The local sparky and the local AHJ says these double taps are not a problem.
Mid America Property Inspections, Inc. Shawnee, KS 66217 NACHI # 05110992 KS-Registration # 0110-0008 |
| Find an InterNACHI certified Idaho Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Sounds like at least two more people need a Code update class or read the label inside the panel.
|
|
#3
|
||||
|
||||
|
so they are kidding ...right?
|
|
#4
|
||||
|
||||
|
Please Note:
ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
ARTICLE 408 Switchboards and Panelboards
408.41 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor. Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor. |
|
#5
|
|||
|
|||
|
It hard to say what you are talking about since everything looks good.
If you are talking about the neutral and ground wires, it's fine. |
|
#6
|
||||
|
||||
|
In what part of the world would that be? Even the panel listing will tell you this is wrong. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 10/9/09 at 9:27 PM.. |
|
#7
|
|||
|
|||
|
Two hot wires are not allowed.
Two neutral wires not allowed. But a neutral and a ground from the same circuit, why not? Last edited by kluce; 10/9/09 at 9:46 PM.. |
|
#8
|
||||
|
||||
|
It's specifically prohibited in the NEC, and is in direct contradiction with the listing of the panel.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
|||
|
|||
|
Still don't know what is the worst thing that can happen.
Around here it is considered an acceptable practice. I don't know one city inspector that will call it out. I'm so use to seeing this type of installation around here that I never questioned it. I though I seen in the NEC that a neutral and ground are allowed. I'll have to look. |
|
#10
|
||||
|
||||
|
Quote:
|
|
#11
|
|||
|
|||
|
Quote:
I agree that two neutrals are not allowed and clearly noted in the NEC. City Inspectors around here would also not allow that kind of installation. |
|
#12
|
||||
|
||||
|
Quote:
408.21 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor. The panel listing allows for 1 neutral per termination, and up to 3 grounding conductors per termination.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#13
|
|||
|
|||
|
Trying to get a home inspection report done so I don't have time now to look it up.
Still don't know what the worst thing that can happen. |
| Find an InterNACHI certified Idaho Home Inspector (and anywhere else in North America) |
|
#14
|
||||
|
||||
|
In general terms:
I believe it has to do with the "clamping pressure" of the terminal screw with respect to surfaces and a "current" carrying conductor. Normally the Grounding conductor is NOT carrying current (in a perfect world ,its a "safety") so they can be grouped per NEC up to three per termination as Jeff P. has posted. If you add two "conductors" such as the Grounded (neutral, current carrying) conductor and a Grounding conductor under one terminal it maybe possibly to not properly "fastened" or properly apply correct pressure on the conductors for proper amperage (current) to pass on a smaller surface area due to clamping screw making less contact on the two conductors. Proper torque or pressure on the conductor also determines the amperage at that point. Think surface area and current with respect to responsibility of the conductor. |
|
#15
|
||||
|
||||
|
Doug Edwards, CMI |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Weird water heater problem | kweiss | Plumbing | 3 | 4/5/09 7:34 PM |
| furnace problem ? | Aaron lore | General Inspection Discussion | 11 | 2/5/09 2:04 PM |
| Internet browser problem | bking | Misc. Discussion | 33 | 1/26/09 2:45 AM |
| I have a problem | cbottger | Electrical | 17 | 1/20/09 5:45 PM |
| Plumbing problem at home. | mnahrgang | Plumbing | 25 | 7/10/07 6:32 PM |