Default Is this a problem???

The local sparky and the local AHJ says these double taps are not a problem.
Attached Thumbnails
problem-100_6180.jpg   problem-100_6181.jpg  



Mid America Property Inspections, Inc.
Shawnee, KS 66217
www.mapii.com
NACHI # 05110992
KHIRB # 0110-0008
KS-Radon Cert.# KS-MS-0035
KS-Termite Cert. # 18933
M0-Termite Cert. # N 5033

Reply With Quote
Find an InterNACHI certified Arizona Home Inspector (and anywhere else in North America)
  #2  
Old 10/9/09, 8:48 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 739
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a problem???

Sounds like at least two more people need a Code update class or read the label inside the panel.
Reply With Quote
  #3  
Old 10/9/09, 9:19 PM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 5,393
Default Re: Is this a problem???

so they are kidding ...right?



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #4  
Old 10/9/09, 9:21 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 6,929
Default Re: Is this a problem???

ARTICLE 408 Switchboards and Panelboards

408.41 Grounded Conductor Terminations.

Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.

Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.



Christopher Currins
Certified, Licensed

Proudly serving the Illinois Metro-East

Illinois Home Inspector

Top 5 Tasks for January
Reply With Quote
  #5  
Old 10/9/09, 9:23 PM
kluce kluce is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Highland, Indiana
Posts: 265
Please Note: kluce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a problem???

It hard to say what you are talking about since everything looks good.

If you are talking about the neutral and ground wires, it's fine.
Reply With Quote
  #6  
Old 10/9/09, 9:24 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Is this a problem???

Quote:
Originally Posted by kluce View Post
If you are talking about the neutral and ground wires, it's fine.
In what part of the world would that be? Even the panel listing will tell you this is wrong. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 10/9/09 at 9:27 PM..
Reply With Quote
  #7  
Old 10/9/09, 9:42 PM
kluce kluce is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Highland, Indiana
Posts: 265
Please Note: kluce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a problem???

Two hot wires are not allowed.

Two neutral wires not allowed.

But a neutral and a ground from the same circuit, why not?

Last edited by kluce; 10/9/09 at 9:46 PM..
Reply With Quote
  #8  
Old 10/9/09, 9:47 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Is this a problem???

It's specifically prohibited in the NEC, and is in direct contradiction with the listing of the panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 10/9/09, 9:50 PM
kluce kluce is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Highland, Indiana
Posts: 265
Please Note: kluce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a problem???

Still don't know what is the worst thing that can happen.

Around here it is considered an acceptable practice. I don't know one city inspector that will call it out.

I'm so use to seeing this type of installation around here that I never questioned it. I though I seen in the NEC that a neutral and ground are allowed. I'll have to look.
Reply With Quote
  #10  
Old 10/9/09, 9:55 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,799
Default Re: Is this a problem???

Quote:
Originally Posted by kluce View Post
Still don't know what is the worst thing that can happen.

Around here it is considered an acceptable practice. I don't know one city inspector that will call it out.

I'm so use to seeing this type of installation around here that I never questioned it. I though I seen in the NEC that a neutral and ground are allowed. I'll have to look.
Acceptable practice???? Um....do the letters "BS" mean anything to you?
Attached Thumbnails
problem-doublelugneutrals.jpg  



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #11  
Old 10/9/09, 10:01 PM
kluce kluce is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Highland, Indiana
Posts: 265
Please Note: kluce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a problem???

Quote:
Originally Posted by mnahrgang View Post
Acceptable practice???? Um....do the letters "BS" mean anything to you?
The picture in question are not two neutrals. They are a neutral and a ground wire.

I agree that two neutrals are not allowed and clearly noted in the NEC. City Inspectors around here would also not allow that kind of installation.
Reply With Quote
  #12  
Old 10/9/09, 10:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Is this a problem???

Quote:
Originally Posted by kluce View Post
I agree that two neutrals are not allowed and clearly noted in the NEC.
The NEC says nothing about two neutrals;

408.21 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.

The panel listing allows for 1 neutral per termination, and up to 3 grounding conductors per termination.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 10/9/09, 10:26 PM
kluce kluce is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Highland, Indiana
Posts: 265
Please Note: kluce is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a problem???

Trying to get a home inspection report done so I don't have time now to look it up.

Quote:
Originally Posted by kluce View Post
Still don't know what is the worst thing that can happen.
Still don't know what the worst thing that can happen.
Reply With Quote
Find an InterNACHI certified Arizona Home Inspector (and anywhere else in North America)
  #14  
Old 10/9/09, 10:30 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Is this a problem???

In general terms:

I believe it has to do with the "clamping pressure" of the terminal screw with respect to surfaces and a "current" carrying conductor. Normally the Grounding conductor is NOT carrying current (in a perfect world ,its a "safety") so they can be grouped per NEC up to three per termination as Jeff P. has posted.

If you add two "conductors" such as the Grounded (neutral, current carrying) conductor and a Grounding conductor under one terminal it maybe possibly to not properly "fastened" or properly apply correct pressure on the conductors for proper amperage (current) to pass on a smaller surface area due to clamping screw making less contact on the two conductors. Proper torque or pressure on the conductor also determines the amperage at that point. Think surface area and current with respect to responsibility of the conductor.
Reply With Quote
  #15  
Old 10/9/09, 10:34 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,759
Default Re: Is this a problem???

Here, read this. It will "esplain" it.

http://static.schneider-electric.us/...0100DB0705.pdf



"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself."

- John Stuart Mill







Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Weird water heater problem kweiss Plumbing Inspections 3 4/5/09 7:34 PM
furnace problem ? Aaron lore General Inspection Discussion 11 2/5/09 2:04 PM
Internet browser problem bking Miscellaneous Discussion for Inspectors 33 1/26/09 2:45 AM
I have a problem cbottger Electrical Inspections 17 1/20/09 5:45 PM
Plumbing problem at home. mnahrgang Plumbing Inspections 25 7/10/07 6:32 PM