Unhappy Properly Testing GFCI Outlets

Mornin All,
I have a question I need with about GFCI outlets replaced in 2-wire systems & haven't seen this addressed or missed it when it was. I live in Wyoming & there are probably more 2 prong outlets here than in the whole rest of the world. A lot of "wet areas" that I've tested that have 2 prong outlets (numerous 2 prong outlets present throughout the rest of the house)replaced with GFCI outlets show "open ground" & won't trip when challenged with any external tester I've tried ( the ones w/black button on top), BUT will when their own "test" button is pushed on the outlet. Is this a "false positive" or am I missing something?? Don't these external testers (like I use) cause a direct short to similiate an actual short in an appliance?? How accurate are they?
T.J. " 2-prong " Christopher



NACHI #03120124
www.aplushomeinspections.net

Proundly Serving S.E. Wyoming & Western Nebraska


"Learn from the mistakes of others,
Life is to short to make them all yourself"
Reply With Quote
  #2  
Old 3/15/07, 2:40 PM
cbrands's Avatar
cbrands cbrands is offline
New User
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 96
Please Note: cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Properly Testing GFCI Outlets

most simple testers just cause a small ground fault.
no ground to fault to, no trip.

this is how most testers will behave.

no trip with tester.
test button trips and resets fine.
Reply With Quote
  #3  
Old 3/15/07, 2:48 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Properly Testing GFCI Outlets

T.J., the plug-in GFCI testers function by simulating a "fault" to the ground pin. In a 2 wire outlet there is no available "ground" so the tester can't simulate the fault.
If the GFCI's own test button produces a "tripped outlet" it is working fine.

edited: Chris beat me to it.
Reply With Quote
  #4  
Old 3/15/07, 3:59 PM
jbreazeale jbreazeale is offline
Active Poster
 
Join Date: Aug 2006
Location: Sardis, MS
Posts: 618
Please Note: jbreazeale is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Properly Testing GFCI Outlets

Yes, T.J. ....GFCI replacement receptacles on 2-wire ungrounded circuits do work, but as everyone says, won't "test" for the reasons already stated. I make a habit of recommending them...not only in "wet" locations, but suggesting that they can be installed at the upstream receptacle in each branch circuit for added child safety. Clients appreciate that info. Here's a suggested comment:

"The home has a two-wire, ungrounded system, which was the norm when the home was built. Modern standards call for GFCI (Ground Fault Circuit Interruptors) in kitchens, outdoor locations, and other wet locations such as pools and spas. AFCI (Arc Fault Circuit Interruptors) are now required for bedroom circuits. While these upgrades are not a requirement in this particular home, I strongly recommend consulting a licensed electrician about installing GFCI receptacles in all the locations and conditions mentioned above that may be present in this home."

I recommend GFCI upstream on bedroom circuits simply because AFCI won't work on an ungrounded system, and installation of GFCI renders more protection than simply leaving it alone. I have found that people usually follow up on this, as it is relatively inexpensive....and even the agents like it!

It's a win win.

Jimmy B.
Reply With Quote
  #5  
Old 3/15/07, 11:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Properly Testing GFCI Outlets

Quote:
Originally Posted by jbreazeale

I recommend GFCI upstream on bedroom circuits simply because AFCI won't work on an ungrounded system
Jimmy B.
Can I ask where you received that information?

AFCI’s have superior performance protection over a standard circuit breaker when it comes to low-level line-to-neutral faults. In an old house I would surely install them and recommend them, even though they are not required by the NEC because the code is not retrocative...But safety is.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 3/16/07, 5:26 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Properly Testing GFCI Outlets

Quote:
Originally Posted by pabernathy
the code is not retrocative...But safety is.
No, no, no, Paul. Safety is not retroactive. Just read the newspaper each day or watch your local news.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #7  
Old 3/16/07, 8:16 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Properly Testing GFCI Outlets

As we have joked about in the past:

fill the sink with water
put one hand in the water
put one finger in the small plughole
does it trip?

If the circuit does not have a ground at the plug, you must become ground for the device to work.
I don't personally practice this test procedure, nor do I endorse it!

I never trust the test buttons on GFCI outlets. They lie all the time! So when you report it, describe how you tested the device (with the devices internal test circuit) and report the results of the test. Do not report that all GFCI's were tested and functional (because you don't know).
Reply With Quote
  #8  
Old 3/16/07, 1:12 PM
John Lomonaco John Lomonaco is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Greentown, PA
Posts: 83
Default Re: Properly Testing GFCI Outlets

Quote:
Originally Posted by tchristopher
Mornin All,
I have a question I need with about GFCI outlets replaced in 2-wire systems & haven't seen this addressed or missed it when it was. I live in Wyoming & there are probably more 2 prong outlets here than in the whole rest of the world. A lot of "wet areas" that I've tested that have 2 prong outlets (numerous 2 prong outlets present throughout the rest of the house)replaced with GFCI outlets show "open ground" & won't trip when challenged with any external tester I've tried ( the ones w/black button on top), BUT will when their own "test" button is pushed on the outlet. Is this a "false positive" or am I missing something?? Don't these external testers (like I use) cause a direct short to similiate an actual short in an appliance?? How accurate are they?
T.J. " 2-prong " Christopher
GFCI's will not work properly with out a ground. The ground provides a reference point for the internal circuitry of the GFCI, removing the reference point from the circuitry anything goes....

John
Reply With Quote
  #9  
Old 3/16/07, 1:17 PM
tchristopher tchristopher is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Torrington, WY
Posts: 276
Default Re: Properly Testing GFCI Outlets

Hey All,
Thanx for the replies (more are welcome)
1. Can you properly test a GFCI outlet? If so how..(within reason & not extending your inspection into a full blown electrical evaluation.)
2. Also is there anyway to test 2 prong outlets to see if grounded??
Thanx,
T.J.



NACHI #03120124
www.aplushomeinspections.net

Proundly Serving S.E. Wyoming & Western Nebraska


"Learn from the mistakes of others,
Life is to short to make them all yourself"
Reply With Quote
  #10  
Old 3/16/07, 1:19 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Properly Testing GFCI Outlets

Quote:
Originally Posted by jlomonaco
GFCI's will not work properly with out a ground. The ground provides a reference point for the internal circuitry of the GFCI, removing the reference point from the circuitry anything goes....
John
Hey, John.

I think every electrician here in San Diego will disagree with you. In fact, a common fix for two-prong outlets without rewiring a house is simply to replace the two-prong outlets with GFCI outlets since they don't need to be grounded.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #11  
Old 3/16/07, 1:21 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Properly Testing GFCI Outlets

Quote:
Originally Posted by tchristopher
Hey All,
Thanx for the replies (more are welcome)
1. Can you properly test a GFCI outlet? If so how..(within reason & not extending your inspection into a full blown electrical evaluation.)
2. Also is there anyway to test 2 prong outlets to see if grounded??
Thanx,
T.J.
I test GFCI outlets using the manufacturer's test button, just like the manufacturer recommends in their installation instructions. If it's good enough for the manufacturer, it's good enough for me.

Two-prong outlets, by definition, are not grounded.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #12  
Old 3/16/07, 1:41 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Properly Testing GFCI Outlets

I dislike seeing the myth, that GFCI's require a ground to function. This scares people off from upgrading older homes with them, and put many people at risk.

How do we get rid of this type of thinking, when those 'who should know' perpetuate it?

Also, where did the idea that AFCI's require a ground? They don't even accept an equipment grounding conductor. Did this stem from that AFCI's now have a lower ground fault detection like a GFCI, but not as low?

Would you not recommend Smoke Detectors in homes built prior to their being required? Ofcouse not. So always include information about the personal safety of GFCI's and property/personal safety of AFCI's in all your reports for homes that don't have any. We might just save some one's home or life.

IMHO!!!!!!

tom
Reply With Quote
  #13  
Old 3/16/07, 1:56 PM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,559
Default Re: Properly Testing GFCI Outlets

Quote:
Originally Posted by tdietrich1
I dislike seeing the myth, that GFCI's require a ground to function. This scares people off from upgrading older homes with them, and put many people at risk.

How do we get rid of this type of thinking, when those 'who should know' perpetuate it?
We just have to keep educating everyone, sometimes even our own. Hec, one of the reasons why I stick around NACHI is because the education here is great.

NACHI rocks!
NACHI rolls!
NACHI rules!



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #14  
Old 3/16/07, 5:58 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Properly Testing GFCI Outlets

Quote:
Originally Posted by rray
No, no, no, Paul. Safety is not retroactive. Just read the newspaper each day or watch your local news.
lol...thats what I mean RRay.......thats the HI's job to demand safety and ignore the fact NEC guys ( like myself ) will say it fine..as it was CODE at the time of installation....when in fact codes change because of safety issues and news findings.........thats why i favor AFCI's so much....

And yes they DO work without a " Grounding " conductor, not sure now who made that statement but it is false.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #15  
Old 3/16/07, 9:20 PM
tchristopher tchristopher is offline
InterNACHI Member
 
Join Date: Dec 2003
Location: Torrington, WY
Posts: 276
Default Re: Properly Testing GFCI Outlets

Hey Paul, T.J. here, the original poster, is there any way or need to test these GFCI (that show open ground on my tester) outlets other than with their own trip buttons & just list as GFCI outlet w/open ground.
Thanx,
T.J.
P.S. If you ever sit on a toilet seat in Wyoming, you better tap it with the back of your hand first to make sure it's grounded, LOL!!!!



NACHI #03120124
www.aplushomeinspections.net

Proundly Serving S.E. Wyoming & Western Nebraska


"Learn from the mistakes of others,
Life is to short to make them all yourself"
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 2 1/8/11 8:04 PM
bbbb mcyr Structural Inspections 1 8/19/07 11:26 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 10:31 AM
Replacing 2-prong outlets with GFCI outlets kshepard Electrical Inspections 7 6/24/06 7:58 AM
UL Information about Testing of GFCIs jtedesco1 Electrical Inspections 0 2/5/06 5:38 PM