Default Pushmatic questions

This is a pushmatic panel. 125 amp rating. The meter is a 100/200 amp. There does not appear to be a main shutoff. There is a 60 amp breaker that is the second breaker that says "main lights" on the breaker and "main 110v" on the panel cover. Is that the main breaker? Seems like that is the wrong spot if it is. Also, there are no conductors to that breaker. I was thinking that it didn't need one because of the "5 hand motion" rule, but it would take at least 11 movements by my count to shut off everything.
Attached Thumbnails
pushmatic-questions-p6100141.jpg   pushmatic-questions-p6100142.jpg   pushmatic-questions-p6100144.jpg   pushmatic-questions-p6100150.jpg   pushmatic-questions-p6100151.jpg  




Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
Find an InterNACHI certified North Carolina Home Inspector (and anywhere else in North America)
  #2  
Old 6/11/09, 1:16 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic questions

It's a split bus. The breaker below the dryer breaker kills the "lighting section", which is everything below it.
Reply With Quote
  #3  
Old 6/11/09, 3:15 PM
Michael J. Merino's Avatar
Michael J. Merino Michael J. Merino is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Oak Forest, IL
Posts: 757
Default Re: Pushmatic questions

Quote:
Originally Posted by brian winkle View Post
It's a split bus. The breaker below the dryer breaker kills the "lighting section", which is everything below it.
Thanks Brian, I was reading about split bus last night. What is the best indicator of a split bus?



Michael Merino
Merino's Home Inspection & Education Inc.
"Not just an Inspection, an Education"SM
Phone/Fax 708~535~6057
Reply With Quote
  #4  
Old 6/11/09, 6:57 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,472
Default Re: Pushmatic questions

I recommend electrical panel replacement when I see any push-matic panel/breakers. Springs inside rust, corrode, and break. Some insurance companies, will not insure a home with these panels in place. I have had many issues with these breakers when I used to test them; they would never re-set.
Reply With Quote
  #5  
Old 6/11/09, 8:03 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 30,554
Default Re: Pushmatic questions

From someone who used to post here and was usually very helpful.

mdshunk

The PushMatics were of famously high-quality, and were probably discontinued because it was hard for old people to push them in completely to click them over from 'on' to 'off' and vice-versa. It takes a firm press. There aren't really any reported problems with the actual trip mechanism failing over the years. The PushMatic breakers are my all-time favorite residential breaker, and I wish they still made them. They had to be the most bullet-proof residential breaker design ever made. Sadly, many of them are simply at the end of their lives now. They were installed up until the late 70's and very early 80's. Most of what you'll run across is from the 60's.



He who knows nothing is closer to the truth than he whose mind is filled with falsehoods and errors - Thomas Jefferson - Founding Father

The democracy will cease to exist when you take away from those who are willing to work and give to those who would not. Thomas Jefferson

Never underestimate the difficulty of changing false beliefs by facts.
- Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
and
Minnesota Home Inspector

Reply With Quote
  #6  
Old 6/11/09, 9:14 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic questions

Pushmatics are great.
Insurance companies have no problem with them as they are high end.
Reply With Quote
  #7  
Old 6/11/09, 10:00 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 740
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic questions

The best indication is opening the cover and seeing wires going from a breaker in the top section heading down to the buss below. Typically the cover is divided into two sections with space for up to six double pole breakers up top and the smaller branch circuits in the lower section.
Reply With Quote
  #8  
Old 6/12/09, 8:50 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Pushmatic questions

Quote:
I recommend electrical panel replacement when I see any push-matic panel/breakers. Springs inside rust, corrode, and break. Some insurance companies, will not insure a home with these panels in place. I have had many issues with these breakers when I used to test them; they would never re-set.
Pushmatic started with Bulldog Electric, which became ITE, then Gould, and finally Siemens.
There were NO reported problems with them. There are still virtually NO reported problems with them. In fact, you can still purchase them, though a bit pricey.

Which insurance companies? None that I know of. "Springs rust, corrode, and break". I submit that if a spring rusts and corrodes for a Pushmatic breaker, then there is a problem with the environment in which the panel was installed, which would likely adversely affect any panel.

Test them? Does that mean you would short circuit them. Who's SOP are you following?

Last edited by jfarsetta; 6/12/09 at 8:54 AM..
Reply With Quote
  #9  
Old 6/12/09, 12:33 PM
Gary Farnsworth Gary Farnsworth is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Olathe, KS
Posts: 3,472
Default Re: Pushmatic questions

Push-matic breaker concerns.

http://www.inspect-ny.com/electric/Pushmatic.htm
Reply With Quote
  #10  
Old 6/12/09, 12:56 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic questions

Quote:
Originally Posted by gfarnsworth View Post
From that link...

Quote:
Originally Posted by www.inspect-ny.com/electric/Pushmatic.htm
As of February 2009 we have received occasional field reports on product failures of PushMatics, and older similar Bulldog circuit breakers and electrical panels, but not enough data to reach a sound conclusion about the reliability and safety of this electrical equipment. we have been unable to find independent research reports on this product.
Reply With Quote
  #11  
Old 6/12/09, 1:00 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic questions

Quote:
Originally Posted by gfarnsworth View Post
Some insurance companies, will not insure a home with these panels in place.

I have had many issues with these breakers when I used to test them; they would never re-set.
I think we tread on dangerous ground when we start to advise on insurance or insurability of properties.

Likewise, there are very few absolutes in the world. Always and never are dangerous to use.

Unless it's "The Cubs will never win the World Series."
Reply With Quote
  #12  
Old 6/12/09, 2:53 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Pushmatic questions

While I do appreciate the information provided on the InspectNY site, remember that, like my own, there are merely someone's OPINION.

I have lots of opinions on lots of things.

Doesnt mean I am always right, or always wrong.

Last I checked, InspectNY wasn't a testing lab.
Reply With Quote
  #13  
Old 6/12/09, 3:50 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,758
Default Re: Pushmatic questions

Quote:
Originally Posted by rmaday View Post
I think we tread on dangerous ground when we start to advise on insurance or insurability of properties.
I disagree. I feel it's very important to point out issues that may hinder the ability to insure the residence.

Having said that, I have NEVER heard of an instance where insurance was denied because of the brand of panel (i.e. FPE, Zinsco, etc.) or the type of circuit breaker (i.e. pushmatic, Stab-lok, etc.). I would like to see someone support these claims.

I have had experience with insurance companies denying insurance based on fused panels, K&T wiring and AL wiring that has not been "upgraded."



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
Find an InterNACHI certified North Carolina Home Inspector (and anywhere else in North America)
  #14  
Old 6/12/09, 4:02 PM
rmaday's Avatar
rmaday rmaday is offline
Active Poster
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 5,197
Please Note: rmaday is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic questions

Quote:
Originally Posted by jpope View Post
I disagree. I feel it's very important to point out issues that may hinder the ability to insure the residence.
What are some other issues, outside of what you mentioned, that have made insuring a property difficult?

I would guess that there are many insatances, like this, of an HI saying something makes the property uninsureable, when in fact, it does not.

There was a thread, a while back, that stated 60AMP electrical service made a property uninsurable.
Reply With Quote
  #15  
Old 6/12/09, 4:18 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Pushmatic questions

Quote:
Originally Posted by rmaday View Post
What are some other issues, outside of what you mentioned, that have made insuring a property difficult?

I would guess that there are many insatances, like this, of an HI saying something makes the property uninsureable, when in fact, it does not.

There was a thread, a while back, that stated 60AMP electrical service made a property uninsurable.
The Carson Dunlop many of us trained under makes Insurance denial claims on things such as asphalt siding and may have something on Pushmatics but I know that is B.S.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
980 Questions/Answers to the NHIE....Free! jbushart Legislation, Licensing & Legal Issues for Inspectors 50 4/20/08 2:26 AM
Honest questions about CMI lcapaul General Inspection Discussion 493 2/28/08 12:38 AM
FetchReport Questions for NIck lcapaul Miscellaneous Discussion for Inspectors 51 6/12/07 1:53 PM
Some good questions that always need answers jtedesco1 Electrical Inspections 5 6/16/06 10:10 PM


All times are GMT -4. The time now is 9:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts