Found a tub outside wired with a 30 amp regular panel breaker and 10 gauge wire.
Down the line they had an additional 50 amp gfci breaker before the tub. Is this sufficent. I figured it should be. Just wanted to confirm Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
| Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
What does the nameplate on the hot tub say? Is a 30 amp circuit large enough for the load?
|
|
#3
|
||||
|
||||
|
The hot tub was broken so I did not inspect it. I guess it s up to the new installer huh?
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#4
|
||||
|
||||
|
For future reference RObert, If it does say 30 amp, would the 50 gfci still serve the purpose of a safety breaker?
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
The GFCI will still function properly and can also serve as the unit disconnect.
|
|
#6
|
||||
|
||||
|
The label is law and should never be install otherwise under or over. Reason for operating the way it was designed to. If calls for 30 amps it should be 30 amps. Electricity is nothing to play with or guess if not known should ask a qualified electrician.
Florida Licensed Home Inspector HI #36 Certified Master Inspector Palm City, Florida, 34990 772 240 0431 / 954 330 2227 |
|
#7
|
||||
|
||||
|
Thanks Robert, thats what I thought!
Infraspection Institute Level 1 Certified Infrared Thermographer Fogarty Inspection Services Group of Knoxville TN Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas. 865-256-5397 www.homeinspectorknoxville.com www.moldandradon.com www.thermal-inspection.net www.commercial-building-inspector.net |
|
#8
|
||||
|
||||
|
On a similar subject, most hot tubs have a low voltage control jumper option where you choose whether or not to allow the pump to run on high with the heat running. When the smaller of the two circuits is used you have to jumper it to use less current which means the heat will only run if the pump is on low. This option may make the nameplates confusing if you don't know about it. The dataplates are usually not accessible without removing part of the skirting.
B.A. King Home Inspections, LLC www.BAKingHomeInspections.com Serving Charlotte NC area and Rock Hill SC areas. CMI Certified Master Inspector and Independent License NC2449 and SC1597 704 301-3207 "Discovery consists in seeing what everyone else has seen and thinking what no one else has thought." - Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937 |
|
#9
|
|||
|
|||
|
Is there a difference in tripping sensitivity of a higher amperage GFCI breaker over a lower amperage GFCI breaker, or do they monitor the difference in current between the neutral and ungrounded conductor at same rate and would trip at same time regardless of the amperage?
by the above post assume it does , just want to make sure. Carlos Orellana Houston Texas |
|
#10
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#11
|
|||
|
|||
|
Thank You Robert.
Carlos |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Evaluating your home's wiring system | mcyr | Electrical Inspections | 0 | 12/30/09 1:31 PM |
| Top Ten Wiring Hazards Threaten Life and Property | jtedesco1 | Electrical Inspections | 3 | 9/2/08 5:15 PM |
| Electricians Check List | pabernathy | Electrical Inspections | 74 | 12/5/07 6:39 PM |
| Nice Report on AL Wire Terminations - Enjoy | pabernathy | Electrical Inspections | 0 | 7/2/07 12:35 PM |