Default Pushmatic and service size help

this Pushmatic has two 100 amp breakers labeled "main disconnect"
they are the top breakers in each of the two columns.

notice the way the 120 volt legs strap back and forth from the columns.
am i to assume this is actually a 200 amp service.

panel did not have a rating
entrance conductors were rated for 200 amp...CL200 meter.
Attached Thumbnails
pushmatic-and-service-size-help-100_3242-small-.jpg.jpg
Views:	138
Size:	35.9 KB
ID:	14728   pushmatic-and-service-size-help-100_3239-small-.jpg.jpg
Views:	121
Size:	67.9 KB
ID:	14729  
Reply With Quote
  #2  
Old 9/23/07, 9:18 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic and service size help

That's a 200 amp Pushmatic panel, and you might note the working space violation.
Reply With Quote
  #3  
Old 9/23/07, 9:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Pushmatic and service size help

Quote:
Originally Posted by Marc D. Shunk
That's a 200 amp Pushmatic panel, and you might note the working space violation.
And the transformer laying in the bottom of the panel. Next? There's more.
Reply With Quote
  #4  
Old 9/23/07, 9:29 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,937
Default Re: Pushmatic and service size help

Quote:
Originally Posted by mlarson
And the transformer laying in the bottom of the panel. Next? There's more.
Whats wrong with that its worked great for over thirty years , Thats what the agent will say .
...... Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #5  
Old 9/23/07, 9:32 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Pushmatic and service size help

Quote:
Originally Posted by rcooke
Whats wrong with that its worked great for over thirty years , Thats what the agent will say .
...... Cookie
Ya, I know. They have all kinds of excuses don't they?
Reply With Quote
  #6  
Old 9/23/07, 9:36 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,937
Default Re: Pushmatic and service size help

Quote:
Originally Posted by mlarson
Ya, I know. They have all kinds of excuses don't they?
Actually I see some Pushmatic's and have no concerns with those I have inspected but none have been over 100 amp and the room was OK.
You could still buy new breakers for them in Canada the last time I looked .
Very expensive but they where available.About $27.00 for a 15 amp I think
......... Cookie



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #7  
Old 9/23/07, 9:40 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Pushmatic and service size help

Roy, I don't consider push-matics a problem.
Reply With Quote
  #8  
Old 9/23/07, 9:51 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic and service size help

I assume Marc is referring to the ceiling grid "L" track on the wall.
Is that really the ceiling line???
Reply With Quote
  #9  
Old 9/23/07, 10:20 PM
cbrands's Avatar
cbrands cbrands is offline
New User
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 96
Please Note: cbrands is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic and service size help

Quote:
Originally Posted by Speedy Petey
I assume Marc is referring to the ceiling grid "L" track on the wall.
Is that really the ceiling line???
yes, ceiling line.
bedroom in basement...drop ceiling left about a 6" space for egress...or lack thereof.
Reply With Quote
  #10  
Old 9/23/07, 10:46 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic and service size help

Quote:
Originally Posted by cbrands
yes, ceiling line.
bedroom in basement...drop ceiling left about a 6" space for egress...or lack thereof.
OK....YIKES!!


DAMN, I just looked again and I see the ceiling tile in the second pic!
Reply With Quote
  #11  
Old 9/23/07, 10:55 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic and service size help

I might guess that the top most breakers are also above the 6' 7" limit.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 4:30 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts