Default Pool pump bonding

Must a pool pump be bonded? (See the attached photo which would seem to answer my question.) If so, what would they bond it to? The ground rod was on the other side of the house and the plumbing pipes were PEX.

Why would that be necessary if the pump has a grounded (3 prong) power cord?

pool-pump-bonding-101609-057.jpg pool-pump-bonding-101609-058.jpg pool-pump-bonding-101609-056.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Find an InterNACHI certified Colorado Home Inspector (and anywhere else in North America)
  #2  
Old 10/16/09, 11:20 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: Pool pump bonding

I don't see many pools but this thread has a similar discussion:

http://www.nachi.org/forum/f19/pool-...111/#post23588



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 10/16/09, 11:28 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Pool pump bonding

Doesn't look like there's much to bond on this pool, with the exception of the pump motor.

pool-pump-bonding-101609-012.jpg



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 10/17/09, 4:26 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Pool pump bonding

Yes, generally on a permenent installed pool with pool pump motors you would indeed bond the pool pump motor. It gets bonded to the equipotential plane that is required at the pool.
Quote:
680.26(B) Bonded Parts.
Quote:
The parts specified in 680.26(B)(1)
through (B)(7) shall be bonded together using solid copper
conductors, insulated covered, or bare, not smaller than
8 AWG or with rigid metal conduit of brass or other identified
corrosion-resistant metal. Connections to bonded
parts shall be made in accordance with 250.8. An 8 AWG or
larger solid copper bonding conductor provided to reduce
voltage gradients in the pool area shall not be required to be
extended or attached to remote panelboards, service equipment,
or electrodes.
(6) Electrical Equipment.
Metal parts of electrical equipment
associated with the pool water circulating system,
including pump motors and metal parts of equipment associated
with pool covers, including electric motors, shall be
bonded.
Exception: Metal parts of listed equipment incorporating
an approved system of double insulation shall not be
bonded.
(a) Double-Insulated Water Pump Motors. Where a
double-insulated water pump motor is installed under the
provisions of this rule, a solid 8 AWG copper conductor of
sufficient length to make a bonding connection to a replacement
motor shall be extended from the bonding grid to an
accessible point in the vicinity of the pool pump motor.
Where there is no connection between the swimming pool
bonding grid and the equipment grounding system for the
premises, this bonding conductor shall be connected to the
equipment grounding conductor of the motor circuit.
(b) Pool Water Heaters. For pool water heaters rated
at more than 50 amperes and having specific instructions
regarding bonding and grounding, only those parts designated
to be bonded shall be bonded and only those parts
designated to be grounded shall be grounded.




Hope this helps....




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 10/17/09, 1:29 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,830
Send a message via Yahoo to jfunderburk
Default Re: Pool pump bonding

Thanks guys for your input. It seems it all hangs on the definition of "permanently installed" pool. This is an above ground and probably doesn't meet that def. If you disagree, please let me know.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #6  
Old 10/17/09, 4:02 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool pump bonding

Per 680 Definitions

Permanently installed swimming, wading, and therapeutic pools. Those that are constructed in the ground or partially in the ground, and all others capable of holding water in a deppt greater than 1 meter (42 inches), and all pools installed inside of a building, regardless of water depth, whether or not served by electrical circuits of any nature.

I would say the pool shown meets that definition.
Reply With Quote
  #7  
Old 10/18/09, 1:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Pool pump bonding

I agree with Jim.....if deeper than 42 inches and is most certainly falling under the "All Others" label...it would be permenent to me and my electrical inspectors.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #8  
Old 10/18/09, 3:02 PM
Linas I. Dapkus's Avatar
Linas I. Dapkus Linas I. Dapkus is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Lockport, IL
Posts: 3,730
Default Re: Pool pump bonding

Here's a couple of pics of my pool (above ground) pump bonding wire. The electrician attached it to the base of the pool.
Attached Thumbnails
pool-pump-bonding-img_4922.jpg   pool-pump-bonding-img_4923.jpg  
Reply With Quote
  #9  
Old 10/18/09, 5:26 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,701
Default Re: Pool pump bonding

Don't ask me why, or what the difference is, but above ground does not require the same bonding as in ground.
The second is "closer to ground" than either.???!!!

A pool is a pool.
I think they all should be bonded, but this is about code which "holds little water with me" (pun intended)!



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues 50 4/20/08 2:26 AM
This House Met Code. jbushart Electrical 76 1/16/08 1:28 PM
Pool Bonding hgordon Electrical 22 4/24/06 5:56 PM


All times are GMT -4. The time now is 5:26 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts