This is a mother-in-law new construction add-on to main home.

At the panel, 50 amp breaker labeled for range is wired with 3 conductor CU. The two (2) #6 awg are connected to the breaker, with the smaller bare #12 conductor spliced and extended to the neutral bus.

Shouldn't the 'neutral' be the same size as the 2 hots?
Shouldn't 4 wire conductor have been used so it would be grounded?

Also, the conductors for upper right 60 amp breaker are not the right size !

Thanks,
Attached Images
File Type: jpg 101_2339a.jpg (72.6 KB, 54 views)
File Type: jpg 101_2339b.jpg (78.3 KB, 45 views)



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

TREC #7654
InterNACHI #06032691

Reply With Quote
  #2  
Old 10/24/08, 11:51 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,301
Richard L. Bennett .
Default Re: Power supply for range

Yes and No

Range mfg is god in this case -- New ranges can be wired as three or four wire. Remember a lot of old homes that need new ranges are three wire and new homes and some up grades are four wire

So the answer is Yes and No

rlb
Reply With Quote
  #3  
Old 10/24/08, 11:53 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,301
Richard L. Bennett .
Default Re: Power supply for range

Neutral wire size is OK

Can't address the other question because to the pix size

rlb
Reply With Quote
  #4  
Old 10/25/08, 10:10 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 200
Pierre Belarge is generally well trusted
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Power supply for range

As per code (250.140), new installations of ranges and dryers are required to be installed with 4 conductors.

Existing ranges/dryers wiring is permitted to stay as the wiring was installed.

If, as you stated this is a new installation, the number of conductors to the range is incorrect.


Note:
Is the bus connecting the lefthand side of the neutral bus still bonded to the righthanded side, the equipment ground side? If so, that should also be corrected.


Are the cables of NM? If so, the conductor ampacity is restricted to the 60C column of Table 310.16 for sizing.
Reply With Quote
  #5  
Old 10/25/08, 11:03 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Power supply for range

That is X/2NM cable. The bare wire is NOT a neutral. They simply (and incorrectly) used a piece of #12 white to extend the #10 bare GROUND.

IF, and only if, this is a straight 240v oven, then this is all fine except for the undersized ground jumper.

If, as Pierre says, this is 120/240v range or similar appliance it is extremely incorrect and unsafe.

Even if this was a old 120/240v installation, it would not have been code. X/2NM cable was never allowed to be used as a "3-wire" range or dryer circuit. The bare GROUND in NM cable was never allowed to carry circuit current.
The only time this was allowed was if type SEU cable was used. SEU cable has a bare neutral, and no ground.
Reply With Quote
  #6  
Old 10/25/08, 12:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,897
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Power supply for range

Quote:
Originally Posted by Speedy Petey View Post
That is X/2NM cable. The bare wire is NOT a neutral. They simply (and incorrectly) used a piece of #12 white to extend the #10 bare GROUND.

IF, and only if, this is a straight 240v oven, then this is all fine except for the undersized ground jumper.

If, as Pierre says, this is 120/240v range or similar appliance it is extremely incorrect and unsafe.

Even if this was a old 120/240v installation, it would not have been code. X/2NM cable was never allowed to be used as a "3-wire" range or dryer circuit. The bare GROUND in NM cable was never allowed to carry circuit current.
The only time this was allowed was if type SEU cable was used. SEU cable has a bare neutral, and no ground.
What he said.

There remains the possibility that this is a straight 240 volt range, but they are normally only the little 24" apartment ranges and commercial ranges that are straight 240. I'd seriously doubt this is a 240 volt range, though, unless it looks abnormal to you. This is more than likely just an improperly connected ordinary range.
Reply With Quote
  #7  
Old 10/25/08, 1:38 PM
Linda J. Foster's Avatar
Linda J. Foster Linda J. Foster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 341
Linda J. Foster is generally well trusted
Default Re: Power supply for range

This is for a new standard home range. GE brand, smooth top electric.

It didn't look right to me.
Panel labeling is suspect (no biggie)
The bonding screw should be removed also.

I'll call for evaluation by qualified electrician of all that was done.

The contractor that did all this has been fired. Over budget and time frame. Kept pushing the pencil on the owner.

Thanks for all the input. Sure is great !!



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

TREC #7654
InterNACHI #06032691

Reply With Quote
  #8  
Old 10/25/08, 1:38 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 286
John Allingham is generally well trusted John Allingham is generally well trusted
Default Re: Power supply for range

Quote:
Originally Posted by Speedy Petey View Post
IF, and only if, this is a straight 240v oven, then this is all fine except for the undersized ground jumper.
Is this a sub-panel? If so, shouldn't the undersized ground jumper at least go to the grounding bus bar i.e. separated from the neutrals.
Still trying to learn.
Reply With Quote
  #9  
Old 10/25/08, 1:47 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Power supply for range

Quote:
Originally Posted by jallingham View Post
Is this a sub-panel? If so, shouldn't the undersized ground jumper at least go to the grounding bus bar i.e. separated from the neutrals.
Still trying to learn.
Actually yes. I missed that in the pic.
Reply With Quote
  #10  
Old 10/25/08, 1:47 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Power supply for range

Quote:
Originally Posted by lfoster View Post
This is for a new standard home range. GE brand, smooth top electric.
Then this is an extremely non-compliant installation and should be called out as unsafe.
Reply With Quote
  #11  
Old 10/25/08, 2:29 PM
Linda J. Foster's Avatar
Linda J. Foster Linda J. Foster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 341
Linda J. Foster is generally well trusted
Default Re: Power supply for range

This is a subpanel. Power supplied from original home panel.

The whole addition has some problems. Owner wanted to use overhead garage doors on one wall to take advantage of the view at times. Trouble is the floor is flat (not dropped down at the o.h. doors), and can't seal sides or bottom well enough.

She also wanted ceiling fans, so the overhead doors will only open up about 3 feet before hitting the shaft of the ceiling fan.

Contractor saved couple hundred finding damaged A/C condenser, but the coils are damaged.

Jacuzzi tub looks to have been at a scratch & dent. The top deck is scratched and has a chunk missing on one corner.

It goes on and on.



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

TREC #7654
InterNACHI #06032691

Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

Similar Threads
Thread Thread Starter Forum Replies Last Post
no power Mirror image Electrical 11 10/19/08 10:59 PM
Power Supply to Subpanel Mick D. Jones Electrical 6 8/27/08 5:55 PM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical 72 3/12/08 12:19 AM
Selected Electrical Incidents and Occurrences - First Quarter pabernathy Electrical 0 12/2/07 2:43 PM
Emergency Lighting (commercial) mcyr Electrical 24 6/10/06 11:06 AM


All times are GMT -4. The time now is 5:59 PM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics