Question Problems with Ideal SureTest Circuit Analyzer #61-165

Help. I typically check receptacles in homes with an Ideal SureTest Circuit analyzer (#61-165). This unit will apply an appropriate load to a circuit and measure voltage drops. I will recommend further evaluation if over 10% voltage drop. I originally purchased it for testing AFCI at receptacles. I just recently discovered I lost an inspection due to a Realtors recommendation, since I recently "almost" killed a deal from being wrong about measured voltage drops on one of his listings. The owner had an electrician check voltage drops and they came up with a 3% voltage drop, which is of course acceptable. However he did mention they (electricians) plugged in a drill or a lamp to check it. I explained that my testing device costs several hundred dollars and is engineered to test the circuits with a specific load. Does anyone use this particular (or similar) tester and check voltage drops. Does anyone check for voltage drops???? I intend to follow up with the purchaser and find out if possible who the electrician was and challenge them regarding this. Any input on this one greatly appreciated. I do not think many inspectors in my locale are checking voltage drops. Thanks.

John

John M. Wickline
JW Home Inspections, Inc.
Hilton Head Island, SC
JWInspect@hargray.com
Reply With Quote
  #2  
Old 1/26/08, 2:00 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 4,351
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

John,

Been there done that just haven't been caught that wrong yet.

http://www.nachi.org/forum/showthrea...t=voltage+drop



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year
National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes, accept the good
Reply With Quote
  #3  
Old 1/26/08, 4:16 PM
John Wickline John Wickline is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Hilton Head Island, SC
Posts: 85
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Thanks for the reply Barry. Interesting thread.
It appears to be a slightly controversial topic.
Do you still test for Voltage drop?
I think I am getting the picture that most electricians will pull out a small drill or small table lamp to use for a load test, and assure the home owner everything is fine.

John

John M. Wickline
JW Home Inspections, Inc.
Hilton Head Island, SC
JWInspect@hargray.com
Reply With Quote
  #4  
Old 1/26/08, 4:19 PM
gporter's Avatar
gporter gporter is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Orlando, fl
Posts: 3,260
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Model Description List Price Sale Price 61-165 ARCFAULT 165 w/AFCI $312.31 $282.71 Model Accessories List Price Sale Price 61-179 CARRYING CASE $14.45 $14.01 61-182 REPLMT,PWR CORD,SURETEST ARCFA $9.16 $8.89 61-175 GROUND CONTINUITY ADAPTER $17.07 $16.55 61-176 ISOLATED GROUND ADAPTER $17.07 $16.55 61-183 LIGHTG CIRC APT,SURETEST $33.92 $32.91

Which accessories do you need with it



Gary Porter

GLP's Home and Mold Inspections
321-239-0621

Certified Commercial Mold Inspector

Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford
Orange County, Seminole County, Volusia County, Osceola County

www.homeandmoldinspections.com
Reply With Quote
  #5  
Old 1/27/08, 9:50 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 939
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

I had 2 ST testers. My helper used one and it found a lv problem. I, for whatever reason, used mine and it said it was Ok. Hmmmm?

Which is right and which is wrong? So I called the manufacturer and asked how to calibrate. They said "send in with a check". Well I have two of them and do not know which one is wrong. Well heck it almost cost as much calibrate them as buy a new one.

So I am real smart. I figure I'll buy two more and cull out the bad one. Well here come the two new ones and they disagree. Now I have 2 that say OK and 2 that say not OK. So then I say I'll buy 3 more and use them to cull . . . . . well forget that.

Until I can verify calibration I use them for bootleg neutrals and GFCI testing.I simply recommend an electrician verify voltage and voltage drop when other electrical is done (and I always find something).

John
Reply With Quote
  #6  
Old 1/27/08, 10:01 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,795
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

I would really like to see a suretest next to a 1440w space heater and a meter on a long circuit, see if they agree. I fear the short pulse of the suretest might give different results than a regular load. If there is anyone with a suretest in SW Florida near Ft Myers and you want to try it, I have some long circuits, a scope with a current probe and a bunch of meters. We can play with this. We might even be able to get some scope pictures for the gang.
Reply With Quote
  #7  
Old 1/27/08, 10:21 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 4,351
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Quote:
Originally Posted by jcahill
I had 2 ST testers. My helper used one and it found a lv problem. I, for whatever reason, used mine and it said it was Ok. Hmmmm?

Which is right and which is wrong? So I called the manufacturer and asked how to calibrate. They said "send in with a check". Well I have two of them and do not know which one is wrong. Well heck it almost cost as much calibrate them as buy a new one.

So I am real smart. I figure I'll buy two more and cull out the bad one. Well here come the two new ones and they disagree. Now I have 2 that say OK and 2 that say not OK. So then I say I'll buy 3 more and use them to cull . . . . . well forget that.

Until I can verify calibration I use them for bootleg neutrals and GFCI testing.I simply recommend an electrician verify voltage and voltage drop when other electrical is done (and I always find something).

John
John,
Mine has been verified in the field by 2 different electricians (see link in post # 2). Next time you plan on going to the NACHI meeting let me know and we can use one of Richards test panels to verify yours against mine.



badair

ADAIR INSPECTION
972-487-5634

Commercial-Residential-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year
National Association of Commercial Building Inspectors & Thermographers™ Member ID 12011-14TX

life is the random lottery of events followed by numerous narrow escapes, accept the good
Reply With Quote
  #8  
Old 1/27/08, 10:35 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,953
Send a message via Yahoo to tdietrich1
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Curious, why are checking afci's with a hand tester? What are manufature's instrutons?

tom
Reply With Quote
  #9  
Old 1/28/08, 10:49 AM
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 5,118
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

One reason could be, when testing the AFCI at the panel it trips as required. One could assume everything is fine and not bother to walk thru the house or go upstairs and check the receptacles in the room. But using the hand tester the HI can observe the lights on the tester determine it is working properly. Case in point; I did a large house in an upscale neighborhood. The AFCI breaker that was marked Mstr Bedroom was in fact wired to the kitchen and the Mastr bedroom was not AFCI protected at all. Had I stood in the Garage and used only the AFCI test, I may not have found this out.
Reply With Quote
  #10  
Old 1/28/08, 11:01 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,795
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Make 2 trips
Trip the AFCIs from the panel, be sure the BR receptacles, smokes and lights are off, then reset it and see if they all came back on.
A lot of muni inspectors skip step 2.
Reply With Quote
  #11  
Old 1/28/08, 11:28 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Quote:
Originally Posted by tdietrich1
Curious, why are checking afci's with a hand tester? What are manufature's instrutons?

tom
Also why are we checking for voltage drop. Is this not outside the scope of the SOP?
Reply With Quote
  #12  
Old 1/28/08, 11:42 AM
Jeffrey R. Pope, CMI's Avatar
Jeffrey R. Pope, CMI Jeffrey R. Pope, CMI is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 11,795
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Outside the scope of our SOP? Absolutely. I do it as a matter of practice on all new construction inspections, and include my findings in the report. I've been doing this for several years, and have a pretty good understanding of what's going on in most cases. Generally, I report it as an "efficiency" and/or "workmanship" issue, unless there are other obvious indications.

I check for VD on older homes as well, however, I only report on excessive VD when there are indications of other problems within the circuit.

There's much more to understanding and interpreting VD. It's not just a matter of pushing the buttons on our meter.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 1/28/08, 12:20 PM
Doug Edwards Doug Edwards is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 5,118
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Greg,
Exactly. That is the way I do it; one to check to make sure the press to test function is operational and then to make sure the brkr in fact is providing the protection to the proper circuits. The episode with the miswired AFCI make me think about how many times are things mislabeled and never get caught by the Code guys or subsequent owners. Like neglected HVAC, most homeowners never open the panel or have a reason to.
Reply With Quote
  #14  
Old 1/28/08, 12:37 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 8,004
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Friday Insp.


Quote:
INVESTIGATE FURTHER: There was a substantial voltage drop located in the office/bedroom (to the right of the front entry door entering the house). The voltage drop exceeded 17% under a 15 amp load. Supply voltage was less than 100 V under this load (photograph 2744). Wall outlet receptacles are backstabbed instead of using the terminal screws and could potentially create a high resistance due to and inadequate connection. The client intends to use this room as a home office where electronic equipment will be utilized. Manufacturers of electronic equipment require a minimum of 108 V AC to prevent damage to the equipment. This condition should be further evaluated and repaired. The electrical contractor was present at the time of inspection. During our discussion he indicated that smoke detectors were on the circuit with the wall outlets and may have created an excessively long run and high resistance. However, while installing additional lighting the electrical contractor created an arc-fault which tripped the AFCI breaker. Testing of the circuit after this occurrence resulted in greater resistance readings on the neutral wire and higher voltage drops. The voltage surge may have caused the inadequate electrical connection to become worse, resulting in greater resistance/voltage drop. This condition warrants further investigation by a specialist.
I think that when there is a huge voltage differential in a house, there is something there of concern. Maybe the readings may not be 100%, but they indicate there is something going on.

Last edited by dandersen; 12/9/09 at 12:24 PM..
Reply With Quote
  #15  
Old 1/28/08, 1:18 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,953
Send a message via Yahoo to tdietrich1
Default Re: Problems with Ideal SureTest Circuit Analyzer #61-165

Ah, David Anderson.....

Your photo raises questions:

Was it a 15 am circuit?

Where you plugged into a duplex receptacle, or a single?

Was that outlet > 100 feet from it's service/distribution panel?

tom
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Suretest circuit analyzer problems? mporras Electrical Inspections 14 9/24/07 1:26 PM