I had a client today who claimed to be an electrical engineer and had a problem with the main electric panel. There was a 100amp feed, no single main disconnect, and instead 4 disconnects with combined amperage exceeding 100amp by 60 or 70 amps. He assured me that the 100amp feed could overheat unless a 100amp main breaker was added. I told him he was full of crap. Kidding.
I see this set up all the time from the 70's and 80's and never heard of it being an issue. Any thoughts? |
| Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Take a look at NEC 230.90(A)Exception #3.
|
|
#3
|
|||
|
|||
|
VII. Service Equipment — Overcurrent Protection
230.90 Where Required. Each ungrounded service conductor shall have overload protection. (A) Ungrounded Conductor. Such protection shall be provided by an overcurrent device in series with each ungrounded service conductor that has a rating or setting not higher than the allowable ampacity of the conductor. A set of fuses shall be considered all the fuses required to protect all the ungrounded conductors of a circuit. Single-pole circuit breakers, grouped in accordance with 230.71(B), shall be considered as one protective device. Exception No. 3: Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the overload protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors. InterNachi Awards Portal: http://co.nachi.org/inachiawards/ ____________________________________________ "An Education, not just an Inspection" Larry Kage, CMI Welcome Home Inspection Services, LLC whis11 @ charter.net Lake Ann, Michigan 49650 The above post represents my personal opinion. For statements of fact or advice or my professional opinion, on this or another subject, please contact me, directly. Thnx, Jim.
|
|
#4
|
|||
|
|||
|
Would the calculated load be the all equipment used by any paticular home owner added up?
Cameron Anderson Bachelor of Architecture, U of I, Urbana IL Illinois Licensed Inspector www.aaintegrityhomeinspection.com |
|
#5
|
||||
|
||||
|
If I understand correctly, you are describing a service entrance feeding multiple units? If that is right, then the connected load is not the sum of all the individual loads. There is demand factors applied to the calculations, in addition to the minimum required dwelling circuits. Logically, for example, it stands to reason not every occupant would be cooking, or doing laundry at the exact time. That is the pupose of the demand factors.
|
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
So if by using your method the total connected load were 150 amps and using the Article 220 method the connected load was calculated to be 100 amps then the service entrance conductor size would only need to be 100 amps. Even if you had up to 6 service disconnects when you add their ampacities together (as in the OP) they could total more than the ampacity of the service entrance conductors and still be code compliant by the Exception #3 in 230.90(A). |
|
#7
|
|||
|
|||
|
You guys are great. Thanks a bunch!
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Have you ever seen this? | jgorum | Electrical Inspections | 15 | 4/1/12 10:06 AM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| question on electrical service | Coral Chesney | Electrical Inspections | 6 | 2/24/07 9:35 AM |
| Electrical Inspection with Temp. Service? | dandersen | Electrical Inspections | 16 | 6/27/06 10:41 PM |