Quote:
I had it in my brain from a electronics circuit analysis class with a cube or delta "type" circuit based on multiple similar value of resistors. A source applied to cube and points of voltage / current tested / calculated to see what is happening.. In a "perfect" world zero current across a resistor at center of cube... |
|
#17
|
|||
|
|||
|
Please Note:
Joey D'Adamo is a non-member guest and is in no way affiliated with InterNACHI or its members.
I'm surprised all of you are ignoring how volts and amps work mathematically.
For a standard single-phase 120/240V supply at 200A, what you have is 200A @ 240V. That is 200Ax240V = 48kW. You can also measure it as 400A@120V if you want to becuase 400Ax120V = 48kW as well. That would just be a highly unconventional way of representing the service, but both are equivilant mathematically. You could feed 200A worth of 240V equipment from that service, 400A worth of 120V equipment, or anywhere in between. The latter being the common means, of course. For three phase, you have a factor of ~1.73 (sqrt(3)) introduced. So a 120/208V three-phase supply at, say, 200A, has 200A*208V*1.73 = 71.9kW. Ultimately, when power sources are expressed using watts, it is easier to compare them. |
|
#18
|
|||
|
|||
|
Joey
The cable size (gage and conductor type) is based on amps, how it is installed and the length of the run computed with the allowable voltage drop - the insulation is based on voltage. And yes this is part of the math to comput the size of a neutral conductor As you can see it is all simple math -- how much to you need and how big is the required pipe In your example if the limiting factor was the 48Kw rating you would exced the curent rating of the conductors at 400 amps if they were rated at 200 amps. Thus your statement of 400 amp of equipment at 120 volts is not correct and will not work. Real simple the cable is only rated for 200 amps for the length that it is being used. Remember this is also part of the design. One can not run a # 14 extention cord from NY to Tx and light a 100 watt light bulb with 120 volts - too much resistance in the wire rlb rlb Last edited by rbennett; 7/23/06 at 11:29 PM.. |
|
#19
|
|||
|
|||
|
Please Note:
Joey D'Adamo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Lets suppose you have the following two circuits available to you: Circuit #1 offers 20A at 120v from two wires (hot/neutral). Circuit #2 offers 10A at 120/240v from three wires (hot/hot/neutral). Assume that the 80% rule does not apply, and assume that all wires are adequately sized for their amperage such that circuit #1 has a minimum of 12 guage wire and circuit #2 has a minimum of 16 gauge wire. Also assume that voltage drop is not a concern. None of these assumptions hurt the validity of the examples. Work out the math to show that both supplies can power the same amount of 100 watt light bulbs without exceeding the capacity of any wires . Then you should understand what I was saying. Or think about how twice as much power is available between a 30A, 120V and 30A, 240V air conditioner circuits. Or how a transformer on any given circuit could be used to provide twice the amperage at half the voltage, or half the voltage at twice the amperage. (or any other similar ratio such as 1/3 the amperage at 3x the voltage). Work some of those examples out and you will see my point. I think what I am saying is quite relevant to the original poster's question. |
|
#20
|
|||
|
|||
|
Joe
Yes, power is equal to voltage times amperage. One of the points that is a good one to make is that we rate for current and voltage - Not wattage on a 120/240 three wire ckt. Yes, as we all know, it is all directly related. The main condition that will mess the system up and cause current ratings to exceed design is LOW VOLTAGE. Low voltage will cause higher current and higher power loses in all areas of the electrical system Paul A --- help me out here -- maybe we need a new thread -- we are sort of off the original question Wattage is work -- Voltage and current rating is potential work (KVA rating) rlb Last edited by rbennett; 7/24/06 at 8:10 PM.. |
|
#21
|
||||
|
||||
|
Mathematically it may work but we are talking about a non-controlled, non-laboratory environment here Joey. Sure you can use assumptions all you want but we have so many variables to deal with you cannot use this approach in a real world practical application.
If this where the case then high power transmission stations, lines, equipment would not exist in the form they do. Think of all the loss and load issues, power fluctuations not to mention how the consumer changes the load on super hot days when all those A/C units are running and the factories are running all those motors...hmmmm Coils..hmmmm Wouldn't it be great if we could forget about resistance altogether. How about the Loss of energy in heat!! You talk of watts but what a watt.. Well that is the conversion of one type of energy to another with loss... Heat from a light bulb, motor ...gone...lost..... So living in a imperfect world with all those variables leads me to believe that we can only get so much out of all that "stuff" ... |
|
#22
|
|||
|
|||
|
Quote:
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| question on electrical service | Coral Chesney | Electrical Inspections | 6 | 2/24/07 9:35 AM |
| Electrical Safety Principles | pabernathy | Electrical Inspections | 8 | 1/1/07 1:13 PM |
| Some good questions that always need answers | jtedesco1 | Electrical Inspections | 5 | 6/16/06 9:10 PM |
| Electrical Safety Information | jtedesco1 | Electrical Inspections | 0 | 2/19/06 1:48 AM |
| Wired for Safety Video | jtedesco1 | Electrical Inspections | 0 | 1/4/06 6:31 AM |