Default Proper distance between a washer drain pipe and 220 volt dryer connection

Can any tell me if there is a specific distance or recommended distance between the drain pipe and a 220 volt dryer plug. I was asked by a Real Estate Salesperson. I can not find it.

Rick
Reply With Quote
  #2  
Old 1/1/06, 2:11 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

There is no requirement. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/1/06, 2:21 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Smile Re: Proper distance between a washer drain pipe and 220 volt dryer connection

Quote:
Originally Posted by rpaul
Can any tell me if there is a specific distance or recommended distance between the drain pipe and a 220 volt dryer plug. I was asked by a Real Estate Salesperson. I can not find it.

Rick
Rick:

Please be more specific. Is the 240 volt dryer supplied by a cord and plug connection, or is it wired directly, and if so with what type of wiring methods?

Is the washer drain entry above, or below the connection? A picture would be helpful here.
Reply With Quote
  #4  
Old 1/1/06, 5:48 AM
Bob Badger Bob Badger is offline
New User
 
Join Date: Dec 2003
Posts: 77
Please Note: Bob Badger is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

Quote:
Originally Posted by jpope
There is no requirement. . .
I agree with Mr Pope.
Reply With Quote
  #5  
Old 1/1/06, 11:46 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

I also agree with Mr. Pope. The overwhelming majority of dryer connections are going to the plug and cord which also aids in the disconnection of the unit as well and so on.....yada..yada..yada.

My only concern really in your question is if the dryer is the old 3 prong or the newer requirement for the 4 prong. Even if the code does not directly speak on distances and we will assume that because of actual spacing the dryer plug is not under the drain area technically the concern could be in the flooding of the washer in that area and a metal casing of the dryer being energized due to a improper situation with the old style 3 wire setup as it is very easy for stray voltage to leak onto the case as they age.

So really that would be my only concern...that is assuming it is a plug and cord which is in about 99.9% of the homes since dryers are not something I would consider permanent...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 1/1/06, 12:04 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

That last post gave me a question???

Dryers: Are the recepticles required to be 4 prong recepticles in ALL new construction now? (In older homes should we be pointing 3 prong recepticles out as "Suggest upgradeing due to new codes and safety concerns."

Stoves/Ranges: Are the recepticles required to be 4 prong recepticles in ALL new construction now? (In older homes should we be pointing 3 prong recepticles out as "Suggest upgradeing due to new codes and safety concerns."

Upgrading could be expensive, not that safety isn't of more concern then the expense.
Reply With Quote
  #7  
Old 1/1/06, 12:08 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

Jason,

Yes, in all new construction the dryers and ranges are required to be of the 4 prong design. The safety concerns are the same as I listed above in which the case can become energized and present a hazzard.

Can you make them change it....surly not...but as a safety concern the NEC is the minimum standard and they felt it was a big enough issue to make the change in newer construction.

Sure you will get those old timers saying...well the 3 prong has worked for years....it is safe....well the leaning tower of PIZA is standing but I don't want to live in it.

Is it expensive....well surly not as much as some obervation suggestions we make as HI's but lets say you don't atleast mention it and something happens....I could see Mr. Ferry having a field day with....." You should have made the owner aware of the potential hazzard "...in the end it is up to the home buyer or owner anyway to weigh the concerns.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 1/1/06, 12:14 PM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

Thank You for your quick response. I knew out here about 7 or so years ago I was told that they were requireing them in all rental homes, apt., etc. regardless of their age. I just didn't know if the code required them in all new construction.
Reply With Quote
  #9  
Old 1/1/06, 4:48 PM
rpaul rpaul is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Elmira, NY
Posts: 101
Send a message via MSN to rpaul Send a message via Yahoo to rpaul
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

To answer the question about the drain and plug. I was asked this by a Real Estatesales person. I could not find anything in writing.
Senerio: Drain Opening is above the 240 outlet with a 1/2 inch space in between.
I could not find anything in writing about this. Common Sense is too close but code there is nothing in writing.

Rick
Reply With Quote
  #10  
Old 1/1/06, 8:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

lol.......AS I am sure Joe, Bob, Greg and myself will tell everyone many times...their is many things about the NEC that does not always make sense which is why in many cases it changes from year to year and in some cases reverts back to previous statements.

As someone once said...Aint the CODE fun....thehehe



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 1/1/06, 8:45 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

Paul:

I agree with all posts here, and my point in my question to Rick was covered by your comments above concerning the water and the electrical system. I always asked nicely that the receptacles in the laundry area be installed above the water and drains.

I am aware of situations where the cause of damage by fire was because of this problem, in fact a proposal for a rule in 110-11? years ago resulted in some code rule (not sure where it is now) that supported the fire problem where a panelboard was located under a tub drain on the second floor.
Reply With Quote
  #12  
Old 1/1/06, 8:52 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

I knew ya had it covered my man.......Excellent post and I always like posts that get the person thinking.....like looking at one aspect and forgetting the safety of another.

Thats what makes the NACHI boards so great... It has electrical nerds like me, you , bob and greg and others feeding endless amounts of information and hoping many learn from it......Only in America Baby !

If only the other 9,000 NACHI members who are not using the message boards would log on to get some great information....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 1/3/06, 8:05 PM
lagudo lagudo is offline
Active Poster
 
Join Date: Nov 2005
Location: Roswell, GA
Posts: 156
Please Note: lagudo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

Paul,
Being in the construction field for 25 yrs.and as a residential GC for 18 of those years I find these boards invaluable. When it came to the construction aspects , I am fine. Electrical,Hvac I relied on the expertise of others. Now as a HI , there is so much I don't know . Thank you all for your insight.
Louis
Reply With Quote
  #14  
Old 1/3/06, 9:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

Hey my friend....thats what i am here for....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 1/3/06, 10:43 PM
jrivera's Avatar
jrivera jrivera is offline
Active Poster
 
Join Date: Jun 2004
Location: Shirley, NY
Posts: 1,340
Please Note: jrivera is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Proper distance between a washer drain pipe and 220 volt dryer connection

Nice job Joe, you da BRAIN

Mickey
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 10:07 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts