not stated in the NEC.
Reply With Quote
  #23  
Old 4/24/06, 4:56 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Bonding

This grid has to be #8 copper. It is a 2005 requirement.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
It's time for Professional Pool Inspections Revel L. Thom Ancillary Inspection Services & Additional Topics 13 7/26/07 10:50 AM
Pentair Water Pool Gas Heater Recall Gary Reecher Inspecting HVAC Systems 0 1/4/07 8:15 PM
Demystify Grounding & Bonding Class pabernathy Inspection Education & Training 5 12/24/06 1:10 AM


All times are GMT -4. The time now is 9:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts