Default Power tripped without touching breaker

Is it possible to trip a main breaker (Bryant panel) without the main breaker popping over?

I took the dead front off a main today and the power went off. There was no click (unless my hearing is going) , no sparks, no burns, no smoke and all the breakers remained in the "ON" position. Yet no power!

The homeowner turned the main off and then on again and everything was fine.

I have never had this happen before and was wondering what could have caused this and has this happened to anyone else?
Reply With Quote
  #2  
Old 6/28/06, 9:33 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is online now
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,223
Default Re: Power tripped without touching breaker

I think that breaker has a problem. If you had bumped it, it would have moved. If you would have caused an overcurrent condition you would have known it. It is possible for the internal portion to trip without moving the handle but not a common occurence for what you describe. I would have recommended consulting an electrician and consider replacement of the breaker regardless of the results of any "checking".
Reply With Quote
  #3  
Old 6/28/06, 11:08 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
Active Poster
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 260
Default Re: Power tripped without touching breaker

Thanks for input Bruce!

I have recommended evaluation and seller is being very willing to have it looked at.
Reply With Quote
  #4  
Old 6/29/06, 1:12 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Power tripped without touching breaker

Shawn,

I had an EXACT call like that yesterday, The client called me and said she did not have power to her Kitchen Counter for nearly (3) weeks and so I made a visit to her house.

She tells me the receptacle in the kitchen sparked and then that was it...so I first removed the recept. in the kitchen and checked it rather fast with my non-contact ticker....no power...I said...ok....(2) things....

1.) Something is wrong in the WALL......or
2.) Something is wrong in the Panel.........

So rather than pulling out receptacles that are DEAD ( I am not cheap so that saved here some money ) I went right to the panel.

Sure enough...all the breakers were in the "ON" position and nothing was tripped.......BUT before I mess with them I use my TICKER at every breaker terminal point....to make sure the breakers are REALLY on.....

Sure enough........got to (1) 20A breaker and it was on.....but NO output voltage.........went to trip that one OFF....and it did.....clicked it BACK on and the power was fine........defective or becoming defective breaker so I replaced it.......done service call.

Moral is.......Circuit breakers have a life span, I personally like to see them 20 years or older replaced with newer ones.....but again thats just me....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 6/29/06, 1:19 PM
rcooke rcooke is offline
Banned for Violating COE
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 9,381
Please Note: rcooke is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Power tripped without touching breaker

Quote:
Originally Posted by pabernathy
Shawn,

I had an EXACT call like that yesterday, The client called me and said she did not have power to her Kitchen Counter for nearly (3) weeks and so I made a visit to her house.

She tells me the receptacle in the kitchen sparked and then that was it...so I first removed the recept. in the kitchen and checked it rather fast with my non-contact ticker....no power...I said...ok....(2) things....

1.) Something is wrong in the WALL......or
2.) Something is wrong in the Panel.........

So rather than pulling out receptacles that are DEAD ( I am not cheap so that saved here some money ) I went right to the panel.

Sure enough...all the breakers were in the "ON" position and nothing was tripped.......BUT before I mess with them I use my TICKER at every breaker terminal point....to make sure the breakers are REALLY on.....

Sure enough........got to (1) 20A breaker and it was on.....but NO output voltage.........went to trip that one OFF....and it did.....clicked it BACK on and the power was fine........defective or becoming defective breaker so I replaced it.......done service call.

Moral is.......Circuit breakers have a life span, I personally like to see them 20 years or older replaced with newer ones.....but again thats just me....
I new an electrician like that Got rid of a great 40 year old wife got
two 20 year old girl friends then found out he was not wired for 220


Roy sr.
Reply With Quote
  #6  
Old 6/29/06, 1:21 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Power tripped without touching breaker

lol........yeah well If I did that......I am 100% my BREAKER would not RESET



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 6/29/06, 4:43 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
Active Poster
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 260
Default Re: Power tripped without touching breaker

Update...

Electrician went out today and found nothing wrong. I did speak to him and explained what happened. He said that he checked all connections and inspected the panel and there were no problems. He did admit that the main breaker was very tough to move and said that the "Bryant" breaker should have moved when tripped (which it did NOT).

Paul, this would be a good house for your rule of thumb, the home is about 35 years old with no upgrade to the electrical system.

Electrician told me he was going to write a letter stating everything was fine.

Not much more for me to do now.
Reply With Quote
  #8  
Old 6/29/06, 7:01 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Power tripped without touching breaker

Quote:
Originally Posted by srowe
Update...
He did admit that the main breaker was very tough to move and said that the "Bryant" breaker should have moved when tripped (which it did NOT).
Which is a GOOD reason to replace it.....breakers are CHEAP......LIFE is not !



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #9  
Old 6/29/06, 10:45 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
Active Poster
 
Join Date: Jul 2003
Location: East Northport, NY
Posts: 741
Default Re: Power tripped without touching breaker

Its probably a good thing if a breaker trips internally when it starts to go bad ...

P.S. A breaker should still trip internally when overloaded (with a few exceptions like FPE ... lol) even if the handle is jambed/locked in the ON position.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 6/29/06 at 10:55 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Guru Question? Breaker lock outs pdoane Electrical 4 9/7/07 3:05 PM
Double Tapped Breaker tjohnson3 Electrical 8 4/20/07 10:04 AM
No power vsantos Electrical 18 4/17/07 3:11 PM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 1:24 PM
Emergency Lighting (commercial) mcyr Electrical 24 6/10/06 11:06 AM


All times are GMT -4. The time now is 10:15 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts