Default Re: A Question for the Electrical Gurus

Quote:
Originally Posted by jtedesco1
If that was ever possible, here is the link for an article: "Characteristics of the Neutral Conductor, written by James Stallcup.

Courtesy: EC&M

Code Basics
Thanks Joe, Paul,

I had it in my brain from a electronics circuit analysis class with a cube or delta "type" circuit based on multiple similar value of resistors.
A source applied to cube and points of voltage / current tested / calculated to see what is happening.. In a "perfect" world zero current across a resistor at center of cube...
Reply With Quote
  #17  
Old 7/23/06, 10:40 PM
Joey D'Adamo Joey D'Adamo is offline
New User
 
Join Date: Aug 2004
Posts: 38
Please Note: Joey D'Adamo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A Question for the Electrical Gurus

I'm surprised all of you are ignoring how volts and amps work mathematically.

For a standard single-phase 120/240V supply at 200A, what you have is 200A @ 240V. That is 200Ax240V = 48kW. You can also measure it as 400A@120V if you want to becuase 400Ax120V = 48kW as well. That would just be a highly unconventional way of representing the service, but both are equivilant mathematically. You could feed 200A worth of 240V equipment from that service, 400A worth of 120V equipment, or anywhere in between. The latter being the common means, of course.

For three phase, you have a factor of ~1.73 (sqrt(3)) introduced. So a 120/208V three-phase supply at, say, 200A, has 200A*208V*1.73 = 71.9kW.

Ultimately, when power sources are expressed using watts, it is easier to compare them.
Reply With Quote
  #18  
Old 7/23/06, 11:15 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: A Question for the Electrical Gurus

Joey

The cable size (gage and conductor type) is based on amps, how it is installed and the length of the run computed with the allowable voltage drop - the insulation is based on voltage.

And yes this is part of the math to comput the size of a neutral conductor

As you can see it is all simple math -- how much to you need and how big is the required pipe

In your example if the limiting factor was the 48Kw rating you would exced the curent rating of the conductors at 400 amps if they were rated at 200 amps. Thus your statement of 400 amp of equipment at 120 volts is not correct and will not work. Real simple the cable is only rated for 200 amps for the length that it is being used. Remember this is also part of the design. One can not run a # 14 extention cord from NY to Tx and light a 100 watt light bulb with 120 volts - too much resistance in the wire

rlb


rlb

Last edited by rbennett; 7/23/06 at 11:29 PM..
Reply With Quote
  #19  
Old 7/24/06, 6:13 PM
Joey D'Adamo Joey D'Adamo is offline
New User
 
Join Date: Aug 2004
Posts: 38
Please Note: Joey D'Adamo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: A Question for the Electrical Gurus

Quote:
Originally Posted by rbennett
Joey

The cable size (gage and conductor type) is based on amps, how it is installed and the length of the run computed with the allowable voltage drop - the insulation is based on voltage.

And yes this is part of the math to comput the size of a neutral conductor

As you can see it is all simple math -- how much to you need and how big is the required pipe

In your example if the limiting factor was the 48Kw rating you would exced the curent rating of the conductors at 400 amps if they were rated at 200 amps. Thus your statement of 400 amp of equipment at 120 volts is not correct and will not work. Real simple the cable is only rated for 200 amps for the length that it is being used. Remember this is also part of the design. One can not run a # 14 extention cord from NY to Tx and light a 100 watt light bulb with 120 volts - too much resistance in the wire

rlb


rlb
I admit that referring to my example service as 400A @ 120V is unconventional, but to understand why I am not wrong, work out the following example.

Lets suppose you have the following two circuits available to you:
Circuit #1 offers 20A at 120v from two wires (hot/neutral).
Circuit #2 offers 10A at 120/240v from three wires (hot/hot/neutral).

Assume that the 80% rule does not apply, and assume that all wires are adequately sized for their amperage such that circuit #1 has a minimum of 12 guage wire and circuit #2 has a minimum of 16 gauge wire. Also assume that voltage drop is not a concern. None of these assumptions hurt the validity of the examples.

Work out the math to show that both supplies can power the same amount of 100 watt light bulbs without exceeding the capacity of any wires . Then you should understand what I was saying.

Or think about how twice as much power is available between a 30A, 120V and 30A, 240V air conditioner circuits. Or how a transformer on any given circuit could be used to provide twice the amperage at half the voltage, or half the voltage at twice the amperage. (or any other similar ratio such as 1/3 the amperage at 3x the voltage).

Work some of those examples out and you will see my point.

I think what I am saying is quite relevant to the original poster's question.
Reply With Quote
  #20  
Old 7/24/06, 8:02 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: A Question for the Electrical Gurus

Joe

Yes, power is equal to voltage times amperage. One of the points that is a good one to make is that we rate for current and voltage - Not wattage on a 120/240 three wire ckt. Yes, as we all know, it is all directly related.

The main condition that will mess the system up and cause current ratings to exceed design is LOW VOLTAGE. Low voltage will cause higher current and higher power loses in all areas of the electrical system

Paul A --- help me out here -- maybe we need a new thread -- we are sort of off the original question

Wattage is work -- Voltage and current rating is potential work (KVA rating)

rlb

Last edited by rbennett; 7/24/06 at 8:10 PM..
Reply With Quote
  #21  
Old 7/25/06, 11:38 AM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: A Question for the Electrical Gurus

Mathematically it may work but we are talking about a non-controlled, non-laboratory environment here Joey. Sure you can use assumptions all you want but we have so many variables to deal with you cannot use this approach in a real world practical application.

If this where the case then high power transmission stations, lines, equipment would not exist in the form they do. Think of all the loss and load issues, power fluctuations not to mention how the consumer changes the load on super hot days when all those A/C units are running and the factories are running all those motors...hmmmm Coils..hmmmm

Wouldn't it be great if we could forget about resistance altogether.
How about the Loss of energy in heat!! You talk of watts but what a watt..

Well that is the conversion of one type of energy to another with loss...
Heat from a light bulb, motor ...gone...lost.....

So living in a imperfect world with all those variables leads me to believe that we can only get so much out of all that "stuff" ...
Reply With Quote
  #22  
Old 7/25/06, 1:09 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: A Question for the Electrical Gurus

Quote:
Originally Posted by Joey D'Adamo
I'm surprised all of you are ignoring how volts and amps work mathematically.

For a standard single-phase 120/240V supply at 200A, what you have is 200A @ 240V. That is 200Ax240V = 48kW. You can also measure it as 400A@120V if you want to becuase 400Ax120V = 48kW as well. That would just be a highly unconventional way of representing the service, but both are equivilant mathematically. You could feed 200A worth of 240V equipment from that service, 400A worth of 120V equipment, or anywhere in between. The latter being the common means, of course.

For three phase, you have a factor of ~1.73 (sqrt(3)) introduced. So a 120/208V three-phase supply at, say, 200A, has 200A*208V*1.73 = 71.9kW.

Ultimately, when power sources are expressed using watts, it is easier to compare them.
lol..Why would you be surprised...you yourself said it was highly unconventional...lol



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
question on electrical service Coral Chesney Electrical Inspections 6 2/24/07 9:35 AM
Electrical Safety Principles pabernathy Electrical Inspections 8 1/1/07 1:13 PM
Some good questions that always need answers jtedesco1 Electrical Inspections 5 6/16/06 9:10 PM
Electrical Safety Information jtedesco1 Electrical Inspections 0 2/19/06 1:48 AM
Wired for Safety Video jtedesco1 Electrical Inspections 0 1/4/06 6:31 AM