for inspecting an electrical panel. The checklist was developed from http://www.nachi.tv/ppv/3.
Every item in the list appears as a defect or comment in the inspection that Nick and Joe T. perform in the 21 minute video. INSPECTION PROCEDURAL CHECKLIST Electrical panel Follow InterNACHI Standards of Practice Wear personal safety protection, including glasses and gloves Report location of the electrical panel Check adequate workspace Panel must be readily accessible Use proper inspection tools, including magnet handle, insulated screwdriver, and flashlight Check adequate illumination at workspace Inspect cabinet front cover Check for incorrect type of screws or missing screws at the cabinet front cover Measure height of main disconnect Inspect panelboard All disconnects must have specific identification Check for inspection stickers and dates Check for identified filler plates Identify all breakers in the off position Identify main overcurrent device Determine size of service Safe removal of cabinet front cover No foreign objects or contamination inside cabinet Check entrance conductors and lugs Identification of grounded conductor Check clamps, connectors, and bushings No open knockouts permitted Check for disconnected or loose conductors Inspect main bonding jumper Inspect main grounding electrode conductor (GEC) Check for doubled neutrals Check for doubled hot conductors Identify any breakers that are not permitted by manufacturer No white wires on breakers Test GFCIs and AFCIs No doorbell transformers inside cabinet Check for loose equipment grounding conductor (EGC) Check for ampacity or overfusing defects No melted conductor insulation No rust, corrosion, or water inside cabinet No gaps between cabinet and wallboard greater than 1/8 inch Check multiple cables in connectors Check for damage to wires Check for damage to insulation sheathing Inspect for exposed live wires Check identified handle ties Read the label on the cabinet front cover Identify product name and type of cabinet from label Confirm amps and volts are identified on label Inspect the panelboard diagram Count maximum number of poles from the diagram Confirm location of main bonding jumper Identify twin or ฝ breakers In the subpanel, confirm that the EGC's (equipment grounding conductors) are on a separate terminal bar that is bonded to the cabinet, and that the grounded conductors (neutrals) are isolated or floating from the cabinet Never leave panelboard exposed Replace cabinet cover correctly BEN GROMICKO InterNACHI Director of Education 'Now That You've Had a Home Inspection' Book Home Inspection Training Video on USB |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
That list still has "measure height of main disconnect", which doesn't mean a blessed thing.
|
|
#3
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
While at the front of the panelboard during our inspection, I mention the that the main overcurrent device is required to be readily accessible, and is to be installed so that the center of the grip of the operating handle of the switch or circuit breaker, when in its highest position, is not more than 6 ft 7 in. above the floor or working platform. I think Ben was looking for comments, and suggestions for improvement and I am sure he can fix the words and mention the height. |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc:
Do you have an image from a dwellling showing an example of the situation you describe that we could use? I understand what you are saying, and I agree. |
|
#6
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Here's a clip. The top of the main breaker here is much too high for sure. We discovered this during our inspection. Last edited by jtedesco1; 6/12/08 at 5:38 PM.. |
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
||||
|
||||
|
Quote:
He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father |
|
#9
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#10
|
||||
|
||||
|
Quote:
He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
For these that don't know; how about a separate section on inspecting the panels on manufactured homes (mobile homes/trailers) not modular homes.
Confirm that the equipment grounding conductors (EGCs) are on a separate terminal bar that is bonded to the cabinet, and that the grounded conductors or neutrals are isolated and not bonded to the cabinet or to the EGCs. Most states require a disconnect attached to or within 30 ft. of the home. Also 4 separate entrance conductors besides the 3 conductors you find in a typical panel there has to be one for the equipment grounding conductor, plus the grounded conductor run from main panel or the disconnect to a grounding rod. Panel also has to be bonded to the frame, if it has 2 sections or more all frames have to be bonded together and if it has a gas line it has to be bonded to the frame. Location of panel in some manufactured homes different than in most homes, places that you would write up in a typical home. Marc, Joe or anyone; what have I miss or forgotten. Gary |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Procedural Inspection Checklist | bgromicko | General Inspection Discussion | 0 | 3/8/08 11:40 AM |
| inspection procedural checklist | bgromicko | Electrical Inspections | 24 | 3/2/08 11:00 AM |
| InterNACHI's accessibility checklist being used in approved real easte course. | gromicko | Legislation, Licensing & Legal Issues for Inspectors | 1 | 11/7/07 7:02 PM |