Default Pool supply

I am going to install a new electrical supply for the pool equipment. The existing was laid under a slab that has been removed and will not be replaced. The junction box at the equipment will service the two one hp motors, light and a blower. I will also have seven landscape lights. I plan to bury the line 18" pull two black one white #8 and a #12 ground. Question is, is this good enough or "over kill" Thanks
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/2/10, 10:54 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool supply

Could you provide some further details? Type of conduit? Lights and conduit distance from edge of pool? Type of lighting?

First thing that seems to be a problem is the #12 EGC with the #8 phase and neutral conductors. If these are 20 amp circuits then 250.122(B) would require that the EGC be the same size as the other conductors.
Reply With Quote
  #3  
Old 3/2/10, 9:32 PM
gfitzgerald's Avatar
gfitzgerald gfitzgerald is offline
Active Poster
 
Join Date: Jun 2009
Location: Sherman Oaks Ca.
Posts: 335
Please Note: gfitzgerald is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool supply

My brain kicked in I remember I need the same size ground as the conductors. The run is 70 ft. berried 18" 4' away from the pool.The lights are pole lamps so I can't use low voltage. The pipe is rigid I will use a WP J box to feed the equipment disconnect and the light circuit. What I was wondering is the # 8 over kill ??
Reply With Quote
  #4  
Old 3/3/10, 11:28 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Pool supply

Just to chime in.......when dealing with NEC 250.122(B) we are figuring a ratio situation where we increased the size of the ungrounded conductors for a variety of conditions ( voltage drop might be one of them ) and in doing so we have to increase the size of the EGC in a ratio proportionally to what would have been required if we sized it normally to the load itself.

let me flavor you an example.......

Calculation Example
A 240-volt, single-phase, 250-ampere load is supplied from a 300-ampere breaker
located in a panelboard 500 ft away. The conductors are 250-kcmil copper, installed in rigid nonmetallic conduit, with a 4 AWG copper equipment grounding conductor. If
the conductors are increased to 350 kcmil, what is the minimum size for the equipment
grounding conductor based on the proportional-increase requirement?
Solution
STEP 1.
Calculate the size ratio of the new conductors to the existing conductors:

350,000 cmil (divided by ) 250,000 cmil = 1.4 Ratio
STEP 2.
Calculate the cross-sectional area of the new equipment grounding conductor:
According to Chapter 9, Table 8, 4 AWG, the size of the existing grounding
conductor, has a cross-sectional area of 41,740 circular mils.

41,740 x 1.4 ratio = 58,463 cmil
STEP 3.
Determine the size of the new equipment grounding conductor. Again, referring to
Chapter 9, Table 8, we find that 58,436 circular mils is larger than 3 AWG. The next
larger size is 66,360 circular mils, which converts to a 2 AWG copper equipment
grounding conductor.

So you see....2 AWG is not the same size as the ungrounded conductors...but it is increased proportinally based on the requirements of NEC 250.122(B). The example is straight out of the NEC Handbook if anyone is wondering



Paul W. Abernathy
Reply With Quote
  #5  
Old 3/4/10, 7:14 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,251
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pool supply

Quote:
Originally Posted by gfitzgerald View Post
My brain kicked in I remember I need the same size ground as the conductors. The run is 70 ft. berried 18" 4' away from the pool.The lights are pole lamps so I can't use low voltage. The pipe is rigid I will use a WP J box to feed the equipment disconnect and the light circuit. What I was wondering is the # 8 over kill ??

It might be overkill and it might not. If you want to check for voltage drop you can use a simple calculator like this one:

http://www.elec-toolbox.com/calculators/voltdrop.htm

Is this an in-ground pool? If so the underground conduit must be 5' from the inside edge of the pool unless feeding equipment in the pool such as an underwater light. Take a look at 680.10.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
HELP! What do you call a 3 prong male plug with a cord. gromicko Electrical Inspections 5 1/9/09 12:33 AM
Pool Executive Charged in Drain Death jhagarty Ancillary Inspection Services & Additional Topics 1 7/23/08 11:15 PM
This House Met Code. jbushart Electrical Inspections 88 1/16/08 12:29 PM
Pentair Water Pool Gas Heater Recall Gary Reecher Inspecting HVAC Systems 0 1/4/07 8:15 PM


All times are GMT -4. The time now is 9:18 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts