I am doing an inspection on Saturday. Dropped off the radon monitor this morning, and took the opportunity to check out the house while I was there.

I noticed, that in the garage, (opposite the meter) there was a panel with a single shut off. It appears that this is the main.

In the basement, the panel with all the breakers for the home also has a "Main" shut off.

I haven't opened the panels yet, but will do so on Saturday. When I examine this further, should this be wired with the single breaker in the garage being the "Main" panel, and the one in the basement as a sub? I'm thinking thats what it is, and how it should be, but wanted to make sure.

Also if this is the case, the neutrals and grounds should be separate in the sub, with no panel bonding on the neutral bar, and no ground and neutral connection correct?



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #2  
Old 9/18/08, 1:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Preliminary question:

Quote:
Originally Posted by mnahrgang View Post
When I examine this further, should this be wired with the single breaker in the garage being the "Main" panel, and the one in the basement as a sub? I'm thinking thats what it is, and how it should be, but wanted to make sure.

Also if this is the case, the neutrals and grounds should be separate in the sub, with no panel bonding on the neutral bar, and no ground and neutral connection correct?
Yes.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 9/18/08, 2:58 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Preliminary question:

I find main SE's in many garages.

You sound like you know what you're looking for. The LSE should contain bonded grounds with floating neutrals.
Reply With Quote
  #4  
Old 9/20/08, 4:08 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Preliminary question: UPDATE

Ok, heres an update with the picks. It seems to me that the first panel (pics 1 & 2) is simply a pass through, with a whole house shutoff, and is not actually a "main" panel.

The second panel (pics 3 & 4) actually acts as the "main" panel. Can that be right? I did see the double taps, double neutrals and the neutral/grounds doubled.

So is this a main panel followed with a sub panel (that has it's neutrals and grounds incorrectly on the same bus bar), or is it a pass through panel (1&2), with the main panel (3 & 4) generally wired ok with the exception of the doubles?

I'm confusing myself Can someone help?

Thanks
Attached Thumbnails
preliminary-question-p1010609.jpg   preliminary-question-p1010613.jpg   preliminary-question-p1010615.jpg   preliminary-question-p1010619.jpg  



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #5  
Old 9/20/08, 5:48 PM
rbrady's Avatar
rbrady rbrady is offline
Active Poster
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Preliminary question:

Looks like the neutral and ground should be separated to me. The problem/issue is that the neutral wire and the ground wire between the two panels create a parallel circuit. Any current going through the neutral wire will be split between the neutral and ground wires. Anytime current passes through a wire you have a voltage drop, so the ground is no longer 'at ground potential'.
Reply With Quote
  #6  
Old 9/20/08, 6:05 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Preliminary question: UPDATE

Quote:
Originally Posted by mnahrgang View Post
So is this a main panel followed with a sub panel (that has it's neutrals and grounds incorrectly on the same bus bar...?

Thanks
Yes, the first is the service equipment (main) that contains the service disconnect and the next is loadside equipment (sub) where the grounded conductors (neutrals) can not be grounded.

Typically, neutrals are to be grounded only at the service equipment (with some exceptions that I am not familiar with).



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 9/20/08 at 6:09 PM..
Reply With Quote
  #7  
Old 9/20/08, 6:11 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Preliminary question:

That basement panel is improperly fed and wired. Since the service disconnect is in the garage, the basement panel should be fed with 4-wire and the grounds and neutrals separated.
Reply With Quote
  #8  
Old 9/20/08, 10:04 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Preliminary question:

Thanks guys! I really appreciate it!



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #9  
Old 9/21/08, 12:09 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Preliminary question:

The "whole house disconnect" is the service equipment. Everything else is a "sub" panel (load side equipment) and should have isolated neutrals and bonded grounds.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 9/21/08, 6:25 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Preliminary question: UPDATE

Quote:
Originally Posted by mnahrgang View Post

I'm confusing myself Can someone help?

Thanks
Mark,

Another way to un-confuse yourself in determining which panel is the SE, is to look for the panel that is right after/behind the exterior meter. That will be your SE panel. From there you can determine the validity of the wiring methods that are being used in the LSE and the SE's.
Reply With Quote
  #11  
Old 9/21/08, 8:49 AM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Preliminary question: UPDATE

Quote:
Originally Posted by dvalley View Post
Mark,

Another way to un-confuse yourself in determining which panel is the SE, is to look for the panel that is right after/behind the exterior meter. That will be your SE panel. From there you can determine the validity of the wiring methods that are being used in the LSE and the SE's.
Thanks again guys. That's where I was at. What got me confused was the LSE was wired like I see most SE wired. And then there were problems there too.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #12  
Old 9/21/08, 10:58 AM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Preliminary question:

I think you guys missed the most important aspect of the inspection he has the "Handyman club of America" sticker right on the panel. That is a huge red flag! When I am told, O yea I am a handyman or my dad was a GC, electrician, plumber.... I just shrill inside!
Reply With Quote
  #13  
Old 9/21/08, 1:52 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Preliminary question:

Quote:
Originally Posted by rhensel View Post
I think you guys missed the most important aspect of the inspection he has the "Handyman club of America" sticker right on the panel. That is a huge red flag! When I am told, O yea I am a handyman or my dad was a GC, electrician, plumber.... I just shrill inside!
That concerned me at the beginning too , but I believe the owner. He is a retired county inspector. When I shared my concerns with him, he didn't sound surprised and said that he had never been in the boxes himself. There were numerous upgrades to the home, many documented to be "professional" and many of the "homeowner" upgrades were done well. Over all, the house was very well taken care of. I think this foul up happened at construction (17 years ago) and no one caught it originally, and no one since then paid any attention to the fact that it didn't look right. (I'm actually feeling kind of smug this weekend. Even though I confused myself, I did recognise something wasn't right, and thats really what we are being paid for.)



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #14  
Old 9/21/08, 6:49 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Preliminary question:

Nothing wrong with confusion....Not knowing and admitting it and finding the correct answer is what it is all about...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
Basement Bathroom Venting Question Sean M. Jeric Plumbing Inspections 4 3/20/07 11:56 PM
National Certification Program - Preliminary discussion to Bill Mullen presentation. Bill Mullen Canadian Inspectors 134 12/22/06 11:08 PM


All times are GMT -4. The time now is 9:19 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts