I have a sub panel that is powered by wires tapped directly into the main lugs of the main panel. My inspector pointed this out but an electrician is saying it's ok. Does anyone have a code saying one way or the other. I found your site and it seems like there are some electricians on here.
|
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Please post your pictures.
What was the distance from that bus tap to the breaker it terminated on in the subpanel? This can be legal, but there are distance and a few other limitations. The typical violation of what you describe would be if those lugs were double tapped, which I might guess they were. Darned few lugs are rated for more than one large conductor in the sizes we're likely dealing with in this scenario. |
|
#3
|
||||
|
||||
|
Yes, there are codes that address the issue(s). One with regards to the listing of the lugs - whether they're rated for more than one conductor, and another referencing the requirement for a disconnect, and yet another for appropriate over-current protection for the conductors supplying the panel.
Do you have a picture? IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
|||
|
|||
|
Please Note:
Mick D. Jones is a non-member guest and is in no way affiliated with InterNACHI or its members.
I don't have a picture right now. I'm not home to take a picture it is a push matic box? The house was built in the late 50's early 60's. The aluminum wires come in to the main lugs and there is braided copper wires attached there.
|
|
#5
|
||||
|
||||
|
Quote:
|
|
#6
|
|||
|
|||
|
if I understand you correctly they tapped the main lugs before the main disconnect if so they cannot disconnect the sub panel with the main breaker in the main panel and this would be a violation. The Pushmatic lugs would not be rated for a double tap the buss would have to be tapped and lugs installed or a breaker installed in the body of the panel used to disconnect the sub panel.
|
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Power to subpanel | lfoster | Electrical Inspections | 2 | 4/3/08 2:11 PM |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical Inspections | 72 | 3/12/08 12:19 AM |
| Selected Electrical Incidents and Occurrences - First Quarter | pabernathy | Electrical Inspections | 0 | 12/2/07 2:43 PM |
| supply in slab or walls? | jeubank | Plumbing Inspections | 1 | 7/8/06 11:36 AM |
| Emergency Lighting (commercial) | mcyr | Electrical Inspections | 24 | 6/10/06 11:06 AM |