Default Pool Equipment Bonding

I would like to hear opinions from everyone, expert or not.

Do you believe the metal pool filter should be bonded to the rest of the equipment? Why or why not?

I welcome any code interpretation you feel might be relevant.

In this case, the filter is about 8 feet from the water, so let's stay away from the five-foot rule and focus on the "equipment."
Attached Thumbnails
pool-equipment-bonding-p3190001.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #2  
Old 3/19/08, 10:57 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Equipment Bonding

Hmmm, well it is metal, but it is not electrical equipment as stated in 680.26(4). I think it would be a stretch to call it part of the electrical equipment associated with the recirculating water.
Reply With Quote
  #3  
Old 3/19/08, 10:59 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Equipment Bonding

Besides, where would you drill a hole in the darn thing for a lug?
Reply With Quote
  #4  
Old 3/19/08, 11:00 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Pool Equipment Bonding

Quote:
Originally Posted by brian winkle
Besides, where would you drill a hole in the darn thing for a lug?
Don't get caught up in the details . In this case it would be difficult, but many of these older filters have a steel base that you could tap a lug to.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 3/19/08, 11:09 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Equipment Bonding

It's not required to be bonded, and I can think of no benefit derived from bonding it at the distance from the pool you say it is.
Reply With Quote
  #6  
Old 3/19/08, 11:17 PM
Stephen W. Stanczyk's Avatar
Stephen W. Stanczyk Stephen W. Stanczyk is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Kapowsin, WA
Posts: 2,826
Send a message via AIM to sstanczyk
Default Re: Pool Equipment Bonding

Well looking at the picture, there is separation from any metal piping that may connect the filter from the motor but there are signs of puddling in the area around the filter that head right over to the motor on the ground. I would mention, but not sure which direction I would head.




Stephen Stanczyk
Washington State Licensed Home Inspector # 221
Structural Pest Inspectors License # 71043
Vice-President, Washington Association of Property Inspectors (WAPI)
(253) 241-0602 calls answered until 10pm


Pierce County -Thurston County - King County - Snohomish County
Reply With Quote
  #7  
Old 3/19/08, 11:27 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Pool Equipment Bonding

I don't believe it's required, but I've had AHJ's disagree with me, which is why I'm starting the discussion.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 3/19/08, 11:32 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Equipment Bonding

Why would you care what the AHJ thought? Did you ask them if they have some local rule that modifies the base text?
Reply With Quote
  #9  
Old 3/20/08, 1:19 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Pool Equipment Bonding

It's not about "caring" what they think. I'm trying to understand where their logic comes from.

I had been doing a "phase" inspection on a large custom home. After the pool and equipment was in (before the city inspector showed up), I inspected the installation - not for compliance, but for quality.

The owner questioned my "qualifications" when the AHJ said the filter needed bonding and I hadn't mentioned it.

The same type of issue came up again recently where the AHJ required bonding of the filter when some "other" work was being done on the property.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 3/20/08, 1:23 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Equipment Bonding

They're just over stepping their bounds as an AHJ. Same old story. Happens to us electricians all the time on a variety of issues, and we resolve it by asking them for a code citation.
Reply With Quote
  #11  
Old 3/20/08, 4:26 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Equipment Bonding

Quote:
Originally Posted by jpope
I'm trying to understand where their logic comes from.
Their logic comes from their opinions rather than facts. As Marc said, this all too common.
Reply With Quote
  #12  
Old 3/20/08, 10:08 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Equipment Bonding

I am curious.
How is a metal pool filter not associated with the "pool water circulating system"?

In the picture, I see two pipes that I am assuming are carrying water circulating to the pool system.


680.26(B)(4)Electrical Equipment.
Metal parts of electrical equipment associated with the pool water circulating system,..."

I am not sure what the distance from the pool would have to do with this section...pool equipment is installed remote from pools all the time and still require bonding as per 680.26.
Reply With Quote
  #13  
Old 3/20/08, 10:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Pool Equipment Bonding

Thanks Pierre. That's the kind of thinking I'm looking for. I can understand that. I just don't see it as "metal parts of electrical equipment."

You are correct - the pipes are carrying water as part of the "water circulating system." So what's your position?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #14  
Old 3/20/08, 10:37 PM
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 11,730
Default Re: Pool Equipment Bonding

Quote:
National electrical standards require the metal filter in the equipment area to be attached to a common bonding wire that conveys errant electricity harmlessly to ground, which we recommend as a safety upgrade.
Boiler plate I use, bond it.



"Never ever threaten anyone in Camoflage"
Tim Wilson

"Not everyone follows the same path"
Governor Sanford, musings on the Appalachian Trail
Reply With Quote
  #15  
Old 3/20/08, 10:46 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool Equipment Bonding

The real question would be "how". Drilling a hole in the can would void the warranty and would need a gasket that would insulate the lug. You certainly couldn't connect a solid wire to a part that moves like the band or cover.
There is no code article that requires it
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What do you think? Can this work for you? jtedesco1 Electrical 13 2/9/09 11:58 PM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical 72 3/12/08 12:19 AM
Where is it written.... bgromicko General Inspection Discussion 18 1/19/08 10:02 PM
Dwelling and Commercial Electrical Equipment jtedesco1 Electrical 4 1/10/08 7:46 AM


All times are GMT -4. The time now is 5:52 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts