#1
|
||||
|
||||
|
I would like to hear opinions from everyone, expert or not.
Do you believe the metal pool filter should be bonded to the rest of the equipment? Why or why not? I welcome any code interpretation you feel might be relevant. In this case, the filter is about 8 feet from the water, so let's stay away from the five-foot rule and focus on the "equipment." IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#2
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hmmm, well it is metal, but it is not electrical equipment as stated in 680.26(4). I think it would be a stretch to call it part of the electrical equipment associated with the recirculating water.
|
|
#3
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Besides, where would you drill a hole in the darn thing for a lug?
|
|
#4
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
It's not required to be bonded, and I can think of no benefit derived from bonding it at the distance from the pool you say it is.
|
|
#6
|
||||
|
||||
|
Well looking at the picture, there is separation from any metal piping that may connect the filter from the motor but there are signs of puddling in the area around the filter that head right over to the motor on the ground. I would mention, but not sure which direction I would head.
Stephen Stanczyk Washington State Licensed Home Inspector # 221 Structural Pest Inspectors License # 71043 Vice-President, Washington Association of Property Inspectors (WAPI) (253) 241-0602 calls answered until 10pm Safe Haven Inspections Puyallup Home Inspectors - Olympia Home Inspectors Tacoma Home Inspectors - Bellevue Home Inspectors Pierce County -Thurston County - King County - Snohomish County |
|
#7
|
||||
|
||||
|
I don't believe it's required, but I've had AHJ's disagree with me, which is why I'm starting the discussion.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Why would you care what the AHJ thought? Did you ask them if they have some local rule that modifies the base text?
|
|
#9
|
||||
|
||||
|
It's not about "caring" what they think. I'm trying to understand where their logic comes from.
I had been doing a "phase" inspection on a large custom home. After the pool and equipment was in (before the city inspector showed up), I inspected the installation - not for compliance, but for quality. The owner questioned my "qualifications" when the AHJ said the filter needed bonding and I hadn't mentioned it. The same type of issue came up again recently where the AHJ required bonding of the filter when some "other" work was being done on the property. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#10
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
They're just over stepping their bounds as an AHJ. Same old story. Happens to us electricians all the time on a variety of issues, and we resolve it by asking them for a code citation.
|
|
#11
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
I am curious.
How is a metal pool filter not associated with the "pool water circulating system"? In the picture, I see two pipes that I am assuming are carrying water circulating to the pool system. 680.26(B)(4)Electrical Equipment. Metal parts of electrical equipment associated with the pool water circulating system,..." I am not sure what the distance from the pool would have to do with this section...pool equipment is installed remote from pools all the time and still require bonding as per 680.26. |
|
#13
|
||||
|
||||
|
Thanks Pierre. That's the kind of thinking I'm looking for. I can understand that. I just don't see it as "metal parts of electrical equipment."
You are correct - the pipes are carrying water as part of the "water circulating system." So what's your position? IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#14
|
|||
|
|||
|
Quote:
"Never ever threaten anyone in Camoflage" Tim Wilson "Not everyone follows the same path" Governor Sanford, musings on the Appalachian Trail
|
|
#15
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The real question would be "how". Drilling a hole in the can would void the warranty and would need a gasket that would insulate the lug. You certainly couldn't connect a solid wire to a part that moves like the band or cover.
There is no code article that requires it |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| What do you think? Can this work for you? | jtedesco1 | Electrical | 13 | 2/9/09 11:58 PM |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical | 72 | 3/12/08 12:19 AM |
| Where is it written.... | bgromicko | General Inspection Discussion | 18 | 1/19/08 10:02 PM |
| Dwelling and Commercial Electrical Equipment | jtedesco1 | Electrical | 4 | 1/10/08 7:46 AM |