Default Procedural Inspection Checklist

for inspecting an electrical panel. The checklist was developed from http://www.nachi.tv/ppv/3.

Every item in the list appears as a defect or comment in the inspection that Nick and Joe T. perform in the 21 minute video.


INSPECTION PROCEDURAL CHECKLIST
Electrical panel

• Follow InterNACHI Standards of Practice
• Wear personal safety protection, including glasses and gloves
• Report location of the electrical panel
• Check adequate workspace
• Panel must be readily accessible
• Use proper inspection tools, including magnet handle, insulated screwdriver, and flashlight
• Check adequate illumination at workspace
• Inspect cabinet front cover
• Check for incorrect type of screws or missing screws at the cabinet front cover
• Measure height of main disconnect
• Inspect panelboard
• All disconnects must have specific identification
• Check for inspection stickers and dates
• Check for identified filler plates
• Identify all breakers in the “off” position
• Identify main overcurrent device
• Determine size of service
• Safe removal of cabinet front cover
• No foreign objects or contamination inside cabinet
• Check entrance conductors and lugs
• Identification of grounded conductor
• Check clamps, connectors, and bushings
• No open knockouts permitted
• Check for disconnected or loose conductors
• Inspect main bonding jumper
• Inspect main grounding electrode conductor (GEC)
• Check for doubled neutrals
• Check for doubled hot conductors
• Identify any breakers that are not permitted by manufacturer
• No white wires on breakers
• Test GFCIs and AFCIs
• No doorbell transformers inside cabinet
• Check for loose equipment grounding conductor (EGC)
• Check for ampacity or overfusing defects
• No melted conductor insulation
• No rust, corrosion, or water inside cabinet
• No gaps between cabinet and wallboard greater than 1/8 inch
• Check multiple cables in connectors
• Check for damage to wires
• Check for damage to insulation sheathing
• Inspect for exposed live wires
• Check identified handle ties
• Read the label on the cabinet front cover
• Identify product name and type of cabinet from label
• Confirm amps and volts are identified on label
• Inspect the panelboard diagram
• Count maximum number of poles from the diagram
• Confirm location of main bonding jumper
• Identify twin or ฝ breakers
• In the subpanel, confirm that the EGC's (equipment grounding conductors) are on a separate terminal bar that is bonded to the cabinet, and that the grounded conductors (neutrals) are isolated or floating from the cabinet
• Never leave panelboard exposed
• Replace cabinet cover correctly



BEN GROMICKO
InterNACHI Director of Education
"
Now That You've Had a Home Inspection" Book
Reply With Quote
  #2  
Old 3/8/08, 4:50 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

That list still has "measure height of main disconnect", which doesn't mean a blessed thing.
Reply With Quote
  #3  
Old 3/8/08, 6:47 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

Quote:
Originally Posted by Marc D. Shunk
That list still has "measure height of main disconnect", which doesn't mean a blessed thing.
Marc:

While at the front of the panelboard during our inspection, I mention the that the main overcurrent device is required to be readily accessible, and is to be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 6 ft 7 in. above the floor or working platform.

I think Ben was looking for comments, and suggestions for improvement and I am sure he can fix the words and mention the height.
Reply With Quote
  #4  
Old 3/8/08, 7:01 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

Quote:
Originally Posted by jtedesco1
Marc:

While at the front of the panelboard during our inspection, I mention the that the main overcurrent device is required to be readily accessible, and is to be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 6 ft 7 in. above the floor or working platform.

I think Ben was looking for comments, and suggestions for improvement and I am sure he can fix the words and mention the height.
Right, but no breaker is allowed to be over that height... not just the main. You could very easily have a panel installed with the main at the bottom, with the main at only 4 feet, and the top most installed branch breaker outside of the permitted limits. That's all I'm saying.
Reply With Quote
  #5  
Old 3/8/08, 7:31 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

Marc:

Do you have an image from a dwellling showing an example of the situation you describe that we could use?

I understand what you are saying, and I agree.
Reply With Quote
  #6  
Old 3/8/08, 7:45 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

Quote:
Originally Posted by Marc D. Shunk
Right, but no breaker is allowed to be over that height... not just the main. You could very easily have a panel installed with the main at the bottom, with the main at only 4 feet, and the top most installed branch breaker outside of the permitted limits. That's all I'm saying.
Marc:

Here's a clip. The top of the main breaker here is much too high for sure. We discovered this during our inspection.

Last edited by jtedesco1; 6/12/08 at 4:38 PM..
Reply With Quote
  #7  
Old 3/8/08, 7:57 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

Quote:
Originally Posted by jtedesco1
Here's a clip. The top of the main breaker here is much too high for sure. We discovered this during our inspection.
Yes, that is cause for concern, but junior's list only talks about the main. In reality, this same concern applies to any breaker in the panel; not just the main.
Reply With Quote
  #8  
Old 3/8/08, 8:53 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Procedural Inspection Checklist

Quote:
Originally Posted by jtedesco1
Marc:

Do you have an image from a dwellling showing an example of the situation you describe that we could use?

I understand what you are saying, and I agree.
Like this?
Attached Thumbnails
procedural-inspection-checklist-img_3987small.jpg  



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #9  
Old 3/8/08, 9:07 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

Quote:
Originally Posted by mlarson
Like this?
Thank you, your picture illustrates what Marc was talking about, if the "main" was up high the branch circuit CB's would be near the ceiling.
Reply With Quote
  #10  
Old 3/8/08, 9:13 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Procedural Inspection Checklist

Quote:
Originally Posted by jtedesco1
Thank you, your picture illustrates what Marc was talking about, if the "main" was up high the branch circuit CB's would be near the ceiling.
It's from today's inspection. My client was from India. I don't think he would be able to reach the breakers if they were installed in the upper portion of the panel.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

[/I]
Reply With Quote
  #11  
Old 3/8/08, 9:35 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

Quote:
Originally Posted by jtedesco1
Thank you, your picture illustrates what Marc was talking about, if the "main" was up high the branch circuit CB's would be near the ceiling.
Even if the main was relatively at a reasonable height, the top most breakers can easily be beyond the recommended 2 meter reach limit.
Reply With Quote
  #12  
Old 3/8/08, 11:47 PM
grusk grusk is offline
Active Poster
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 191
Please Note: grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Procedural Inspection Checklist

For these that don't know; how about a separate section on inspecting the panels on manufactured homes (mobile homes/trailers) not modular homes.

Confirm that the equipment grounding conductors (EGC’s) are on a separate terminal bar that is bonded to the cabinet, and that the grounded conductors or neutrals are isolated and not bonded to the cabinet or to the EGC’s. Most states require a disconnect attached to or within 30 ft. of the home. Also 4 separate entrance conductors besides the 3 conductors you find in a typical panel there has to be one for the equipment grounding conductor, plus the grounded conductor run from main panel or the disconnect to a
grounding rod. Panel also has to be bonded to the frame, if it has 2 sections or more all frames have to be bonded together and if it has a gas line it has to be bonded to the frame. Location of panel in some manufactured homes different than in most homes, places that you would write up in a typical home.

Marc, Joe or anyone; what have I miss or forgotten.


Gary
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Procedural Inspection Checklist bgromicko General Inspection Discussion 0 3/8/08 10:40 AM
inspection procedural checklist bgromicko Electrical Inspections 24 3/2/08 10:00 AM
InterNACHI's accessibility checklist being used in approved real easte course. gromicko Legislation, Licensing & Legal Issues for Inspectors 1 11/7/07 6:02 PM


All times are GMT -4. The time now is 4:07 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts