  #1  
Old 1/31/10, 11:44 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default power company temporary repair to get 120/240V from 120V

An engineer client told me about his dad's power problem at 2am during very cold weather. One of the underground hot conductors burned out going to his house. The power company came out with what they called a "regenerator" on a handtruck. It was actually a 180 degree phase shift transformer with the primary connected to the good leg and neutral. The secondary connected to the other house leg and the neutral. This provided the full 120/240 service at enough current capability until they could send out the repair truck.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Need a home inspection in Delaware? Check out InterNACHI's listing of Delaware certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 2/1/10, 8:41 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: power company temporary repair to get 120/240V from 120V

Interesting...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 2/1/10, 9:27 AM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,908
Default Re: power company temporary repair to get 120/240V from 120V

I am just wondering why it was so important to use it rather than wait for repair.
Reply With Quote
  #4  
Old 2/1/10, 10:22 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: power company temporary repair to get 120/240V from 120V

Likely that a 240 v heat pump system was the only heat in the house.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 2/1/10, 8:21 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: power company temporary repair to get 120/240V from 120V

Another problem that occured recently to someone I know a few hours away, her meter panel fried at one incoming leg, the power company declined to repair it because it had been double tapped. They cut off both incoming legs up at the roof mast and left her in total darkness, they (actually a subcontractor for the power company) handed her a business card with an electricians name on it and said they would come back and reconnect the feed when repairs were finished. The electrician and helper worked at night during the cold snap and had to come back for a 2nd trip for some reason, the bill was $1700.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got a letter from ASHI's President today. gromicko General Inspection Discussion 55 12/12/10 11:51 PM
screw lolly column rjack1 Structural Inspections 27 1/23/10 10:22 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM