Default Is this a problem?

problem-remote-distribution-panel-510-ober..jpg

Is this an issue of the grounds being attached to the neutral bar on a plastic remote panel?
Need some feedback on this one.



Ashburn Inspections
724-516-1665
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #2  
Old 12/23/09, 4:40 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Is this a problem?

I can't see it too well because it's a dark picture, but it doesn't matter what material the enclosure is made of, the grounds and neutrals cannot be interconnected/bonded at a load-side panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 12/23/09, 4:49 PM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Is this a problem?

Thank you Jeff. In the upper right hand corner the neutral and grounds are all under the same buss. I called it out and then I spoke to an electrician who showed up today to repair and said that he disagrees with me about this.



Ashburn Inspections
724-516-1665
Reply With Quote
  #4  
Old 12/23/09, 9:04 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Is this a problem?

I can see it better on my home screen.

Let him disagree. He's wrong.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 12/23/09, 9:28 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Is this a problem?

Quote:
Originally Posted by mashburn View Post
Thank you Jeff. In the upper right hand corner the neutral and grounds are all under the same buss. I called it out and then I spoke to an electrician who showed up today to repair and said that he disagrees with me about this.
Did the electrician say why he disagreed with you? The white wire on the breaker is not good either.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #6  
Old 12/23/09, 10:29 PM
Brian C. Hoagland Brian C. Hoagland is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Cocoa, FL
Posts: 3,410
Default Re: Is this a problem?

This is wrong. Often unenforced by local AHJ does not make it right. You gotta love it when you get arguments like this. Be strong you have represented your clents best interests here. The electrical path to the transformer has been compromised due to improper wiring by the allowance of the interference of ground and neutral (ungrounded conductor) connections in the circuit pathway downstream from the main breaker. The only proper location for this connection is in the panel which contains the main disconnect.
Reply With Quote
  #7  
Old 12/24/09, 7:41 AM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Is this a problem?

Thank you all gentleman. I did believe that I was correct.
The electrician said that the ground and neutral are not together, period. I told him that I have a picture and I believed he was wrong. The selling agent wants me to pay the bill for his service call to fix it. The agent is a little feisty and doesn't refer out anyway, so I am respectfully going to decline paying the $35 service call. Yes, $35.00 is all he charges for a service call. He works regularly with this multi-million selling agent, I am sure you can all draw your own conclusions about his integrity and quality of work.

Merry Christmas and Happy Holidays to All!!!!



Ashburn Inspections
724-516-1665
Reply With Quote
  #8  
Old 12/24/09, 11:20 AM
Ron Chorey II's Avatar
Ron Chorey II Ron Chorey II is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Las Cruces, NM eating chili!!
Posts: 638
Default Re: Is this a problem?

Let him take the liability, personally your client should get a second opinion from someone not associated with this agent



Ron Chorey
LAS CRUCES Home Inspections,LLC
Las Cruces NM
88005
575-640-0795
NACHI Membership 04070981
www.lascruceshomeinspections.com



Reply With Quote
  #9  
Old 12/24/09, 11:40 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,749
Default Re: Is this a problem?

I see a neutral lug with the white neutral from the service panel. I see the ground buss with several bare ground wires. They may very well not be in contact with each other. Be careful of the camera angle...could be deceiving. I tend to think the electrician is correct here.
Reply With Quote
  #10  
Old 12/24/09, 12:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Is this a problem?

Looks like a neutral and and a ground are tied together to me.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 12/24/09, 1:53 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this a problem?

They extended the short "neutral" (grouinded conductor) with a piece of bare copper conductor. They could have at least taped it with white tape to better identify it and make it safer.

By the way, in the Canadian Elect. Code, there are instances where bare neutrals are allowed.
Reply With Quote
  #12  
Old 12/24/09, 4:18 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Is this a problem?

My ?????? refer to the short wire and its purpose.

Since it is a 220 volt circuit it could b either "neutral" or equipment grounding.

Without knowing the load it is connected too we can't tell.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #13  
Old 12/27/09, 8:56 AM
mashburn's Avatar
mashburn mashburn is offline
InterNACHI Member
 
Join Date: May 2006
Location: Pittsburgh, PA
Posts: 286
Default Re: Is this a problem?

Quote:
Originally Posted by mboyett View Post
I see a neutral lug with the white neutral from the service panel. I see the ground buss with several bare ground wires. They may very well not be in contact with each other. Be careful of the camera angle...could be deceiving. I tend to think the electrician is correct here.
The neutral and grounds were tied together in the panel.

Thank you all for your replies. The client is getting another electrician to evaluate and separate the grounds here. There are other electrical issue tat neeed repaired anyway so they are picking up the tab.

Hope you all had a great holiday!!



Ashburn Inspections
724-516-1665
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #14  
Old 12/28/09, 10:38 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Is this a problem?

MiKe,

Stick to your guns. If a neutral is present, then it must be electrically and mechanically isolated from the ground and the enclosure. But, based on the photo, there may be more. This may be the electrician's bone of contention, and may be in part based on facts. But he isnt seeing the entire picture, as a neutral IS present and as such, the rules must be followed...

Here goes.

The only time a neutral would not be needed is if the panel supported only a 220V appliance (doesnt need 110V). In that instance, its a simple hot-hot-ground. My contention is that the neutral is not required and should actually be removed in this configuration. No 110volt connection is involved. Everything is 220.

Also, if the cable to the lower left is armor-sheathed, then it should not be terminated into a plastic enclosure. It appears as if this cable's neutral is serving as the ground conductor. I'd look downstream to see what this panel serves. If it serves appliances that have 110volt derivatives (like a clock and controls), there may be even more wrong...

Last edited by jfarsetta; 12/28/09 at 10:46 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Weird water heater problem kweiss Plumbing Inspections 3 4/5/09 6:34 PM
furnace problem ? Aaron lore General Inspection Discussion 11 2/5/09 1:04 PM
Internet browser problem bking Miscellaneous Discussion for Inspectors 33 1/26/09 1:45 AM
I have a problem cbottger Electrical Inspections 17 1/20/09 4:45 PM
Plumbing problem at home. mnahrgang Plumbing Inspections 25 7/10/07 5:32 PM


All times are GMT -4. The time now is 9:21 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts