Default PVC conduit interior location

I installed some PVC conduit under a raised platform area today to use as a chase for some low voltage speaker wires in my church. (we're doing some major remodeling, and a new addition so I volunteered a little time today) This area will shortly become very inaccessable, so I was dreaming up ways to get wires through the area after the deck gets covered. The electrician on the job gave me a heapin' helpin' of grief about it, because that same area actually serves as a draw area for hvac return air, and his rationale is that the gray pvc conduit is not "plenum rated". I knew you only used pvc for exterior applications for full-current applications, but I thought the issue was it's vulnerability to injury and failure in a wall or overhead- say, in the bar joists. But the real issue, I learned, was it's fire rating, and the toxic fume issue in a fire. and especially in an area that would serve as a return air plenum. So my initial argument that it was only to be used for low-voltage speaker wire didn't matter according to him. PVC isn't allowed inside for any reason, even if it's just being stored there!

I felt a little foolish, well alright, a lot foolish, as he made some sideways comment about me being a home inspector and not knowing any better... But it was a lesson learned. I don't know that I've ever seen it used inside a residential application, so it wasn't something that leaped to mind while I was doing it. It will from now on tho!
Reply With Quote
  #2  
Old 4/21/06, 1:27 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: PVC conduit interior location

He is right. EMT is a better choice.
Reply With Quote
  #3  
Old 4/21/06, 7:57 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: PVC conduit interior location

See NEC 300.22(C)
Reply With Quote
  #4  
Old 4/21/06, 9:10 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,078
Default Re: PVC conduit interior location

Quote:
Originally Posted by jtedesco1
See NEC 300.22(C)
Joe

A lot of us have the IRC but not the NEC, could you post a snippet from the applicable section and paragraph?



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #5  
Old 4/21/06, 10:49 AM
bkelly1's Avatar
bkelly1 bkelly1 is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,757
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: PVC conduit interior location

Can you not get some plenum rated speaker wire?

And yes he is right.
Reply With Quote
  #6  
Old 4/21/06, 11:19 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: PVC conduit interior location

Quote:
Originally Posted by mgault
Joe

A lot of us have the IRC but not the NEC, could you post a snippet from the applicable section and paragraph?
300.22 Wiring in Ducts, Plenums, and Other Air-Handling Spaces
The provisions of this section apply to the installation and uses of electric wiring and equipment in ducts, plenums, and other air-handling spaces.

(C) Other Space Used for Environmental Air This section applies to space used for environmental air-handling purposes other than ducts and plenums as specified in 300.22(A) and (B). It does not include habitable rooms or areas of buildings, the prime purpose of which is not air handling.

FPN: The space over a hung ceiling used for environmental air-handling purposes is an example of the type of other space to which this section applies.

Section 300.22(C) applies to other spaces that are used to transport environmental air and that are not specifically manufactured as ducts or plenums, such as the space or cavity between a structural floor or roof and a suspended (hung) ceiling. Many spaces above suspended ceilings are intended to transport return air. Some spaces are also used for supply air, but they are far less common than those used for return air. This section does not apply to habitable rooms and other areas whose prime purpose is other than air handling. Such an area is shown in Exhibit 300.20. If the prime purpose of the room or space is air handling as depicted in Exhibit 300.20, then the restrictions in 300.22(C) apply, whether or not electrical equipment is located in the room.

Exception: This section shall not apply to the joist or stud spaces of dwelling units where the wiring passes through such spaces perpendicular to the long dimension of such spaces.

The exception to 300.22(C) permits cable to pass through joist or stud spaces of a dwelling unit, as illustrated in Exhibit 300.21. The joist space is covered with sheet metal and used as a cold-air return for a forced warm-air central heating system. Equipment such as junction boxes or device enclosures is not permitted in this location.

(1) Wiring Methods The wiring methods for such other space shall be limited to totally enclosed, nonventilated, insulated busway having no provisions for plug-in connections, Type MI cable, Type MC cable without an overall nonmetallic covering, Type AC cable, or other factory-assembled multiconductor control or power cable that is specifically listed for the use, or listed prefabricated cable assemblies of metallic manufactured wiring systems without nonmetallic sheath. Other types of cables and conductors shall be installed in electrical metallic tubing, flexible metallic tubing, intermediate metal conduit, rigid metal conduit without an overall nonmetallic covering, flexible metal conduit, or, where accessible, surface metal raceway or metal wireway with metal covers or solid bottom metal cable tray with solid metal covers.

Revised for the 2002 Code, 300.22(C)(1) no longer permits liquidtight flexible metal conduit as covered in Article 350 to be installed within ``other spaces used for environmental air.'' The previous exception permitting this application for single lengths up to 6 ft was removed.

(2) Equipment Electrical equipment with a metal enclosure, or with a nonmetallic enclosure listed for the use and having adequate fire-resistant and low-smoke-producing characteristics, and associated wiring material suitable for the ambient temperature shall be permitted to be installed in such other space unless prohibited elsewhere in this Code.
Electrical equipment with metal enclosures is allowed within spaces used for environmental air. However, nonmetallic enclosures must be listed for this use.

Exception: Integral fan systems shall be permitted where specifically identified for such use.

It is not intended that the requirements of 300.22(B) or 300.22(C) apply to air-handling areas beneath raised floors in information technology rooms. See Article 645, Information Technology Equipment.

(D) Information Technology Equipment Electric wiring in air-handling areas beneath raised floors for information technology equipment shall be permitted in accordance with Article 645.

www.nfpa.org
Reply With Quote
  #7  
Old 4/21/06, 12:55 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: PVC conduit interior location

You may also get grief from the life safety officer (AKA fire marshal) who has his own rules about places of public assembly. Unfortunately churches tend to be the worst offenders, mostly because they do get so much volunteer work.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Conduit as Ground cbuell Electrical 12 4/16/07 7:18 PM
Should this be in conduit kblair1 Electrical 18 12/26/06 5:50 PM
White Paper On Lead In Steel Conduit jtedesco1 Electrical 1 12/19/06 4:32 PM
NACHI Chapters Free Electrical Training Available jtedesco1 Education 5 8/11/06 5:46 PM
Conduit psmothers Electrical 2 6/3/06 1:05 PM


All times are GMT -4. The time now is 11:20 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147