I am going to install a new electrical supply for the pool equipment. The existing was laid under a slab that has been removed and will not be replaced. The junction box at the equipment will service the two one hp motors, light and a blower. I will also have seven landscape lights. I plan to bury the line 18" pull two black one white #8 and a #12 ground. Question is, is this good enough or "over kill" Thanks
|
| Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Could you provide some further details? Type of conduit? Lights and conduit distance from edge of pool? Type of lighting?
First thing that seems to be a problem is the #12 EGC with the #8 phase and neutral conductors. If these are 20 amp circuits then 250.122(B) would require that the EGC be the same size as the other conductors. |
|
#3
|
||||
|
||||
|
Please Note:
gfitzgerald is a non-member guest and is in no way affiliated with InterNACHI or its members.
My brain kicked in
|
|
#4
|
|||
|
|||
|
Just to chime in.......when dealing with NEC 250.122(B) we are figuring a ratio situation where we increased the size of the ungrounded conductors for a variety of conditions ( voltage drop might be one of them ) and in doing so we have to increase the size of the EGC in a ratio proportionally to what would have been required if we sized it normally to the load itself.
let me flavor you an example....... Calculation Example A 240-volt, single-phase, 250-ampere load is supplied from a 300-ampere breaker located in a panelboard 500 ft away. The conductors are 250-kcmil copper, installed in rigid nonmetallic conduit, with a 4 AWG copper equipment grounding conductor. If the conductors are increased to 350 kcmil, what is the minimum size for the equipment grounding conductor based on the proportional-increase requirement? Solution STEP 1. Calculate the size ratio of the new conductors to the existing conductors: 350,000 cmil (divided by ) 250,000 cmil = 1.4 Ratio STEP 2. Calculate the cross-sectional area of the new equipment grounding conductor: According to Chapter 9, Table 8, 4 AWG, the size of the existing grounding conductor, has a cross-sectional area of 41,740 circular mils. 41,740 x 1.4 ratio = 58,463 cmil STEP 3. Determine the size of the new equipment grounding conductor. Again, referring to larger size is 66,360 circular mils, which converts to a 2 AWG copper equipmentChapter 9, Table 8, we find that 58,436 circular mils is larger than 3 AWG. The next grounding conductor. So you see....2 AWG is not the same size as the ungrounded conductors...but it is increased proportinally based on the requirements of NEC 250.122(B). The example is straight out of the NEC Handbook if anyone is wondering Paul W. Abernathy |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
It might be overkill and it might not. If you want to check for voltage drop you can use a simple calculator like this one: http://www.elec-toolbox.com/calculators/voltdrop.htm Is this an in-ground pool? If so the underground conduit must be 5' from the inside edge of the pool unless feeding equipment in the pool such as an underwater light. Take a look at 680.10. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| HELP! What do you call a 3 prong male plug with a cord. | gromicko | Electrical Inspections | 5 | 1/9/09 12:33 AM |
| Pool Executive Charged in Drain Death | jhagarty | Ancillary Inspection Services & Additional Topics | 1 | 7/23/08 11:15 PM |
| This House Met Code. | jbushart | Electrical Inspections | 88 | 1/16/08 12:29 PM |
| Pentair Water Pool Gas Heater Recall | Gary Reecher | Inspecting HVAC Systems | 0 | 1/4/07 8:15 PM |