Help. I typically check receptacles in homes with an Ideal SureTest Circuit analyzer (#61-165). This unit will apply an appropriate load to a circuit and measure voltage drops. I will recommend further evaluation if over 10% voltage drop. I originally purchased it for testing AFCI at receptacles. I just recently discovered I lost an inspection due to a Realtors recommendation, since I recently "almost" killed a deal from being wrong about measured voltage drops on one of his listings. The owner had an electrician check voltage drops and they came up with a 3% voltage drop, which is of course acceptable. However he did mention they (electricians) plugged in a drill or a lamp to check it. I explained that my testing device costs several hundred dollars and is engineered to test the circuits with a specific load. Does anyone use this particular (or similar) tester and check voltage drops. Does anyone check for voltage drops???? I intend to follow up with the purchaser and find out if possible who the electrician was and challenge them regarding this. Any input on this one greatly appreciated. I do not think many inspectors in my locale are checking voltage drops. Thanks.
John John M. Wickline JW Home Inspections, Inc. Hilton Head Island, SC JWInspect@hargray.com |
|
#2
|
||||
|
||||
|
John,
Been there done that just haven't been caught that wrong yet. http://www.nachi.org/forum/showthrea...t=voltage+drop ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#3
|
|||
|
|||
|
It appears to be a slightly controversial topic. Do you still test for Voltage drop? I think I am getting the picture that most electricians will pull out a small drill or small table lamp to use for a load test, and assure the home owner everything is fine. John John M. Wickline JW Home Inspections, Inc. Hilton Head Island, SC JWInspect@hargray.com |
|
#4
|
||||
|
||||
|
Model Description List Price Sale Price 61-165 ARCFAULT 165 w/AFCI $312.31 $282.71
Model Accessories List Price Sale Price 61-179 CARRYING CASE $14.45 $14.01 61-182 REPLMT,PWR CORD,SURETEST ARCFA $9.16 $8.89 61-175 GROUND CONTINUITY ADAPTER $17.07 $16.55 61-176 ISOLATED GROUND ADAPTER $17.07 $16.55 61-183 LIGHTG CIRC APT,SURETEST $33.92 $32.91 Which accessories do you need with it Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
|
#5
|
|||
|
|||
|
I had 2 ST testers. My helper used one and it found a lv problem. I, for whatever reason, used mine and it said it was Ok. Hmmmm?
Which is right and which is wrong? So I called the manufacturer and asked how to calibrate. They said "send in with a check". Well I have two of them and do not know which one is wrong. Well heck it almost cost as much calibrate them as buy a new one. So I am real smart. I figure I'll buy two more and cull out the bad one. Well here come the two new ones and they disagree. Now I have 2 that say OK and 2 that say not OK. So then I say I'll buy 3 more and use them to cull . . . . . well forget that. Until I can verify calibration I use them for bootleg neutrals and GFCI testing.I simply recommend an electrician verify voltage and voltage drop when other electrical is done (and I always find something). John |
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I would really like to see a suretest next to a 1440w space heater and a meter on a long circuit, see if they agree. I fear the short pulse of the suretest might give different results than a regular load. If there is anyone with a suretest in SW Florida near Ft Myers and you want to try it, I have some long circuits, a scope with a current probe and a bunch of meters. We can play with this. We might even be able to get some scope pictures for the gang.
|
|
#7
|
||||
|
||||
|
Quote:
Mine has been verified in the field by 2 different electricians (see link in post # 2). Next time you plan on going to the NACHI meeting let me know and we can use one of Richards test panels to verify yours against mine. ADAIR INSPECTION 972-487-5634 Commercial-Residential-Construction-EIFS-Infrared Thermography TREC # 4563 EDI: EIFS-MA TX # 39 2008 US Member of the Year life is the random lottery of events followed by numerous narrow escapes accept the good |
|
#8
|
||||
|
||||
|
Curious, why are checking afci's with a hand tester? What are manufature's instrutons?
tom |
|
#9
|
||||
|
||||
|
One reason could be, when testing the AFCI at the panel it trips as required. One could assume everything is fine and not bother to walk thru the house or go upstairs and check the receptacles in the room. But using the hand tester the HI can observe the lights on the tester determine it is working properly. Case in point; I did a large house in an upscale neighborhood. The AFCI breaker that was marked Mstr Bedroom was in fact wired to the kitchen and the Mastr bedroom was not AFCI protected at all. Had I stood in the Garage and used only the AFCI test, I may not have found this out.
|
|
#10
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Make 2 trips
Trip the AFCIs from the panel, be sure the BR receptacles, smokes and lights are off, then reset it and see if they all came back on. A lot of muni inspectors skip step 2. |
|
#11
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
||||
|
||||
|
Outside the scope of our SOP? Absolutely. I do it as a matter of practice on all new construction inspections, and include my findings in the report. I've been doing this for several years, and have a pretty good understanding of what's going on in most cases. Generally, I report it as an "efficiency" and/or "workmanship" issue, unless there are other obvious indications.
I check for VD on older homes as well, however, I only report on excessive VD when there are indications of other problems within the circuit. There's much more to understanding and interpreting VD. It's not just a matter of pushing the buttons on our meter. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#13
|
||||
|
||||
|
Greg,
Exactly. That is the way I do it; one to check to make sure the press to test function is operational and then to make sure the brkr in fact is providing the protection to the proper circuits. The episode with the miswired AFCI make me think about how many times are things mislabeled and never get caught by the Code guys or subsequent owners. Like neglected HVAC, most homeowners never open the panel or have a reason to. |
|
#14
|
||||
|
||||
|
Friday Insp.
Quote:
Last edited by dandersen; 12/9/09 at 1:24 PM.. |
|
#15
|
||||
|
||||
|
Ah, David Anderson.....
Your photo raises questions: Was it a 15 am circuit? Where you plugged into a duplex receptacle, or a single? Was that outlet > 100 feet from it's service/distribution panel? tom |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 2 | 1/8/11 8:04 PM |
| Suretest circuit analyzer problems? | mporras | Electrical Inspections | 14 | 9/24/07 2:26 PM |
| Can an AFCI offer GFCI protection | gbeaumont | Electrical Inspections | 19 | 7/7/06 12:45 AM |