Default Proper ground for Csst

Home is a 2007 build.

The main gas line is grounded to the service grounding electrode.

The home has CSST and the builder had it grounded to the gas line.

This is incorrect & a possible safety issue?

Is the correct installation of grounding the CSST is the the earth ground?
(Damm landscapers keep tearing up the cable)

Thanks for your responses.
Attached Thumbnails
proper-ground-corrugated-stainless-steel-tubing-107507-029-small-.jpg.jpg
Views:	678
Size:	54.4 KB
ID:	15521   proper-ground-corrugated-stainless-steel-tubing-107507-034-small-.jpg.jpg
Views:	622
Size:	84.8 KB
ID:	15523  
Reply With Quote
  #2  
Old 10/25/07, 2:42 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Proper ground for Csst

Looks okay from my house.

Now that I think about it more, it seems bonding near the black pipe gas line entry is what I read but here are a couple of links.

http://www.pddocs.com/csst/faq.aspx

http://www.nachi.org/forum/showthrea...sst+bonding%22

http://www.nachi.org/forum/showthrea...sst+bonding%22



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.

Last edited by lkage; 10/25/07 at 2:58 PM..
Reply With Quote
  #3  
Old 10/25/07, 2:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Proper ground for Csst

The gas line is bonded to the grounding electrode and the CSST is bonded to the rigid gas line. Bonding and grounding are different.

CSST manufacturers have specific bonding requirements which, in some cases, include installation of additional grounding electrodes. The requirements vary depending on the Lightning Density Zone (LDZ) of your area.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 10/25/07 at 3:00 PM..
Reply With Quote
  #4  
Old 11/2/07, 11:46 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Proper ground for Csst

Just a note of caution...especially for HIs.

I am in the process of doing research for this topic. Just to let you know that CSST is not UL listed, it is CSA listed. CSST was originally trying to get a UL listing and they did not pass the evaluation there.

The change in the manufacturers installation instructions which happened just recently has some discrepcencies.
1. did they go back to the listing company to get the new instructions evaluated by the listing company....
2. There are discrepcencies with the method they provide for bonding the system.

3. most problems they have encountered are due to lightning/grounding issues not bonding issues. This system is not permitted to be grounded

I could go on, but I will wait until I have received more info back.

As a HI, I would defer all discussions or recommendations back to the building department or AHJ and pass on that responsibility/liability.
Reply With Quote
  #5  
Old 11/2/07, 11:52 PM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,093
Default Re: Proper ground for Csst

Quote:
Originally Posted by Pierre Belarge
Just a note of caution...especially for HIs.

I am in the process of doing research for this topic. Just to let you know that CSST is not UL listed, it is CSA listed. CSST was originally trying to get a UL listing and they did not pass the evaluation there.

The change in the manufacturers installation instructions which happened just recently has some discrepcencies.
1. did they go back to the listing company to get the new instructions evaluated by the listing company....
2. There are discrepcencies with the method they provide for bonding the system.

3. most problems they have encountered are due to lightning/grounding issues not bonding issues. This system is not permitted to be grounded

I could go on, but I will wait until I have received more info back.

As a HI, I would defer all discussions or recommendations back to the building department or AHJ and pass on that responsibility/liability.
Thanks Pierre....



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #6  
Old 11/3/07, 7:56 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Proper ground for Csst

http://www.gastite.com/include/langu.../TB2007_01.pdf



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #7  
Old 11/3/07, 8:07 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,482
Default Re: Proper ground for Csst

Quote:
Originally Posted by jhagarty
I have a similar one around here somewhere for Pro-Flex CSST...but off to an inspection shortly.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
Electricians Check List pabernathy Electrical Inspections 74 12/5/07 7:39 PM
Unable to confirm proper ground.. gmathias Electrical Inspections 22 10/27/06 9:20 PM
Electrical Inspection Training for Home Inspectors jtedesco1 Inspection Education & Training 6 4/27/06 11:43 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 9:48 AM