Default Question ????

Should I or would you be concerned about a 10 degree temp differential between the two legs on a 240 volt double pole breaker Yes or no please
Attached Thumbnails
question-430-greg-ln-enid-7-8-11-073.jpg  



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
Need a home inspection in Indiana? Check out InterNACHI's listing of Indiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/9/11, 8:53 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,186
Default Re: Question ????

Yes.
Reply With Quote
  #3  
Old 7/9/11, 8:57 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Question ????

Quote:
Originally Posted by ldapkus1 View Post
Yes.
Ok I am gathering yes and no's lets see who wins



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #4  
Old 7/9/11, 9:09 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Question ????

Quote:
Originally Posted by cbottger View Post
Should I or would you be concerned about a 10 degree temp differential between the two legs on a 240 volt double pole breaker Yes or no please
No. I wouldn't be too concerned because 240V loads are not always perfectly balanced and 10 degrees F isn't very much of a difference. You might first want to look at what type of load it is. You could also put a clamp-on Ammeter on each leg to see if there is much of a difference between the two legs. Also look for loose connections. If the load is a 240V heating element or something similar, the legs would have exactly the same current flowing. One being hotter than the other would suggest a loose connection. One the other hand, some appliances have both 120V and 240V loads. At any given time, one leg could be carrying more or less current than the other so one leg could be hotter than the other.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #5  
Old 7/9/11, 9:12 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,186
Default Re: Question ????

Quote:
Originally Posted by gwells View Post
No. I wouldn't be too concerned because 240V loads are not always perfectly balanced and 10 degrees F isn't very much of a difference. You might first want to look at what type of load it is. You could also put a clamp-on Ammeter on each leg to see if there is much of a difference between the two legs. Also look for loose connections. If the load is a 240V heating element or something similar, the legs would have exactly the same current flowing. One being hotter than the other would suggest a loose connection. One the other hand, some appliances have both 120V and 240V loads. At any given time, one leg could be carrying more or less current than the other so one leg could be hotter than the other.
A loose connection would be localized to the connection, no?
Any way you look at it, it's a possible deficiency that warrants investigation.

Last edited by ldapkus1; 7/9/11 at 9:18 PM..
Reply With Quote
  #6  
Old 7/9/11, 9:18 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Question ????

Quote:
Originally Posted by gwells View Post
No. I wouldn't be too concerned because 240V loads are not always perfectly balanced and 10 degrees F isn't very much of a difference. You might first want to look at what type of load it is. You could also put a clamp-on Ammeter on each leg to see if there is much of a difference between the two legs. Also look for loose connections. If the load is a 240V heating element or something similar, the legs would have exactly the same current flowing. One being hotter than the other would suggest a loose connection. One the other hand, some appliances have both 120V and 240V loads. At any given time, one leg could be carrying more or less current than the other so one leg could be hotter than the other.
Ok one yes and one no

The appliances that have 120 volt circuits are mostly for clocks and timers that virtually have no amp draw not enough to effect the infrared temp



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #7  
Old 7/9/11, 9:21 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Question ????

Quote:
Originally Posted by ldapkus1 View Post
A loose connection would be localized to the connection, no?
Any way you look at it, it's a possible deficiency that warrants investigation.
Are you sure think about what you are saying. Just asking



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #8  
Old 7/9/11, 9:24 PM
Linas Dapkus's Avatar
Linas Dapkus Linas Dapkus is offline
InterNACHI Member
 
Join Date: Feb 2011
Location: Home
Posts: 2,186
Default Re: Question ????

I would need to be there to make the call.
Reply With Quote
  #9  
Old 7/9/11, 9:26 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Question ????

No big deal I agree with George .
I think you will find this is very common . Roy



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #10  
Old 7/9/11, 9:30 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Question ????

Quote:
Originally Posted by rcooke View Post
No big deal I agree with George .
I think you will find this is very common . Roy
Are you absolutely sure this is very common I take that for a no

one yes and two no's



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #11  
Old 7/9/11, 9:43 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Question ????

yes If we are talking about a feed to a sub panel



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.




Last edited by rcooke; 7/9/11 at 9:50 PM..
Reply With Quote
  #12  
Old 7/9/11, 9:55 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: Question ????

Quote:
Originally Posted by rcooke View Post
yes If we are talking about a feed to a sub panel
I did not say what the breaker was feeding but it was not feeding a sub panel I will give more specifics after I collect a few more yes or no's



Freedom Express Inspections LLC
CMOR Thermography Certified Level III #8486
freedomexpressinspections.com
www.oklahomathermalinfraredimaging.com
freedomexpress495@att.net
NACHI Member
Okla. State DEQ Environmental Phase One Certified
Master HVAC Mechanic (Retired)
Certified Universal Freon by 40CFR 82 Sub-part F
State License # 130
Serving the States of Okla, Texas, Kansas, Missouri , Arkansas and New Mexico with Commercial Inspections,Thermal Imaging
Reply With Quote
  #13  
Old 7/9/11, 10:13 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question ????

Quote:
Originally Posted by cbottger View Post

The appliances that have 120 volt circuits are mostly for clocks and timers that virtually have no amp draw not enough to effect the infrared temp
The motor on a dryer is 120.
Reply With Quote
Need a home inspection in Indiana? Check out InterNACHI's listing of Indiana certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/9/11, 10:21 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Question ????

Quote:
Originally Posted by cbottger View Post
I did not say what the breaker was feeding but it was not feeding a sub panel I will give more specifics after I collect a few more yes or no's
If it is feeding a balanced load then I would expect they should both be very close to same temp.



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #15  
Old 7/9/11, 10:36 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Question ????

Quote:
Originally Posted by cbottger View Post
Ok one yes and one no

The appliances that have 120 volt circuits are mostly for clocks and timers that virtually have no amp draw not enough to effect the infrared temp
I have to respectfully disagree with that one Charlie. I've recorded my highest temps at 900+F and 600+F on 120v circuits.

BTW: Is that a split buss I see? What kind of load is on each leg? Tell me more about that hot spot on the buss.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX

Last edited by cevans; 7/9/11 at 10:39 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sump Pit/Pump Question Joey D'Adamo Plumbing Inspections 4 11/26/08 1:04 PM
Question for all... Bob Hopton-Jones General Inspection Discussion 9 4/6/07 7:43 AM
Basement Bathroom Venting Question Sean M. Jeric Plumbing Inspections 4 3/20/07 11:56 PM


All times are GMT -4. The time now is 9:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts