#1
|
|||
|
|||
|
If a receptalce for a pool motor is required to be on GFCI.
Is a pool motor that is hard wired required to be on GFCI? Also, is a salt water pool more likely to conduct electricity than a chlorine pool? "Arrogance and Ignorance are not mutually exclusive" |
|
#2
|
||||
|
||||
|
If not less than 10 feet from pool wall, it need not be GFCI. (See NEC 680.22A1) But then, 680.22A5 says GFCI is required for pool pump motors any distance from pool. hhhhhmnmmmmm?
I suppose, as home inspectors, we should consider the most conservative of the contradictions and say that it should be on a GFCI. James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Last edited by jbushart; 3/16/08 at 9:47 AM.. |
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
A hard wired pump does NOT need GFI protection, regardless of distance. At least up unitl the 2005 NEC. I'll have to go to the NFPA and check the 2008.
Most of us do protect pool motors though. It just makes everyone feel safer. EDIT: Yes, they changed the 2008 NEC to apply GFI protection to 15 and 20A, 120 and 240v, pump motors whether receptacle or direct connection. Last edited by Speedy Petey; 3/16/08 at 10:06 AM.. |
|
#4
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Oh, also, a salt water pool is NOT what you'd think. It's not even close to the salt levels in sea water so I doubt the water is much more conductive.
|
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Salt water pools are about 5-6 PPT salt (about the same as contact lens solution) but that is plenty of salt when talking about the ionization level.
|
|
#6
|
|||
|
|||
|
Very Interesting information.
Thank you "Arrogance and Ignorance are not mutually exclusive" |
|
#7
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#8
|
|||
|
|||
|
Pool pump motors are required to be bonded though, and I can't even tell you how many I find that have been replaced, and the bonding lug is just sitting there with nothing connected to it!
Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
|
#9
|
|||
|
|||
|
Please Note:
gmortensen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#10
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Boaters know 304 stainless (the hard stuff) will rust in salt water but it is usually just a surface rust. Still that will hasten the loss of pump seals.
|
|
#11
|
|||
|
|||
|
I known many people who just love swimming in Salt water pools. That includes me!! However I will not own a pool !
"Arrogance and Ignorance are not mutually exclusive" |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| This House Met Code. | jbushart | Electrical Inspections | 88 | 1/16/08 12:29 PM |
| More GFCI info from U/L | Greg Fretwell | Electrical Inspections | 9 | 12/4/07 8:33 PM |
| GFCI Safety Notice | rcooke | Electrical Inspections | 1 | 10/30/07 12:29 PM |