#1
|
||||
|
||||
|
Home is a 2007 build.
The main gas line is grounded to the service grounding electrode. The home has CSST and the builder had it grounded to the gas line. This is incorrect & a possible safety issue? Is the correct installation of grounding the CSST is the the earth ground? (Damm landscapers keep tearing up the cable) Thanks for your responses. |
|
#2
|
|||
|
|||
|
Looks okay from my house.
Now that I think about it more, it seems bonding near the black pipe gas line entry is what I read but here are a couple of links. http://www.pddocs.com/csst/faq.aspx http://www.nachi.org/forum/showthrea...sst+bonding%22 http://www.nachi.org/forum/showthrea...sst+bonding%22 InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
Last edited by lkage; 10/25/07 at 2:58 PM.. |
|
#3
|
||||
|
||||
|
The gas line is bonded to the grounding electrode and the CSST is bonded to the rigid gas line. Bonding and grounding are different.
CSST manufacturers have specific bonding requirements which, in some cases, include installation of additional grounding electrodes. The requirements vary depending on the Lightning Density Zone (LDZ) of your area. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 10/25/07 at 3:00 PM.. |
|
#4
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Just a note of caution...especially for HIs.
I am in the process of doing research for this topic. Just to let you know that CSST is not UL listed, it is CSA listed. CSST was originally trying to get a UL listing and they did not pass the evaluation there. The change in the manufacturers installation instructions which happened just recently has some discrepcencies. 1. did they go back to the listing company to get the new instructions evaluated by the listing company.... 2. There are discrepcencies with the method they provide for bonding the system. 3. most problems they have encountered are due to lightning/grounding issues not bonding issues. This system is not permitted to be grounded I could go on, but I will wait until I have received more info back. As a HI, I would defer all discussions or recommendations back to the building department or AHJ and pass on that responsibility/liability. |
|
#5
|
||||
|
||||
|
Quote:
- Mike Michael W. Gault, SC RBI 1728 A to Z Home Inspections Charleston, Dorchester & Berkeley Counties in S.C. NACHI05040682 www.atozinspector.com (843) 442-9755 Charleston Home Inspector |
|
#6
|
||||
|
||||
|
Joseph P. Hagarty, CMI joseph.hagarty@comcast.net Main Line Inspections, Inc. Phone: 610-399-3675 Email: MainLineHI@comcast.net http://pa.nachi.org/mainlinepa/about.html http://www.householdinspector.com National President / NACHI (2003-2004) NACHI Education Committee Member |
|
#7
|
|||
|
|||
|
Quote:
InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector serving the Traverse City, Michigan area and beyond.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 4:56 PM |
| Electricians Check List | pabernathy | Electrical Inspections | 74 | 12/5/07 7:39 PM |
| Unable to confirm proper ground.. | gmathias | Electrical Inspections | 22 | 10/27/06 9:20 PM |
| Electrical Inspection Training for Home Inspectors | jtedesco1 | Inspection Education & Training | 6 | 4/27/06 11:43 PM |
| Harmonized Ground Fault Circuit Interrupters | jtedesco1 | Electrical Inspections | 5 | 3/21/06 9:48 AM |